Guest Guest Posted October 12, 2020 Posted October 12, 2020 We have an APC Smart UPS which currently is failing to run it's self test, when running via the control panel on the UPS itself it refuses to run. When ran via PowerChute it runs for several hours and eventually fails. Does this sound like a failing battery? it still seems to be able to support a load Any help is greatly appreciated
Davit2005 Posted October 12, 2020 Posted October 12, 2020 The APC should tell you if it needs a battery replacement. I've got 2 at home and both have told me, I've got one complaining at the moment. Have you by any chance got a network card in the UPS?
chazzy2501 Posted October 12, 2020 Posted October 12, 2020 won't run the self test vs fails during the self test. Usually pressing the "on" button for a second will trigger the self test.
Koldov Posted October 12, 2020 Posted October 12, 2020 Does the 'PowerChute' software give any indication on battery charge levels etc?
Guest Guest Posted October 12, 2020 Posted October 12, 2020 I disconnected the USB cable and reconnected and now it seems to pass the self test. Although Powerchute says that we're using 0 amps and 0% of the VA despite it powering our phone system and 1 server. Still refuses to run a test via the LCD though
Koldov Posted October 20, 2020 Posted October 20, 2020 Might be worth a quick physical check of the battery too...
robyholmes Posted October 20, 2020 Posted October 20, 2020 (edited) Might be worth a quick physical check of the battery too... [ATTACH=CONFIG]59495[/ATTACH] [ATTACH=CONFIG]59496[/ATTACH] I found our 'Happy' UPS which passed self tests, had a battery in it that had expanded so much, we had to use a lump hammer and crow bar to get it out! The battery had a big hole in the side in the end which it had welded itself to the case side. Had to 'persuade' the rack mount UPS case back in to shape before refitting the new batteries. Edited October 20, 2020 by elsiegee40
MatthewL Posted October 20, 2020 Posted October 20, 2020 Not the first time I've seen or heard about batteries having to be pried out as they had expanded so much.
DrBeaker Posted October 20, 2020 Posted October 20, 2020 Yeah I've had to pretty much dismantle one UPS before in order to get the battery out of the chassis it had expanded that much.