    APC UPS daily reports overvoltage issue

    Our APC 1500 with Power Chute software daily reports that it has experienced over voltage issues. I have carried out the recommendations on settings but still no success. Anyone else having similar events and if so have and how have you resolved the issue please?

  2. #2


    tom_newton's Avatar
    Join Date
    Sep 2006
    Location
    Leeds
    Posts
    4,463
    Thank Post
    866
    Thanked 845 Times in 667 Posts
    Rep Power
    195
    a) yes
    b) we routinely ignore it

  3. Thanks to tom_newton from:

    speckytecky (3rd March 2009)

  4. #3

    Join Date
    May 2007
    Location
    Bradford
    Posts
    71
    Thank Post
    1
    Thanked 3 Times in 3 Posts
    Rep Power
    16
    I ignore it too, shame you cant turn the email alert off.

  5. Thanks to rasssp from:

    speckytecky (3rd March 2009)

  6. #4

    Join Date
    May 2007
    Location
    Suffolk
    Posts
    145
    Thank Post
    2
    Thanked 19 Times in 17 Posts
    Rep Power
    18
    When you say you have carried out the recommendations on settings, do you mean you have adjusted the sensitivity by pressing the button on the back?

    Green light bright - high sensitivity.

    Green light medium - middle

    Green light dull - low.

    It should basically reduce the tendency for the UPS to send alerts every time it THINKS it is heading for an over-voltage / under-voltage.

    Yet will still alert you if it goes over for an extended period.

    The button is on the back of the case near the top, with its indicator light next to it.

    Sorry if you have already done that, the next step would be to re-configure to disable messages. You will know soon enough when the server shuts down and you at least know the system well enough to check it daily using the APC console.

  7. 2 Thanks to Polski:

    speckytecky (3rd March 2009), tom_newton (3rd March 2009)

  8. #5

    Join Date
    May 2007
    Location
    Suffolk
    Posts
    145
    Thank Post
    2
    Thanked 19 Times in 17 Posts
    Rep Power
    18
    I have enclosed the web link this time.

    http://www.apcmedia.com/salestools/A...9KQK_R0_EN.pdf

    See page 8 for the diagram.

  9. Thanks to Polski from:

    speckytecky (3rd March 2009)

  10. #6

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,961
    Thank Post
    64
    Thanked 374 Times in 284 Posts
    Rep Power
    158
    Have you actually checked that the supply isn't over voltage? This can happen especially if you are near the sub-station feeding a long line. The voltage is set high so that by the end of the line the drop doesn't leave the distant consumers on a low voltage. The supply should be 230v ±10%.

  11. Thanks to Andrew_C from:

    speckytecky (4th March 2009)

  12. #7
    speckytecky's Avatar
    Join Date
    May 2006
    Location
    UK
    Posts
    2,497
    Thank Post
    3,372
    Thanked 256 Times in 209 Posts
    Blog Entries
    3
    Rep Power
    109
    Quote Originally Posted by Andrew_C View Post
    Have you actually checked that the supply isn't over voltage? This can happen especially if you are near the sub-station feeding a long line. The voltage is set high so that by the end of the line the drop doesn't leave the distant consumers on a low voltage. The supply should be 230v ±10%.
    Thanks for the suggestion but what would I need kit wise and how would I set about checking that please.

  13. #8

    Ric_'s Avatar
    Join Date
    Jun 2005
    Location
    London
    Posts
    7,590
    Thank Post
    109
    Thanked 762 Times in 593 Posts
    Rep Power
    180
    Quote Originally Posted by speckytecky View Post
    Thanks for the suggestion but what would I need kit wise and how would I set about checking that please.
    A big multimeter

    I know that my UPS units tell me how much voltage they are getting - you can then specify a number as the 'normal' voltage.

  14. Thanks to Ric_ from:

    speckytecky (4th March 2009)

  15. #9

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,961
    Thank Post
    64
    Thanked 374 Times in 284 Posts
    Rep Power
    158
    A multimeter is indeed what you need. It should have fused probes for working on mains.

    However, I just checked that I was right on my 10% figure, and find that there has been another fudge.
    European Voltage Harmonisation

    The United Kingdom for many years had a standardised supply voltage of 240V ±6% (415V for three-phase) whereas continental Europe had a nominal supply level of 220V (380V). From 1 January 1995 the nominal voltage across Europe has been ‘harmonised’ at 230V/400V.

    <SNIP>

    Plans to harmonise the whole of Europe to 230V ±10% (i.e. 207 - 253V), which were due to be applied from 1st January 2003, were first postponed until 1st January 2008 and are now postponed indefinitely pending a consensus between the various parties.
    For more reading chick here.

