    Power Requirements for Server Rack

    Got a bit of a major task on over the next 12 months (which I'll blog about later), but the start of the process is moving the Server Room to a new location.

    The room the equipment is going into is about to be gutted and kitted out, but the question that will come my way shortly is how much power will I need?

    The old server room has 2 x 42U racks in, and both are just plugged into the wall socket on their own 32A Circuit. Not ideal, but I only have 7 servers at present. This number may grow in the short term, but long term hopefully reduce if we start to virtualize.

    The question is, what would be a 'standard' power requirement for each rack? I could work it all out, but servers will be changing over time. One electrical contractor I spoke to a while back suggested have a separate 16A feed for each rack, which seems reasonable.

    What power feed do you have each rack in your server rooms?

    Looks like I'm going for 4 racks in total; 2 for the servers, 1 for the Core Switch(es) and 1 for the fibre patch panels.

    Again, thanks in advance.

    Pete

  2. #2
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by FragglePete View Post
    Got a bit of a major task on over the next 12 months (which I'll blog about later), but the start of the process is moving the Server Room to a new location.

    The room the equipment is going into is about to be gutted and kitted out, but the question that will come my way shortly is how much power will I need?

    The old server room has 2 x 42U racks in, and both are just plugged into the wall socket on their own 32A Circuit. Not ideal, but I only have 7 servers at present. This number may grow in the short term, but long term hopefully reduce if we start to virtualize.

    The question is, what would be a 'standard' power requirement for each rack? I could work it all out, but servers will be changing over time. One electrical contractor I spoke to a while back suggested have a separate 16A feed for each rack, which seems reasonable.

    What power feed do you have each rack in your server rooms?

    Looks like I'm going for 4 racks in total; 2 for the servers, 1 for the Core Switch(es) and 1 for the fibre patch panels.

    Again, thanks in advance.

    Pete
    16A feed per rack should be fine.

    infact you could probably power all your equipment off a single 16A feed [depending on rack density], the second feed could be for server power supply redundancy, no ?

    how have you been advised as far as UPS to protect the loads ?

  3. Thanks to torledo from:

    FragglePete (16th May 2009)

  4. #3

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    13,317
    Thank Post
    681
    Thanked 1,650 Times in 1,471 Posts
    Rep Power
    425
    my servers are not rackmounted but run off a big ups which is hardwired. Why put your fibre patch panels in a seperate rack.

  5. #4

    Michael's Avatar
    Join Date
    Dec 2005
    Location
    Birmingham
    Posts
    9,262
    Thank Post
    242
    Thanked 1,572 Times in 1,252 Posts
    Rep Power
    340
    It really does depend on a lot of factors. For example, some servers I've installed recently are actually much more powerful and less power consuming than the existing servers. In some cases as you have seven servers, I suspect you probably could merge two into one. It depends what they're hosting I suppose.

    16A for a 42U rack seems more than enough. Switches generally consume relatively low power (especially modern switches) and many are completely silent as there are no fans at all.

  6. Thanks to Michael from:

    FragglePete (16th May 2009)

  7. #5

    Join Date
    Feb 2008
    Location
    Wiltshire
    Posts
    891
    Thank Post
    282
    Thanked 139 Times in 112 Posts
    Blog Entries
    27
    Rep Power
    42
    Quote Originally Posted by plexer View Post
    my servers are not rackmounted but run off a big ups which is hardwired. Why put your fibre patch panels in a seperate rack.
    'cos there is going to be a lot of them.

    Completely new backbone going in, 14 fibre runs going into which will all route back to the core. Aiming for a true star topology of the network.

    Pete

  8. #6

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    When I worked in a datacentre we supplied racks with a 16A spine each, which was more than enough for a dense (filled with 1U shelves) rack. There was plenty of overhead for spike demands, so you can probably get away with sharing that between two or even three racks in your new room.

    It's more important that you make sure the phases are relatively clean, that if you can you have smoothing equipment at source, etc to minimise wear and tear on the kit. And of course, you'll be putting UPSs in too

  9. Thanks to powdarrmonkey from:

    FragglePete (17th May 2009)

  10. #7

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,941
    Thank Post
    519
    Thanked 2,500 Times in 1,941 Posts
    Blog Entries
    24
    Rep Power
    840
    We have a 16A supply for our rack - with two 16A plugs, one for each UPS.

  11. Thanks to localzuk from:

    FragglePete (17th May 2009)

  12. #8
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by powdarrmonkey View Post
    When I worked in a datacentre we supplied racks with a 16A spine each, which was more than enough for a dense (filled with 1U shelves) rack. There was plenty of overhead for spike demands, so you can probably get away with sharing that between two or even three racks in your new room.

