    Installing underground Cat5e cable

    Hi all,

    i have been asked about connecting a nursery classroom to the network at a primary School i work at, the building is roughly 25 - 30 feet away from the main school. it is currently connected through wireless but has a poor signal and tends to not work very well.

    it now seems that the fire alarm is to be upgraded on the building and there will be a trench dug up to install new wiring, i was quickly told by the Head on Friday to think about throwing a Cat5e cable in so we could connect them up.

    i was thinking of running External grade Cat5e inside some Polypropylene Conduit as the cheapest option, does anyone know if there is any other factors i should think about?

    not sure if there are any earth potential risks (lightening strikes) or fire risks, any advice would be much appreciated.

    Cheers

  2. #2

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    15,843
    Thank Post
    876
    Thanked 1,679 Times in 1,459 Posts
    Blog Entries
    12
    Rep Power
    444
    Yep bit of cat 5e in plastic piping should do the trick. Nice and cheap there is no need for fibre as it’s so close. You can get armoured cat 5e cable you should consider that.

    I am tempted to say get cat 6 so your feature proofed, it won’t be as easy to upgrade it underground.

  3. #3

    SimpleSi's Avatar
    Join Date
    Jun 2005
    Location
    Lancashire
    Posts
    5,809
    Thank Post
    1,476
    Thanked 592 Times in 444 Posts
    Rep Power
    168
    Remember to run at least 2 cables so if one fails you still stand a chance

    regards

    Simon

  4. 2 Thanks to SimpleSi:

    amfony (16th June 2008), FN-GM (15th June 2008)

  5. #4

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    15,843
    Thank Post
    876
    Thanked 1,679 Times in 1,459 Posts
    Blog Entries
    12
    Rep Power
    444
    Quote Originally Posted by SimpleSi View Post
    Remember to run at least 2 cables so if one fails you still stand a chance

    regards

    Simon
    Very good point

  6. #5

    beeswax's Avatar
    Join Date
    Jul 2005
    Location
    England
    Posts
    2,285
    Thank Post
    285
    Thanked 225 Times in 153 Posts
    Rep Power
    131
    I worked at a place which had the cable slung from roof to roof, which was fine until you had a couple of hot days an the cable stretched and sagged some. Wagon deliveries had to be handled very carefully so they didn't bring down the cable.

  7. #6


    Join Date
    Oct 2006
    Posts
    3,411
    Thank Post
    184
    Thanked 356 Times in 285 Posts
    Rep Power
    148
    You could also run some string through so that should you want to put any more cables through you have something to pull them through with.

  8. #7

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,652
    Thank Post
    516
    Thanked 2,443 Times in 1,891 Posts
    Blog Entries
    24
    Rep Power
    831
    Personally, I'd either install OM3 fibre or some cat6 cable rather than cat5e. Future proofing and all that. And at that length, an install shouldn't cost a lot either.

  9. #8

    maniac's Avatar
    Join Date
    Feb 2007
    Location
    Kent
    Posts
    3,037
    Thank Post
    209
    Thanked 425 Times in 306 Posts
    Rep Power
    144
    If they do it properly then the ducting they install for the firealarm should be bigger than needed diameter, both ends should be accessible, and there should be a pull cord left in place so any contractors or yourself can put in more cables in the future, save digging up the ground all over again.

    I would use as a minimum a good quality external grade cat5 cable, or if finances allow use armoured cat5 cable as mentioned above. If installed properly the outer 'armour' can be (and should be) earthed, which can cut down on possible interference from any other cables that might share the ducting either now or in the future. The only problem with the armoured cable is it is expensive, but in the long term it is worth it, as the last thing you want to have to do is change it because it's been severed at some point along its route. Also as said above, run two or preferably more cables while you have the opportunity.

    Mike

  10. #9
    scottyses's Avatar
    Join Date
    Dec 2007
    Location
    Stamford, Lincolnshire
    Posts
    39
    Thank Post
    0
    Thanked 1 Time in 1 Post
    Rep Power
    0
    The only problem is earth leakage between building you will need to get your sparkies opinion!

  11. #10

    Join Date
    Apr 2008
    Location
    Sheffield
    Posts
    21
    Thank Post
    0
    Thanked 2 Times in 2 Posts
    Rep Power
    13
    Quote Originally Posted by maniac View Post
    If they do it properly then the ducting they install for the firealarm should be bigger than needed diameter, both ends should be accessible, and there should be a pull cord left in place so any contractors or yourself can put in more cables in the future, save digging up the ground all over again.
    I'd be highly annoyed if someone did that to a fire alarm link I'd just installed for several reasons, possibly including but not limited to - alterations to the calculated spacing factors of the containment, damage to the fire alarm cables and segregation of cables. Easiest way is to drop a seperate duct in the trench solely for data cabling between the buildings, saves future buck passing and is actually future proof as cat6 or fibre isn;t really future proof as such, just a bit less non-future proof than cat5e.

