We had a pretty big power surge here this morning; enought to trip out the whole of the office (which used to be an ICT Suite). It seems to have done something to our UPS (which is connected to 2 servers) in that it is dropping from 100% to very low power as soon as it begin to power the servers. Before now it has lasted a good 5+ minutes.

 

Anyone had anything like this? Could the surge have essentially "killed" the battery? There is an indication light for "replace bettery", and it's not on.

 

Pete

Posted
is it just the two servers pulling from the UPS? with Xmas coming up I'd see if you can last a week and a bit and possible move/test the UPS without endangering the Servers. Are the Servers Mission Critical?
Posted

As far as I know the battery is about 4 years old. The server are critical, they are the only 2 in the school and between them do everything we need. The UPS is charging back up, but its very slow, and seems to discharge itself in quite large amounts.

 

Perhaps its setup means it wont power the servers until it has charged a certain amount?

 

Either way, perhaps its time to look at a new one?

 

Pete

Posted
3 years is normally the most you will get out of the battery for it to hold any reasonable amount of charge. It is going flat too quickly for the battery to be flagged up as dead. During the scheduled test I would expect it to fail and power will be lost. I'm guessing its an apc?
  • 2 weeks later...
Posted

I thought I had everything covered.

I have 4 x Smart 1500's covering 5 servers all cross connected using dual redundant power supplies.

1 recently had the battery fail and the red light came on.

So I thought I would just fit a new battery.

Each of the 1500's was showing only 1 LED on it's load indicator.

 

As soon as I powered off the defective unit all the others went into overload and began bleeping frantically.

 

I was unable to release the battery from the defective unit as the sticky label had jammed it firmly in.

In less than a minute or two everything was shutting down.

 

All 4 UPS units had batteries over 3 yrs old.

 

So, UPS's LIE... Do not belive them just because the indicator says everything is ok test them regularly.

Posted
APC UPS'd tell porkies im afraid, I've never had one say its batteries are duff, when they are duff in reality. Fine maybe i've been unlucky with my 4 I've had but I just put it in my records for replacing the batteries every 3-5 years dependent on how mission critcal the units are.
Posted

Cross connected UPS is a good idea but needs regular testing.

I make a point of testing our loads every holiday period as the batteries to tend to show the wrong level of status on the front.

Be careful when replacing the batteries, I still have the scar and bruise on my foot of the last one I changed, I dropped it - not a massive height but enough to cause me not to be able to use my motorbike for a few days....