mitchell1981 Posted February 28, 2017 Posted February 28, 2017 Hi All, We have a number of APC Smart UPS 5000 (SUA5000RMI5U) in our server room. One of them has started to report that a battery need replacing but it isn't telling us which one. We've got a replacement ready to go but there are four batteries in the unit. Do we have to manually test the batteries with a battery tester to see which one has failed, or are we overlooking a log somewhere that identifies the location of the failed battery? Thanks.
Sagima Posted February 28, 2017 Posted February 28, 2017 If the batteries are all the same age I'd be inclined to change them all at once rather than running old and new batteries in the same unit. I have three of those UPSs but I can't see individual battery statuses in any of the web pages so you may be down to testing them yourselves. 1
localzuk Posted February 28, 2017 Posted February 28, 2017 Its normal to change them all at once in a unit. 1
GuyJD Posted February 28, 2017 Posted February 28, 2017 (edited) The APC software works on up-time, so testing the batteries will reveal nothing, best to check manufacturer dates on the batteries to see which is the oldest, that should be a good indication of which one is reporting the message. Edited February 28, 2017 by GuyJD 1
MYK-IT Posted February 28, 2017 Posted February 28, 2017 We have the same UPS, I would (and we did) change all 4 batteries at once. 1
mitchell1981 Posted February 28, 2017 Author Posted February 28, 2017 Thanks all. I think we will follow the general advice and buy more batteries and replace them all. They are around 5 years old anyway so definitely due a replacement.