We're planning to move office, there's one rather large snag however. The previous occupant in a fit of malice decided to cut all of the electrical, telephony and data cabling before they left. The power and telephony have obviously been fixed at the landlord/service providers expense however fixing the internal network cabling has fallen to us. On cursory inspection the situation doesn't look too bad, The cables all come into one room and have been cut where they come under the floor into the room (presumably where the comms cabinet was). There's no extra play in the cabling so I can't simply pull more length in. What is the most cost effective way to fix this? Our current comms contractor wants to recable the entire building at considerable cost.
Posted
Whilst I have no doubt that there is a way to patch (no pun intended) snipped cables inline, I would suggest that it probably wouldn't do the signal quality any favours. It may be best for a complete re-wiring tbh.
Posted (edited)

Wire up 2 sets patch panels under the floor, one set to terminate the old cabling, and another set to terminate your new extensions. Then connect the two together with patch cables.

 

It won't be pretty, but it should work and it will be relatively cheap. If you have (or can rent) a high-end cable tester it will be able to verify if the cabling is still up to standard with the extra patches.

Edited by AngryTechnician
Posted
We're planning to move office, there's one rather large snag however. The previous occupant in a fit of malice decided to cut all of the electrical, telephony and data cabling before they left. The power and telephony have obviously been fixed at the landlord/service providers expense however fixing the internal network cabling has fallen to us. On cursory inspection the situation doesn't look too bad, The cables all come into one room and have been cut where they come under the floor into the room (presumably where the comms cabinet was). There's no extra play in the cabling so I can't simply pull more length in. What is the most cost effective way to fix this? Our current comms contractor wants to recable the entire building at considerable cost.

 

Could the Comms cabinet be moved to where the cable is able to be pulled back to? Might end up sitting outside the comms room though.

Posted
Could the Comms cabinet be moved to where the cable is able to be pulled back to? Might end up sitting outside the comms room though.

 

That location is not ideal for a 42U rack as it is a corridor.

Posted
The couplers work alright, just terminate the cut cables in a normal 8P8C connector and carry on from there. Not ideal, maybe, but they've worked alright here in the couple of places we've needed to move a socket 10m in the old part of the building.
Posted

I would suggest coming to a deal with the landlord. If you use couplers, you will need 154 which is expensive and dodgy as hell. If you re-cable, it is expensive but you get nice new, certified, points.

 

I would suspect that you should give serious consideration to finding other premises as an option... and let the landlord know that fact.