  16. Thanks to Andrew_C from:

    speckytecky (4th March 2009)

  17. #10

    m25man's Avatar
    Join Date
    Oct 2005
    Location
    Romford, Essex
    Posts
    1,625
    Thank Post
    49
    Thanked 455 Times in 335 Posts
    Rep Power
    137
    Do you have an AP9617 installed?
    The detailed logs will show the voltage at given times and might offer a clue to a trend that is outside of your control.
    At one site we look after the input voltage drops steadily from 09:00 until 13:00 as the kitchens get busy then after lunch is over it begins to increase until the APC is trimming until home time.

    Another time we found a laminator had been plugged into a PDU meant for the switches FFS!!

  18. Thanks to m25man from:

    speckytecky (12th March 2009)

  19. #11

    Join Date
    Jun 2007
    Posts
    4
    Thank Post
    0
    Thanked 2 Times in 2 Posts
    Rep Power
    0
    We had similar issues, the volts were over 250 because we were right next to the distribution board (incoming feed) and its sometimes necessary to be raised because of transmission / volt loss over the building (or at the sub depending on distance)- the other end of our building was lower than 220v!

    Ask your facilities manager to check which electrical distribution board you're on - we were jointly on the kitchen one which had fluctuations everytime the fridges, cookers and the like came on which was a real pain.

    We're on a seperate board now and although still some smart trimming there are much less power related events.

    Edit: your PAT testers should be able to check your volts out when they do their annual checks

  20. Thanks to Drax from:

    speckytecky (12th March 2009)

  21. #12

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,961
    Thank Post
    64
    Thanked 374 Times in 284 Posts
    Rep Power
    158
    Quote Originally Posted by Drax View Post
    Edit: your PAT testers should be able to check your volts out when they do their annual checks
    I wouldn't rely on that. Some PATers are monkeys who have been taught which button to press when. They wouldn't know the difference between a Volt and an Amp if it bit them. Nor would PATers necessarily have a meter to measure your line voltage. Their tester MAY indicate the supply voltage when plugged in.

  22. #13

    Join Date
    Jun 2007
    Posts
    4
    Thank Post
    0
    Thanked 2 Times in 2 Posts
    Rep Power
    0
    Quote Originally Posted by Andrew_C View Post
    I wouldn't rely on that. Some PATers are monkeys who have been taught which button to press when. They wouldn't know the difference between a Volt and an Amp if it bit them. Nor would PATers necessarily have a meter to measure your line voltage. Their tester MAY indicate the supply voltage when plugged in.
    Yeh true enough with a number of them- we do use a select number of companies for elec's - you need someone you know will do a good job and has the kit.

  23. #14
    speckytecky's Avatar
    Join Date
    May 2006
    Location
    UK
    Posts
    2,497
    Thank Post
    3,372
    Thanked 256 Times in 209 Posts
    Blog Entries
    3
    Rep Power
    109
    Quote Originally Posted by Drax View Post
    We had similar issues, the volts were over 250 because we were right next to the distribution board (incoming feed) and its sometimes necessary to be raised because of transmission / volt loss over the building (or at the sub depending on distance)- the other end of our building was lower than 220v!

    Ask your facilities manager to check which electrical distribution board you're on - we were jointly on the kitchen one which had fluctuations everytime the fridges, cookers and the like came on which was a real pain.

    We're on a seperate board now and although still some smart trimming there are much less power related events.

    Edit: your PAT testers should be able to check your volts out when they do their annual checks
    Thanks Drax,

    We are a fairly new build and I'm told that the supply to the ICT suite is filtered.

  24. #15

    synaesthesia's Avatar
    Join Date
    Jan 2009
    Location
    Northamptonshire
    Posts
    5,888
    Thank Post
    575
    Thanked 1,001 Times in 773 Posts
    Blog Entries
    15
    Rep Power
    461
    Had this at one of my schools but it was only in the 3phase juiced server rack it was situated in. Went straight into a normal mains socket (not ideal but will help until we can find a lower rated cabinet busbar) and we're all sorted. The busbar in use currently outputs at 253-255v on average :/

SHARE:
+ Post New Thread

Similar Threads

  1. APC UPS clicking constantly
    By ChrisH in forum Hardware
    Replies: 9
    Last Post: 10th April 2011, 01:13 PM
  2. APC Smart UPS 5000
    By jcs808 in forum Hardware
    Replies: 4
    Last Post: 23rd July 2008, 09:50 PM
  3. APC UPS
    By davyboi in forum General Chat
    Replies: 3
    Last Post: 23rd January 2008, 11:42 AM
  4. APC UPS Help
    By Ste_Harve in forum Hardware
    Replies: 4
    Last Post: 12th September 2007, 11:26 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •