PrimaryTech Posted October 19, 2008 Posted October 19, 2008 During a recent power outage it was noted that while both our servers were connected to an APC 1000 UPS, our KVM'd monitor was not, meaning the servers could not be shut down. Power was restored before the UPS ran out of juice but now I want to add the monitor to the UPS. I spoke to a friend of mine about this and he said that it wasn't the best idea to add CRT's to a UPS as they can cause spikes and surges themselves!?! Is my friend right or am I ok to add my monitor to the UPS? Cheers in advance!
DMcCoy Posted October 19, 2008 Posted October 19, 2008 Even a 15" crt can easily overload a 1kv UPS when it turns on (although briefly) If it's on battery power, then the ups will immediately turn off to protect the battery. So, no, not a good idea 1
PrimaryTech Posted October 19, 2008 Author Posted October 19, 2008 Looks like it's hands out for a TFT/LCD then
RabbieBurns Posted October 19, 2008 Posted October 19, 2008 what about a tft? IVe got a small 15" tft plugged into my ups...
torledo Posted October 19, 2008 Posted October 19, 2008 Even a 15" crt can easily overload a 1kv UPS when it turns on (although briefly) If it's on battery power, then the ups will immediately turn off to protect the battery. So, no, not a good idea presumably you mean with other servers and equipment connected to a 1kva UPS......i don't see how the inrush current for the CRT on it's own would overload a 1kva ups. It used to be quite common for people at home to connect their PC's, printers and CRT to a small 500va ups. ALso, not sure what the thread starter means by a CRT creating spikes and surges, surey PDU's and UPS protecting equipment does the necessary power conditioning of 'dirty power' coming from the building leccy supply. I always thought the main issue with the equipment load is the inrush current required for powering up a device which can overload a UPS and it's batteries albeit momentarily.
DMcCoy Posted October 19, 2008 Posted October 19, 2008 tft should be fine, although it will still use quite a lot of power, but shouldn't overload the ups when it powers on.
DMcCoy Posted October 19, 2008 Posted October 19, 2008 presumably you mean with other servers and equipment connected to a 1kva UPS......i don't see how the inrush current for the CRT on it's own would overload a 1kva ups. It used to be quite common for people at home to connect their PC's, printers and CRT to a small 500va ups. ALso, not sure what the thread starter means by a CRT creating spikes and surges, surey PDU's and UPS protecting equipment does the necessary power conditioning of 'dirty power' coming from the building leccy supply. I always thought the main issue with the equipment load is the inrush current required for powering up a device which can overload a UPS and it's batteries albeit momentarily. I have a 1000VA here, with the server using less than 15% of the capacity. I had an old 15" crt that would cause the ups to overload briefly when it turned on. I found out it turned the ups off when overloading on battery after the power failure pop up turned the monitor on, turning the ups and server off instantly. This also occurs when bringing the monitor out of standby for a crt.
PrimaryTech Posted October 19, 2008 Author Posted October 19, 2008 I have a 1000VA here, with the server using less than 15% of the capacity. I had an old 15" crt that would cause the ups to overload briefly when it turned on. I found out it turned the ups off when overloading on battery after the power failure pop up turned the monitor on, turning the ups and server off instantly. This also occurs when bringing the monitor out of standby for a crt. I'll typically take it out of standby at least 10 times every day, so I think a tft looks like a better option. (Currently there are 2 Viglen Servers connected to the UPS)
localzuk Posted October 19, 2008 Posted October 19, 2008 I'll typically take it out of standby at least 10 times every day, so I think a tft looks like a better option. (Currently there are 2 Viglen Servers connected to the UPS) On an unrelated note - why do you use it so much? I only ever turn on the screen for our servers when there is a big emergency... Everything else is done remotely.
PrimaryTech Posted October 19, 2008 Author Posted October 19, 2008 Both servers are in the ICT suite where I spend the majority of my time, so I tend to go direct to them instead of via MSTSC. I use the servers throughout the day to check on backups, run scripts, that sort of thing...
Joedetic Posted October 19, 2008 Posted October 19, 2008 We were in this situation at one point. Our KVM wouldn't work with an LCD monitor (weird I know) so we just replaced it with a new KVM and a rackmount pull out LCD/keyboard/mouse thing.
Pete10141748 Posted October 21, 2008 Posted October 21, 2008 During a recent power outage it was noted that while both our servers were connected to an APC 1000 UPS, our KVM'd monitor was not, meaning the servers could not be shut down Configure the Power Button to Shut Down when pressed? Windows key > "U" > Enter? (for XP) Windows key > "U" > "S"> tab > tab > Enter comment > Enter? (for Server 2003) Remoting in? There are many ways to shut down the system without needing the see the screen, surely? Not meaning to be condesending here, just making some suggestions!
Butuz Posted October 21, 2008 Posted October 21, 2008 To be honest you need to revise your UPS strategy as an APC 1000 between two servers and a monitor is going to give you less than 10 mins of runtime, probably more like 5 minutes! Also you should have both your servers connected to the UPS by serial leads so that the UPS software will automatically shut the servers down.