    Is my UPS dead?

    My big APC UPS has tripped twice now.

    We have the builders in. They've patched in the two circuits that the servers use, and the power is flowing through. Though they're still working on the distribution board.

    The UPS won't power on with all devices attached. No problem... switch a few off and it comes up. Very noisily though.

    I don't know if this is a sign of the UPS being on it's last legs or something dicky with the power feed.

    Anybody have any experience of this??

  2. #2

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    12,963
    Thank Post
    586
    Thanked 1,494 Times in 1,340 Posts
    Rep Power
    397

    Re: Is my UPS dead?

    If it's noisy that doesn't sound good and from those symptoms does sound as if it's knackered but I wouldn't like to give a final answer until you have your power all sorted and they've stopped playing with it.

    It could also be that the batteries are on their last legs and need replacing it should have a light to tell you this though.

    Ben

  3. #3
    mark's Avatar
    Join Date
    Jun 2005
    Posts
    3,943
    Thank Post
    230
    Thanked 48 Times in 44 Posts
    Blog Entries
    2
    Rep Power
    45

    Re: Is my UPS dead?

    Thanks Ben

    Yeah - the indicator lights look as they usually do. The 'regulating excess power' light is lit but it's always said that.

    Gotta see if it still plays up when the sparky is finished, though the job wont finish for a fair few months now.

  4. #4

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    12,963
    Thank Post
    586
    Thanked 1,494 Times in 1,340 Posts
    Rep Power
    397

    Re: Is my UPS dead?

    If it is always regulating a higher than normal power supply then I suppose that could be a reason for it failing prematurely APC may be able to give you a better answer on that one.

    New batteries aren't too expensive.

    Ben

  5. #5

    Join Date
    Jul 2005
    Location
    Blackburn, Lancashire
    Posts
    123
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: Is my UPS dead?

    Be careful

    This is what happened to one of ours recently.

    And look at what happened to the poor old powerbook nearby!!!
    Attached Images Attached Images

  6. #6

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    12,963
    Thank Post
    586
    Thanked 1,494 Times in 1,340 Posts
    Rep Power
    397

    Re: Is my UPS dead?

    Thats not a UK ups is it?

    Ben

  7. #7

    Join Date
    Jul 2005
    Location
    Blackburn, Lancashire
    Posts
    123
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: Is my UPS dead?

    It was in the US.

  8. #8

    Ric_'s Avatar
    Join Date
    Jun 2005
    Location
    London
    Posts
    7,582
    Thank Post
    107
    Thanked 761 Times in 592 Posts
    Rep Power
    179

    Re: Is my UPS dead?

    Does the handy software/web interface not give you any clues? (or isn't it a SmartUPS?)

  9. #9
    mark's Avatar
    Join Date
    Jun 2005
    Posts
    3,943
    Thank Post
    230
    Thanked 48 Times in 44 Posts
    Blog Entries
    2
    Rep Power
    45

    Re: Is my UPS dead?

    It is a SmartUPS Ric a 2200 - i'll take a look on monday. Plus i might give APC a call.

  10. #10

    john's Avatar
    Join Date
    Sep 2005
    Location
    London
    Posts
    10,439
    Thank Post
    1,468
    Thanked 1,035 Times in 908 Posts
    Rep Power
    299

    Re: Is my UPS dead?

    Mine sounds like a Mr whippy machine when you start it up it goes "boof" and "bang" and then "bleep bleep bleep" (its a 3000VA smart rackmount one) it also shakes when it kicks in and blows the main disty board (but thats down to it being over used (it says 121% usage, run time -3 minutes, and yes it did show the - the other day!) So I have taken 2 proliants off it and its now just over 100%. But I would give APC a call, they were very useful last time I had dealings with them

  11. #11
    DMcCoy's Avatar
    Join Date
    Oct 2005
    Location
    Isle of Wight
    Posts
    3,386
    Thank Post
    10
    Thanked 483 Times in 423 Posts
    Rep Power
    110

    Re: Is my UPS dead?

