Hi guys,

 

Late call from the power company saying they need to come in and cut the power to building for up to a 8 hours. The UPS will not last that long. Long story short, we cannot let one of the oldest servers go down (in fear of it not coming back up again...).

 

So, I was wondering if anybody here has previously (and successfully) run the Smart-UPS 5000VA rack mount on a genie? If so, what did you get and where from?

 

Ta in advance...

 

Ben

Posted

A 6kW generator will cost you around £1,300. Make sure you ventilate well, or protect it from the weather if outside.

 

SDMO SH 6000-2 UK 6kW Generator 115/230V | Screwfix.com

 

The '8 hour' run time listed is because you (technically) have to turn it off to refuel the 20 litre tank. Obviously the UPS can handle the load while you do this.

 

Alternatively you could hire a generator. You'll get more bang for your buck this way unless you need it for an extended period of time.

 

Diesel Generator (10kva Silenced) Hire | HSS Hire

 

Also check you are insured the handle heavy plant. If you aren't your site supervisor might be.

Posted

Excrement, thank you Geoff.

 

I think we'll just hire this time round (with a view to buy as we are very rural). I was worried about it being dirty power, but reading the interweb now I can see the Smart-UPS should be able to deal with the fluctuations better than a non-Smart. Fingers crossed...

 

Ta

Posted
If you are going to buy a generator practice the switch over procedure ahead of time, keep a decent supply of fuel on site, and test the generator regularly.
Posted
Have a chat with Borri, they did the install at my last place, generator and UPS too. I ended up over specifying it all and it was enough power to power the whole site for 2 or 3 days!!
Posted

WATCH OUT!!

 

If you don't load a generator sufficiently, you can upset the voltage regulator and get a very poor output. Hanging a single bar heater on it would do.

 

50Hz is UK standard, but this will suffer if the VR isn't working.

Posted
No. The UPS is rated to deliver UP TO 4kW. With only one server hanging on it, I'd guess you would be pulling a few 10s / low 100s of watts. Talk to your suppliers, and explain what you are doing. They should be able to advise.
Posted

Yes the best way to do this is to run on UPS for a few minutes to drain the UPS batteries a little (10-25% depending on capacity). You then want to start up the generator. DO NOT have everything plugged in at start-up, you don't want to load the generator straight away. Simpy plug in the UPS once the generator is running and has settled down.

 

If in doubt read the manual. :)

Posted

Maybe i've got this wrong then.

 

I spoke to APC and they said the generator needs to provide 1.5 to 2 times the FLC. The FLC for that UPS is 4000w. The UPS is saying the current Load Power is 35.7 %Watts and the Apparent Load Power is 33.8 %VA. This is with 10 servers running plus some network gear.

Posted
Yes the best way to do this is to run on UPS for a few minutes to drain the UPS batteries a little (10-25% depending on capacity). You then want to start up the generator. DO NOT have everything plugged in at start-up, you don't want to load the generator straight away. Simpy plug in the UPS once the generator is running and has settled down.

 

If in doubt read the manual. :)

 

Ok right, well this is exactly what I was going to do. Phew, I was doubting myself there (not unusual).

Posted

Sorry. I'd read it as "I'm only going to keep one server up", rather than "I can't let one of them stop".

 

In that case, yes, generator bigger than your UPS.

Posted
Sorry. I'd read it as "I'm only going to keep one server up", rather than "I can't let one of them stop".

 

In that case, yes, generator bigger than your UPS.

 

Sorry, I should have made that clearer.

 

Just ordered for delivery tomorrow, £100 per week (big saving on HSS) from a local firm MJHire - Home

Posted (edited)

Just an update. The test run was successful.

 

Generator on for 5 minutes to warm up

UPS unplugged from the mains supply for 5 minutes to deplete a bit. Email received from UPS to say no longer on mains power.

UPS plugged in to generator. Email received to say UPS is back on mains power and LED on unit indicate as such

 

Bingo bango. Fingers crossed it carries on over a prolonged period (extra fuel on hand just in case)

Edited by Ben_Stanton