    Recommended UK voltage settings for UPS

    We have an APC UPS 1500 which frequently trims due to reported extended over voltage issues.

    The help files tell me that to work around this I need to set the Upper Voltage to the highest setting and set the sensitivity to low.

    Sensitivity is set at low already.

    High transfer Voltage 253

    Low transfer voltage 208

    and nominal voltage 230

    I see I can set the upper voltage to 267 would there be any reason not to do this?

  2. #2
    mjs_mjs's Avatar
    Join Date
    Jan 2009
    Location
    bexleyheath, london
    Posts
    1,004
    Thank Post
    37
    Thanked 108 Times in 93 Posts
    Rep Power
    36
    all of ours are left to the defaults, had no issues like you describe. do you have an abnormal supply and have you measured your incoming supply's voltage?

  3. Thanks to mjs_mjs from:

    speckytecky (15th December 2010)

  4. #3

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,840
    Thank Post
    62
    Thanked 348 Times in 269 Posts
    Rep Power
    149
    Your nominal voltage is much more likely to be 240. The specs changed when we harmonised with Europe, not the generators and transformers. If the kit supplied by the UPS can take a 10% overload that would indicate a higher transfer of 264V as acceptable.

    As mjs writes, it would be worth checking your actual voltage. If you are near a substation, it may be higher than nominal (but still in spec) or it could even be too high. In the latter case, shout at your supplier.

  5. Thanks to Andrew_C from:

    speckytecky (15th December 2010)

  6. #4
    mjs_mjs's Avatar
    Join Date
    Jan 2009
    Location
    bexleyheath, london
    Posts
    1,004
    Thank Post
    37
    Thanked 108 Times in 93 Posts
    Rep Power
    36
    The main reasons i say check you supply voltage are that you could have a high voltage which could damage some non protected kit, or a faulty UPS which could damage kit. Do you have any other APC UPS's displaying a similar issue or not? One would assume that if your supply voltage is going high, other UPS's would display a similar characteristic.

  7. #5
    speckytecky's Avatar
    Join Date
    May 2006
    Location
    UK
    Posts
    2,404
    Thank Post
    3,221
    Thanked 245 Times in 198 Posts
    Blog Entries
    3
    Rep Power
    107
    Thanks Matt,

    We have one of the new Energy Display meters and looking at that it seems all three phases are at a steady between 246V and 248V. Next time I notice the UPS on Trim I'll have another look.

    We do have a Belkin UPS on the Admin machine and a Relios on an old server and neither of them throw up any similar problems.

    I have now changed the APC's settings to an upper of 263V and the nominal to 240V and haven't had any reports from the APC since. It is close on 3 years old so is out of warranty - any ideas of a standard life for the onboard batteries - showing green currently?

  8. #6

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,840
    Thank Post
    62
    Thanked 348 Times in 269 Posts
    Rep Power
    149
    At three years, I'd be starting to at least think of changing them. You don't need to buy from APC, but do make sure you get batteries designed to float for a long time, then deep-discharge.

    You might find that one deep-discharge now will kill them.

  9. Thanks to Andrew_C from:

    speckytecky (16th December 2010)

SHARE:
+ Post New Thread

Similar Threads

  1. Switching PCs to US Voltage
    By BJG in forum General Chat
    Replies: 2
    Last Post: 10th September 2010, 02:52 PM
  2. Laptop Voltage Q
    By Haux in forum Netbooks, PDA and Phones
    Replies: 2
    Last Post: 22nd December 2009, 04:10 PM
  3. Low 3.3 voltage in bios
    By FatBoy in forum Hardware
    Replies: 3
    Last Post: 12th March 2009, 01:23 PM
  4. PSU Voltage Switch Nightmare
    By Lee_K_81 in forum Hardware
    Replies: 15
    Last Post: 26th February 2007, 03:24 PM
  5. Dell Optiplex Voltage Stepper Change Prevention
    By DaveP in forum How do you do....it?
    Replies: 2
    Last Post: 22nd November 2006, 08:12 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •