    ups

    do people put there backbone switches on ups supply at moment we have server on there was thinking of adding at least router and one of switches on so that it can notify me when there is a problem etc...

    russ

  2. #2


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,650
    Thank Post
    275
    Thanked 780 Times in 607 Posts
    Rep Power
    224

    Re: ups

    Yup, but we did it to improve reliability - power round here goes down regularly.

  3. #3

    Join Date
    Nov 2005
    Location
    Middlesbrough
    Posts
    402
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: ups

    Yes, I have all our core switches on UPS in case of power failure. This allows me to recieve an email/sms to tell me about the problem. We host websites/media for various people and I need to know if there's going to be any downtime!

  4. #4

    russdev's Avatar
    Join Date
    Jun 2005
    Location
    Leicestershire
    Posts
    6,930
    Thank Post
    709
    Thanked 552 Times in 367 Posts
    Blog Entries
    3
    Rep Power
    204

    Re: ups

    by bye

    how do you get ti to send sms

    russ

  5. #5

    Join Date
    Nov 2005
    Location
    Middlesbrough
    Posts
    402
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: ups

    Our sms supplier provides us with an email to sms gateway

  6. #6

    russdev's Avatar
    Join Date
    Jun 2005
    Location
    Leicestershire
    Posts
    6,930
    Thank Post
    709
    Thanked 552 Times in 367 Posts
    Blog Entries
    3
    Rep Power
    204

    Re: ups

    git was hoping found some free way of doing it



    russ

  7. #7

    russdev's Avatar
    Join Date
    Jun 2005
    Location
    Leicestershire
    Posts
    6,930
    Thank Post
    709
    Thanked 552 Times in 367 Posts
    Blog Entries
    3
    Rep Power
    204

    Re: ups

    thinking of getting a cheap ups for boxes etc what sort of pwoer does ups need for about 4 switches a router p;us few other bits

    russ

  8. #8
    ChrisH's Avatar
    Join Date
    Jun 2005
    Location
    East Lancs
    Posts
    4,987
    Thank Post
    120
    Thanked 283 Times in 261 Posts
    Rep Power
    107

    Re: ups

    Try the calculator on the APC site it does specific products or loads to tell you what UPS you need.

    http://www.apc.com/tools/ups_selecto...UPS%20Selector

  9. #9

    Join Date
    Aug 2005
    Location
    Birmingham, UK
    Posts
    490
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: ups

    If you are feeling brave, check the power consumption of each unit (in Watts), add them all together. Then compare the result and the maximum running load of the UPS (usually quoted in VA).

    VA is slightly different from W so a 1500VA UPS and you have to use power factor corrections (which differ from device to device) The industry standard however is around 60% i believe.

    To safely spec a UPS, i would reccommend using the calculator above but if you must do it the hard way, multiply the wattage by 1.6 to give the size of the UPS required

    Switches pull 25-50W each, routers and adsl modems (small ones) pull around 20W each, rackmount probably pull some more. From the hardware you mentioned i would put them on a 1000VA unit for decent coverage and some room for expansion.

  10. #10

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224

    Re: ups

    Remeber if your using rackmounts + aircon you need some way of keeping the aircon going while the servers shut down. Due to the horrific power requirements of aircon that usually means a generator.

  11. #11

    russdev's Avatar
    Join Date
    Jun 2005
    Location
    Leicestershire
    Posts
    6,930
    Thank Post
    709
    Thanked 552 Times in 367 Posts
    Blog Entries
    3
    Rep Power
    204

    Re: ups

    arcon whats that

    russ

  12. #12

    webman's Avatar
    Join Date
    Nov 2005
    Location
    North East England
    Posts
    8,407
    Thank Post
    640
    Thanked 961 Times in 661 Posts
    Blog Entries
    2
    Rep Power
    326

    Re: ups

    We have 4 beige SmartUPS 700s at the moment powering our main servers, which will soon be replaced with a huge rackmount UPS for all of them Then we will distribute the small UPSs around the switches.

    When/If we get the money 8O

  13. #13

    Join Date
    Aug 2005
    Location
    Birmingham, UK
    Posts
    490
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0

    Re: ups

    Quote Originally Posted by Geoff
    Remeber if your using rackmounts + aircon you need some way of keeping the aircon going while the servers shut down. Due to the horrific power requirements of aircon that usually means a generator.
    True, but for the short amount of time you want to keep the systems up for, it shouldnt be a problem(ie 5-10 mins).

    Also i wouldnt rely on the UPS to keep the systems up for more than a minimal amount of time, id more look at them for power conditioning (ie brownout and overvolt protection) and to perform graceful shutdowns.

  14. #14
    tarquel's Avatar
    Join Date
    Jun 2005
    Location
    Powys, Mid-Wales, UK
    Posts
    1,740
    Thank Post
    13
    Thanked 45 Times in 35 Posts
    Rep Power
    29

    Re: ups

    [topic moved to networks board - tarquel]


    ...and I have all servers UPS'ed [hehe] and have the main cur switch on a ups - admin switches will have UPS' on them as they will be POE ones and will have the ....*holds breath*....phone system on them.

    Hopefully in time, the trend will carry on throughout all the switches - to protect the switches more than anything else lol

    Nath.

  15. #15

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224

    Re: ups

    Quote Originally Posted by E1uSiV3
    Quote Originally Posted by Geoff
    Remeber if your using rackmounts + aircon you need some way of keeping the aircon going while the servers shut down. Due to the horrific power requirements of aircon that usually means a generator.
    True, but for the short amount of time you want to keep the systems up for, it shouldnt be a problem(ie 5-10 mins).
    Indeed. However a melted rack isn't something I'd personally want to risk.

    Quote Originally Posted by E1uSiV3
    Also i wouldnt rely on the UPS to keep the systems up for more than a minimal amount of time, id more look at them for power conditioning (ie brownout and overvolt protection) and to perform graceful shutdowns.
    Indeed. Thats the point of a UPS. The rules change slightly if you have a diesel generator though becuase you need to keep everything up on UPS for long enough to get the diesel generator online.