    Quote Originally Posted by john
    Mine sounds like a Mr whippy machine when you start it up it goes "boof" and "bang" and then "bleep bleep bleep" (its a 3000VA smart rackmount one) it also shakes when it kicks in and blows the main disty board (but thats down to it being over used (it says 121% usage, run time -3 minutes, and yes it did show the - the other day!) So I have taken 2 proliants off it and its now just over 100%. But I would give APC a call, they were very useful last time I had dealings with them
    I would be very careful when loading ups, the reason they have the limit is so that you don't draw too much power from the battery if it switches to battery mode. If you overload an apc when its in battery mode it will shut down immediatly - losing all power! I guess if you draw too much for too long, they get hot, then they build up gases in a enclosed metal case without room for expansion, worst case is it explodes!

  12. #12

    john's Avatar
    Join Date
    Sep 2005
    Location
    London
    Posts
    10,439
    Thank Post
    1,468
    Thanked 1,035 Times in 908 Posts
    Rep Power
    299

    Re: Is my UPS dead?

    It does shut off in 1 or 2 minutes, so I have to be very fast at typing as well as running to the other end of the building to get to them, it is due for change though so I am not too worried. Its not showing overload on its status now, as its only something like 3 or 4 % overloaded so its not warning overload now, so its better than it was, I think the main thing is never underestimate the power of a Proliant server, those Rackmount ones are beasts for power compaired to the tower ones.

    We have just started getting the pricing in for a big APC Symetra setup (looking around £10K) to be able to run them for a few hours in a power failure as we have 2 staff areas (SMT offices and Finance Dept) on huge UPS's so the PCs there will run for a good few hours as well as the phone system so if we can keep the back end running then they can keep working.

    Just need to get our office on a UPS now, then we can have phones that work in a power failure as well, blasted VOIP phones that are not POE powered, it means I am not contactable (I cannot decide if thats a good thing or a bad thing)

  13. #13

    ZeroHour's Avatar
    Join Date
    Dec 2005
    Location
    Edinburgh, Scotland
    Posts
    5,571
    Thank Post
    869
    Thanked 1,293 Times in 786 Posts
    Blog Entries
    1
    Rep Power
    436

    Re: Is my UPS dead?

    Turner please explain how in the hell that happened as its well scary

  14. #14

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,800
    Thank Post
    110
    Thanked 582 Times in 503 Posts
    Blog Entries
    1
    Rep Power
    223

    Re: Is my UPS dead?

    Its a lead acid battery. It overheats. The acid vapourises. The battery explodes. Hot acid everywhere.

  15. #15

    webman's Avatar
    Join Date
    Nov 2005
    Location
    North East England
    Posts
    8,372
    Thank Post
    624
    Thanked 949 Times in 651 Posts
    Blog Entries
    2
    Rep Power
    317

    Re: Is my UPS dead?

    Quote Originally Posted by Geoff
    Its a lead acid battery. It overheats. The acid vapourises. The battery explodes. Hot acid everywhere.
    Definately one of those "stand well back" moments As in, stand well back in another country

SHARE:
+ Post New Thread

Similar Threads

  1. Is it dead then?
    By plexer in forum BSF
    Replies: 4
    Last Post: 16th October 2007, 11:05 AM
  2. Laptop Dead???
    By DSapseid in forum Hardware
    Replies: 2
    Last Post: 15th August 2007, 12:04 AM
  3. Dead Web Server :(
    By plexer in forum Hardware
    Replies: 3
    Last Post: 19th April 2007, 02:21 PM
  4. motherboard dead?
    By chrbb in forum Hardware
    Replies: 7
    Last Post: 11th December 2006, 09:08 PM
  5. It's back from the dead!!!! YAY!!!
    By Dos_Box in forum General Chat
    Replies: 5
    Last Post: 13th December 2005, 12:39 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •