lphaup Posted June 2, 2014 Posted June 2, 2014 (edited) Hi,Was wondering if anyone knew of good suppliers of industrial sized, power strips? preferably as an under-desk solution and ideally between 12-15 outlets.Thanks! Edited June 2, 2014 by lphaup
Michael Posted June 2, 2014 Posted June 2, 2014 I think the largest you'll probably find is 8 due to safety. If you had 15 sockets, it probably wouldn't be too difficult to reach the magic 3000w per outlet. An iron for example consumes in the region of 2000w on its own, but most notebooks use anywhere between 60w to 90w each. If you're plugging in desktops, it varies - it's not uncommon for a gaming PC to have a 1000w PSU.
Neil-Millgate Posted June 2, 2014 Posted June 2, 2014 Are you just after standard UK 3 pin sockets on the PDU which plugs into a standard 3 pin wall socket too?
Andrew_C Posted June 2, 2014 Posted June 2, 2014 8 is fairly easy. I'd stick two or three 8ways in; not daisy-chainned! Linky
lphaup Posted June 2, 2014 Author Posted June 2, 2014 Basically for every 8 or 9 PCs in the office, there are 3 wall ouputs, currently we are using daisy-chained extensions but due to safety looking for an alternative?
BKGarry Posted June 2, 2014 Posted June 2, 2014 We use these towers :-) Buy Masterplug 10 Socket Surge Protected Extension Lead - 2m at Argos.co.uk - Your Online Shop for Extension leads and cable reels.
Neil-Millgate Posted June 2, 2014 Posted June 2, 2014 You could go for a 15 way PDU - 15 x UK Mains Sockets L/Angled to UK Mains Plug 3Mtr. Technically they are for use in a rack but as long as you have space to mount it then shouldn't be any reason why you cannot mount it under desks. 1
Nibiru Posted June 2, 2014 Posted June 2, 2014 Hi,Was wondering if anyone knew of good suppliers of industrial sized, power strips? preferably as an under-desk solution and ideally between 12-15 outlets.Thanks! Watch your power requirements. A desktop and monitor typically draws about 3amps. So 4 computers will max out a 13A fuse. Plug more in and you are risking a fuse blowing, or a fire. It sounds like you seriously need to get an electrician in to install extra permanent sockets.
lphaup Posted June 2, 2014 Author Posted June 2, 2014 I thought about just mounting them under desks, but most of them dont have 3 pin plugs to plug into the mains socket?
PotNoodleTech Posted June 2, 2014 Posted June 2, 2014 Watch your power requirements. A desktop and monitor typically draws about 3amps. So 4 computers will max out a 13A fuse. Plug more in and you are risking a fuse blowing, or a fire. It sounds like you seriously need to get an electrician in to install extra permanent sockets. What kind of desktop and monitors are you using??? 3 amps @ 240v = 720watts - no desktop in my estate uses anywhere near that - more like a max of ~100 watts (0.4 amps) and idle 40 watts (0.16amps).
Neil-Millgate Posted June 2, 2014 Posted June 2, 2014 I thought about just mounting them under desks, but most of them dont have 3 pin plugs to plug into the mains socket? This is the range I mentioned earlier - Vertical Power Strips with UK Mains Plug | Cabinet PDU Vertical Strips | Rackmount mains distribution (PDU) | Data Comms Cabinets & Accessories | Shop By Type | Videk | Network Systems and IT Solutions It has a 3 metre lead which has the UK 3 pin plug on the end. 1
lphaup Posted June 3, 2014 Author Posted June 3, 2014 Also can anybody advise me on fuses? What will i need to do to ensure everything is up to health and safety standards?
Andrew_C Posted June 3, 2014 Posted June 3, 2014 Depends on the cable. An extension cable 1.25mm sq can be fused at 13A. It should be no longer than 12m, a 1.5mm cable can be 15m, and a 2.5mm cable 25m (but you won't want to try getting that in a 13A plug!) According to the IETs ACOP for PAT testing, appliance flex of 0.5mm fused at 3A can be as long as you like, and 1.25mm fused at 13A likewise. However, I'd be looking at other things in my RA with very long flexes. Like trip hazards...
lphaup Posted June 3, 2014 Author Posted June 3, 2014 I think we are going for a 5m, 6 socket extension, which im sure is 13a?
Andrew_C Posted June 3, 2014 Posted June 3, 2014 As long as the cable is 1.25 or 1.5mm sq that is fine. 1