    Server room floor

    Hi all

    Currently speccing up our new server room and just wondered what sort of floor I should be going for? :? Dont like the carpet tiles - because they just suck and eventually start to smell (aka current server room). Raised floor seems a bit prohibitive cost wise. I think the white shiny floors look good, but not sure what material it is.

    What do you put down in your server room?

  2. #2
    Joanne's Avatar
    Join Date
    Nov 2007
    Location
    Lancashire
    Posts
    1,586
    Thank Post
    132
    Thanked 137 Times in 117 Posts
    Blog Entries
    17
    Rep Power
    78

    Re: Server room floor

    ours is standard puke green crappidy school carpet... the really hard wearing stuff.

    However, the room that has the servers in has one of those plastic vinyl floors... or whatever it is made out of. Not that the servers are on it... we have a big industrial shelving unit for them!

  3. #3
    PEO
    PEO is offline
    PEO's Avatar
    Join Date
    Oct 2007
    Posts
    2,095
    Thank Post
    457
    Thanked 152 Times in 96 Posts
    Rep Power
    72

    Re: Server room floor

    why dont you go for carpet tiles, that way when you spill coffee all over the server and floor you can at least lift the tile to wash

    I would lay carpet, and have the server rack mounted.

    need any tips on what colour to paint the wall?

  4. #4

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,223
    Thank Post
    874
    Thanked 2,717 Times in 2,302 Posts
    Blog Entries
    11
    Rep Power
    780

    Re: Server room floor

    Linoleum is what I got for ours as it does not create excess static and does not get filled up with dust and other rubbish. It is also far less likely to catch fire if there is a nasty hardware failure with the high voltage equipment.

    If you want to get caught up in the Cisco recommendations then it should also have its door opening outwards for a quick exit and should not have a drop ceiling.

  5. #5
    mrforgetful's Avatar
    Join Date
    May 2006
    Posts
    1,639
    Thank Post
    7
    Thanked 15 Times in 15 Posts
    Rep Power
    22

    Re: Server room floor

    I once met a guy on a course who used to work in Industry. He was shocked and appalled that all schools didn't have server rooms with raised floors and pressurised inside.

  6. #6
    ninjabeaver's Avatar
    Join Date
    Jun 2005
    Location
    Norfolk
    Posts
    1,089
    Thank Post
    182
    Thanked 100 Times in 88 Posts
    Rep Power
    46

    Re: Server room floor

    Yep, Linoleum. I just went and asked our site officer what it was called. I'ts very hard wearing, cleans easy and quick to put down.

    Perhaps a mattress for those late nights as well.

  7. #7

    GrumbleDook's Avatar
    Join Date
    Jul 2005
    Location
    Gosport, Hampshire
    Posts
    9,939
    Thank Post
    1,343
    Thanked 1,787 Times in 1,110 Posts
    Blog Entries
    19
    Rep Power
    595

    Re: Server room floor

    We have carpet but I am desperately trying to work out the best way to get rid of it. Because we have a hatch ou to the roof the floor often gets dirty and has to wait to dry before it gets hoovered ...

    A major source of dust and dirt!

  8. #8
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48

    Re: Server room floor

    Quote Originally Posted by SYNACK
    Linoleum is what I got for ours as it does not create excess static and does not get filled up with dust and other rubbish. It is also far less likely to catch fire if there is a nasty hardware failure with the high voltage equipment.

    If you want to get caught up in the Cisco recommendations then it should also have its door opening outwards for a quick exit and should not have a drop ceiling.
    Ooops, our server room has got a suspended ceiling...and by door that opens outwards do you mean a fire door/exit ?

  9. #9
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48

    Re: Server room floor

    Quote Originally Posted by TeddyKGB
    Hi all

    Currently speccing up our new server room and just wondered what sort of floor I should be going for? :? Dont like the carpet tiles - because they just suck and eventually start to smell (aka current server room). Raised floor seems a bit prohibitive cost wise. I think the white shiny floors look good, but not sure what material it is.

    What do you put down in your server room?
    did you get a quote for a raised floor, out of interest how much was it ?

    While raised floors are all well and good for large server rooms and datacenters, they're overkill for schools, prohibitively expensive to retrofit
    and difficult to justify even in a new build. In addition you'd need large and expensive CRAC units to deliver cooling through the floor. Overhead cabling and comfort cooling is just fine for server rooms of up to 4 racks so long as they're not chock full of blades.

    As for you're floor, yes the carpet tiles get smelly, and screws and things can be lost forever if you've got dark coloured tiles. So go for the lino option.

  10. #10

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,223
    Thank Post
    874
    Thanked 2,717 Times in 2,302 Posts
    Blog Entries
    11
    Rep Power
    780

    Re: Server room floor

    Quote Originally Posted by torledo
    Quote Originally Posted by SYNACK
    Linoleum is what I got for ours as it does not create excess static and does not get filled up with dust and other rubbish. It is also far less likely to catch fire if there is a nasty hardware failure with the high voltage equipment.

    If you want to get caught up in the Cisco recommendations then it should also have its door opening outwards for a quick exit and should not have a drop ceiling.
    Ooops, our server room has got a suspended ceiling...and by door that opens outwards do you mean a fire door/exit ?
    Just means that the doorway into the server room should swing outwards from the room. Not 100% sure why but being a cisco guideline it is probably there just in case you catch fire and have to run out of the room or something. I think it was also so no one barged in and hit you with the door if you were near it.

    The drop ceilings are more easily justified as it reduces amount of air space in the room and in some cases those drop ceilings hide the fact that the walls don't go all the way up. This means that the server room can leak noise, expensively air conditioned air or fire into the next room over quite easily.