    Quote Originally Posted by maniac View Post
    I would use as a minimum a good quality external grade cat5 cable, or if finances allow use armoured cat5 cable as mentioned above. If installed properly the outer 'armour' can be (and should be) earthed, which can cut down on possible interference from any other cables that might share the ducting either now or in the future. The only problem with the armoured cable is it is expensive, but in the long term it is worth it, as the last thing you want to have to do is change it because it's been severed at some point along its route. Also as said above, run two or preferably more cables while you have the opportunity.
    As mentioned previously, before connecting earths together between buildings have a word with the electricians looking after the site as exporting earths via the armouring of a cat5 cable can be very dangerous if done incorrectly and can make things worse. There are correct ways to earth armourings.

  12. #11

    Join Date
    May 2008
    Location
    Leeds
    Posts
    26
    Thank Post
    4
    Thanked 3 Times in 3 Posts
    Rep Power
    13
    Many Thanks all,

    some really good points in there, giving me a lot to think about. Looks like ive got some cables to price up.

    Cheers for your all input.

  13. #12

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,622
    Thank Post
    1,240
    Thanked 777 Times in 674 Posts
    Rep Power
    235
    Quote Originally Posted by YorkshireTechie View Post
    I was quickly told by the Head on Friday to think about throwing a Cat5e cable in so we could connect them up.
    I'm no expert on this myself, but for our new building (also having a cable for fire alarms connected to it, like yours) we're having fibre installed - just a length of pre-terminated cable, costs around 200 for 75M (I think), and that was for 8 strands. Admittedly you'll need switches at either end capable of taking fibre links, but heck, you'll need switches of some kind anyway, and fibre capability doesn't add much these days (our 24-port, gigabit, fibre-capable switches were 300). You'll also need GBIC modules for the fibre connections and (seemingly) a fibre patch panel (around 20-ish, if I remember).

    --
    David Hicks

  14. #13

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    15,843
    Thank Post
    876
    Thanked 1,679 Times in 1,459 Posts
    Blog Entries
    12
    Rep Power
    444
    This kind of situation myself I would keep it as simple as possible.

  15. #14
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    47
    Quote Originally Posted by FN-Greatermanchester View Post
    This kind of situation myself I would keep it as simple as possible.
    yes, but theres no such thing as simple when you advocate copper inter-building in order to save costs....as someone else has said when you start using any kind of shielded or armoured cat5e/cat6 cable you need to make sure you maintain equipotential between buildings, i believe that both the buildings inspector and fire inspector will have something to say about an installation that could a) be a potential fire risk b) not meet the required standards for bonding of telecommunications equipment.

    using flexible conduit and suitable rated cable for the task is fine, but it doesn't protect against lightning strike and what an installer will need to avoid is a ground loop.

    much easier and better ROI if TS were to go with fibre....once you start talking about using armoured cable, the cost difference between that and pre-terminated fibres isn't a great deal. Plus fibre means you don't have to worry about transient voltage and you've got plenty of capacity for future expansion.

    it's a no-brainer.

  16. #15

    broc's Avatar
    Join Date
    Jan 2006
    Location
    England
    Posts
    2,046
    Thank Post
    104
    Thanked 401 Times in 265 Posts
    Rep Power
    150
    I agree with torledo, if you do the job professionally (rather than just string a length of CAT5E in ordinary polythene conduit) then the cost differences between fibre & copper are less than you might imagine.

    We linked to our sports hall via fibre a few years ago, having looked at wireless point-to-point, copper cable & fibre. It also had the advantage we gained spare bandwidth & were able to use the sports hall as an 'offsite' DR location for backups. When we installed long-term temporary classrooms last year we installed fibre there too while they were digging a trench for power/alarm systems.

SHARE:
+ Post New Thread
Page 1 of 3 123 LastLast

Similar Threads

  1. Cat5e cable: UTP/FTP/STP?
    By eean in forum Wireless Networks
    Replies: 11
    Last Post: 15th June 2009, 01:16 PM
  2. Cat5e and Cat6
    By HodgeHi in forum Wireless Networks
    Replies: 12
    Last Post: 12th April 2008, 05:17 PM
  3. London underground dinner party
    By eduabncs in forum Jokes/Interweb Things
    Replies: 6
    Last Post: 31st August 2007, 11:15 PM
  4. Burlington, Wiltshire's Underground City
    By webman in forum General Chat
    Replies: 3
    Last Post: 5th June 2006, 11:56 AM
  5. Going underground
    By Dos_Box in forum General EduGeek News/Announcements
    Replies: 9
    Last Post: 16th December 2005, 10:17 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •