AB_IT Posted November 26, 2025 Posted November 26, 2025 Hey All, Just wanted to check if it would be a problem, basically bought this big UPS that's going to help power some of the servers. It requires however a hardwired connection into the back so Positive, Ground, Neutral wires to be stripped and the screwed into the back. Is there anything wrong with me using a Kettle Lead, stripping it and just wiring it in myself, plugging it into a UK 3 Pin Socket or is this a fire hazard etc...? Maybe I'm being dumb but thought it was worth the ask Thanks All
CrootUK Posted November 26, 2025 Posted November 26, 2025 (edited) What model is the UPS usually it has specifc requirements in there doc? I would suspect if its big and requires hard wiring you need atleast a 4mm cable on a 32a circuit. You can wire this cable into a comando socket if you have them available. Edited November 26, 2025 by CrootUK 2
pete Posted November 26, 2025 Posted November 26, 2025 This is one of the few times I let electricians (heavily supervised) into server rooms. (It helps that we've got certified electricians on staff.) We run a separate breaker box in the room from the main school feed with a dedicated breaker for the hard-wired UPS. Commando sockets aren't a bad shout for future-proofing (add a couple). The UPS should have come with an EPO relay that you can connect to a big red button (with mollyguard) mounted just inside the room so you can safely kill power in an emergency. 3
dhicks Posted November 26, 2025 Posted November 26, 2025 1 hour ago, AB_IT said: It requires however a hardwired connection into the back so Positive, Ground, Neutral wires to be stripped and the screwed into the back. If it doesn't have a standard "kettle lead" (IEC C13, which technically only supports up to 10A, or you sometimes see IEC C19 (16A) connectors on servers / UPS equipment) connector, as @CrootUK points out, it's probably expecting a 16A or 32A connection, possibly on a dedicated mains circuit. I would advise getting an electrician to come and get it wired in - if nothing else, they have the proper insurance. I've had one of these go wrong before - there was a loud bang and everything stopped working, which wasn't a fun day. 1
AB_IT Posted November 26, 2025 Author Posted November 26, 2025 Thanks All! So a proper electrician it is. Just a pain we'll be spending extra money out of my budget, was hoping I could save some cash lol.
Davit2005 Posted November 27, 2025 Posted November 27, 2025 13 hours ago, AB_IT said: Thanks All! So a proper electrician it is. Just a pain we'll be spending extra money out of my budget, was hoping I could save some cash lol. Honestly not worth it. An electrician will/should know if it needs a 32amp supply. Wire it into a 13amp socket and you are asking for trouble.
TomHutchinson Posted November 27, 2025 Posted November 27, 2025 13 hours ago, AB_IT said: Thanks All! So a proper electrician it is. Just a pain we'll be spending extra money out of my budget, was hoping I could save some cash lol. Think of it that everyone above have saved you money, because I recon @dhicks would have paid a lot to not have loud bangs, especially if it was anywhere near live production servers. The happy days are when all the flashy lights are still flashing 🙂
dmj Posted November 27, 2025 Posted November 27, 2025 when you say 'big'.. the last UPS we bought needed a three phase power supply, which required a three pole panel mount. I'd also strongly recommend, and a good electrician will advise putting in a bypass switch - you don't want to turn off the servers when you replace the UPS batteries. 1