    Our server room actually also has a drop ceiling but the walls go all the way to the real ceiling above so I'm ok with it.

  11. #11
    Oops_my_bad's Avatar
    Join Date
    Jan 2007
    Location
    Man chest hair
    Posts
    1,738
    Thank Post
    438
    Thanked 53 Times in 50 Posts
    Rep Power
    30

    Re: Server room floor

    Thanks guys - the linoneum stuff looks like what I'm after, I think it was this stuff they had down in the last place I worked at but didnt know what it was

    Torledo, don't quite recall the exact figures but the cost for a raised floor even in a new build was out of this world 8O

  12. #12

    john's Avatar
    Join Date
    Sep 2005
    Location
    London
    Posts
    10,619
    Thank Post
    1,499
    Thanked 1,053 Times in 922 Posts
    Rep Power
    304

    Re: Server room floor

    I have sparkley anti-slip industrial strength catering grade vinyl down on mine, its probably anti-static as well, I know the IT room carpets are anti-static tiles at something like £80 of a box of 20!!

    The floor is raised up a good foot from the rooms around it so they can flood nicely and I would hope someone would have noticed by that point that the IT Centre was starting to swim in water before I needed to look into moving out of the server room.

  13. #13

    Join Date
    Jan 2007
    Posts
    424
    Thank Post
    7
    Thanked 32 Times in 27 Posts
    Rep Power
    21

    Re: Server room floor

    we've got floorboards in ours suspended on 2by4 joists.. its reasonably effective.

    Kyle

  14. #14
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48

    Re: Server room floor

    Quote Originally Posted by SYNACK
    Quote Originally Posted by torledo
    Quote Originally Posted by SYNACK
    Linoleum is what I got for ours as it does not create excess static and does not get filled up with dust and other rubbish. It is also far less likely to catch fire if there is a nasty hardware failure with the high voltage equipment.

    If you want to get caught up in the Cisco recommendations then it should also have its door opening outwards for a quick exit and should not have a drop ceiling.
    Ooops, our server room has got a suspended ceiling...and by door that opens outwards do you mean a fire door/exit ?


    The drop ceilings are more easily justified as it reduces amount of air space in the room and in some cases those drop ceilings hide the fact that the walls don't go all the way up. This means that the server room can leak noise, expensively air conditioned air or fire into the next room over quite easily.

    Our server room actually also has a drop ceiling but the walls go all the way to the real ceiling above so I'm ok with it.
    One side if the wall goes all the way up, the other doesn't but then that's the point of the design of our building, to have a large suspended ceiling void spanning corriders and rooms. we are a small building but have extensive air conditioning, fire and security, lighting and air extraction which were relatively straightforward to install because of the large ceiling void, it also hides a multitude of sins.

    I suspected there could be some fire safety reasons so we may have to look into getting a (real) firewall (i know its in the cabling standards for the demarc /comms room and so our main switching room has a firewall even though it's had to huge holes bored into it to route cat5 cabling) so I'll have to look into whether we'll need one for the server room.

    I expect there to be minimal leakage of conditioned air and noise from the server room, although there's noone next to our room, merely a corridor.

    A low ceiling does mean the room gets hot very quickly, but on the flip side t means their is also a ready made plenum for removing hot exhaust air.

    So up to a certain number of servers and equipment a ceiling tile mounted heat extractor fan is the only thing required to keep the room temperature in check. We still use an A/C unit because we've got a lot of servers.

    Our room is actually more efficient than a high ceilinged room without raised floor cooling. Because the conditioned air is more targeted, blowing down at a 45 degree angle from the centre of the room with the front of the racks located in the air path. And the air extraction fans mounted directly behind the racks sucking the exhust immediately as it rises because there's minimum distance between the equipment and tile-mounted fan.


    Ofcourse our setup is nowhere near as efficient as raise floor cooling with CRAC units, because while we've tried to direct the air to the racks, it's very rudimentary. Not all of the air goes to cool the servers whereas with a raised floor you can direct airflow and even control the amount of air you send to each rack using grills in the ceiling tiles where they are optimally located. But then again I haven't got $200,000+ to spend on raised floor, CRAC unit, gas extinguishing system or anything 'datacenter' other than racks and cable routing.

  15. #15

    Join Date
    Jan 2007
    Posts
    424
    Thank Post
    7
    Thanked 32 Times in 27 Posts
    Rep Power
    21

    Re: Server room floor

    You should really have a firewall round all corridors - or for instance, above fire doors so areas become zones.

    I'd recommend you got one installed - especially in a server room - if you get a fire in that void it'll be through the building in minutes.

    As for boring holes through, you can always fill the gaps up with fire retardent expanding form.

SHARE:
+ Post New Thread
Page 1 of 2 12 LastLast

Similar Threads

  1. Environmental Monitoring in Server Room
    By pete in forum Hardware
    Replies: 7
    Last Post: 23rd May 2009, 06:31 PM
  2. Server room environment monitoring
    By localzuk in forum Hardware
    Replies: 27
    Last Post: 28th November 2007, 09:35 AM
  3. working in the server room
    By Uraken in forum General Chat
    Replies: 27
    Last Post: 21st November 2007, 09:39 AM
  4. Server Room Blitz - Day 1
    By sidewinder in forum General Chat
    Replies: 27
    Last Post: 13th August 2007, 06:19 PM
  5. Server room temperature
    By netadmin in forum General Chat
    Replies: 30
    Last Post: 11th June 2007, 07:35 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •