Jump to content

Recommended Posts

Posted

Hi

 

We have virtual infrastructure in place.

We have the following

1) SAN ,

2) Three host

3)1 Backup server

4)6 switches

5)Telephone EAPBX

 

Please can you let me know what temperature need to be maintained.

 

Thanks

Posted

We've got ours set at 19 degrees.

 

It depends on how many server racks you've got as in the 'olden day' everyone just concentrated on chilling the room whereas large server rooms with a few racks have cold spots and hotspots as air flow is just as important as temperature and by having hot and cold spots you cause the air to move around and moving air is cooler than air that is sitting still.

Posted
21-23c depending on the room and where it is and the kit in the room, where possible we try and get 2 units in each room for resiliency a well so in our London office we have 2x 30,000BTU units we can run on one of them with careful monitoring of the environment whilst the other is repaired, in smaller locations the load is still split where possible over 2 units to give again some level of resiliency as we are usually stuck in the basement or sub-basement so cannot say open a window for a temp unit etc..
Posted
Ours are all set to 22C but we monitor it and get email alerts if it ver gets to 25C (which normally only happens when estates turn off the circuit the AC runs off of to work on other things without telling us)
Posted

As mentioned earlier , humidity is also a concern, if it gets to dry then you can get static build up.

 

We monitor

Temperature ( rack in, rack out)

Humidity

AC HZ

UPS Load ( we have some client sockets on the UPS, we recently saw a 10KVA increase in draw on these, I knew exactly the cause)

Floor level moisture.

And some other stuff.

 

Cooling is all N+1, at one point we were loosing one out of our 4 coolers and could still achieve +1. I think we have actually reduced our thermal load since then too.

 

 

I remember at my old job, we converted an old store room to be the Server room. But after growing from 5-6 Servers to 10+ it was overheating. We installed our own A/C , but the "KIT" had restricted length pipework and the Condenser unit had to be situated in another store room. It worked well enough even in the middle of summer, until the Head complained his office floor was red hot :) . New Pro AC ordered ;)

 

TT

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now



×
×
  • Create New...