    It's more important that you make sure the phases are relatively clean, that if you can you have smoothing equipment at source, etc to minimise wear and tear on the kit. And of course, you'll be putting UPSs in too
    what can be installed specifically to clean power at source ?

  13. #9

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    They're commonly called conditioners and installed either as part of the distribution board or as part of a distribution device in the rack itself.

  14. #10
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by powdarrmonkey View Post
    They're commonly called conditioners and installed either as part of the distribution board or as part of a distribution device in the rack itself.
    but a good ups would do power conditioning.

    if you need to take the ups offline, then it would be good to have clean power for however long, but you can build that redundancy in with a second power conditioner (ups). Adding a second ups would have the advantage of being cheaper than having a line conditioner installed. Plus the second ups would have battery backup for graceful shutdown.

    for a small single server room with 2-4 rack install i'd defintely do with either a N+1 ups if the money is there. If not then 2N ups. 2x 16A feeds coming from 2 ups. i don't know whether you'd need some sort of transfer switch sitting between the ups and the dual psu servers ?

  15. #11

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    Quote Originally Posted by torledo View Post
    but a good ups would do power conditioning.
    Yes, it would, but there are things in the room that I'd like conditioned but not necessarily on UPS - switches, monitors for example. A conditioner for those would be cheaper than a UPS and minimise the hassle of maintaining batteries, testing, etc.

  16. #12
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by powdarrmonkey View Post
    Yes, it would, but there are things in the room that I'd like conditioned but not necessarily on UPS - switches, monitors for example. A conditioner for those would be cheaper than a UPS and minimise the hassle of maintaining batteries, testing, etc.
    why not have switches and monitors on the ups ? it doesn't add much to the load, and as most ups have some sort of bypass you can still get power to monitors and the like if the ups is in bypass for maintenance or testing. Battery maintenance is a valid point, but there isn't i don't believe a cost saving for going with a dedicated line conditioner.....atleast until you have to replace batteries with the UPS. ;0)

    Plus, are you sure about the cost ? dedicated line conditioners are pretty pricey, surge supressers are cheap, but the alternative install cost of a proper TVSS or isolation transformer plus surge supression for the supply to the server room would cost as least as much as a UPS if not more based on the single quote i've had. Told straight off the bat that a line conditoner would be much more costly than an isolation transformer.

    sorry for the inquistion, but i'm looking into getting cheap [as possible] clean power for the supply feeding our server room. And curious as to recommend products that would fit the bill. without breaking the bank.

  17. #13

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    Quote Originally Posted by torledo View Post
    why not have switches and monitors on the ups ? it doesn't add much to the load, and as most ups have some sort of bypass you can still get power to monitors and the like if the ups is in bypass for maintenance or testing. Battery maintenance is a valid point, but there isn't i don't believe a cost saving for going with a dedicated line conditioner.....atleast until you have to replace batteries with the UPS. ;0)
    Maximum runtime. I don't care if the core switch and monitors go off, or periphery servers that don't matter, but I do care if the file server goes while flushing the disk for example. Don't under-estimate the power requirements for a switch

    Quote Originally Posted by torledo View Post
    Plus, are you sure about the cost ? dedicated line conditioners are pretty pricey, surge supressers are cheap, but the alternative install cost of a proper TVSS or isolation transformer plus surge supression for the supply to the server room would cost as least as much as a UPS if not more based on the single quote i've had. Told straight off the bat that a line conditoner would be much more costly than an isolation transformer.
    A rack mount conditioner will set you back something around £50-£150 per rack, versus £300-£2k for a UPS. At that rate, I'd even condition my UPS feeds, since if there's an almighty surge that kills things I'd much rather it be a fifty quid conditioner.

    You're right that a full supply protection in the wall would be more expensive though. But a conditioner per rack plus one on the desk for other bits and pieces really isn't so much of a problem, is it?

    Quote Originally Posted by torledo View Post
    sorry for the inquistion, but i'm looking into getting cheap [as possible] clean power for the supply feeding our server room. And curious as to recommend products that would fit the bill. without breaking the bank.
    Samson PS10 19" Rackmount Power Conditioner - DV247.COM ?

  18. #14
    TNE
    TNE is offline
    TNE's Avatar
    Join Date
    May 2009
    Location
    West Midlands
    Posts
    59
    Thank Post
    7
    Thanked 8 Times in 8 Posts
    Rep Power
    12
    Hello Pete,

    Hope you don't mind me taking this slightly off topic but I notice you may be in the market for some cabinets.

    If you are looking to purchase these yourselves instead of through a contractor I would appreciate the opportunity to provide a quotation. We have just started sponsoring the forum and you can find our banner on the Vista forum

    Thanks

SHARE:
+ Post New Thread

Similar Threads

  1. Wallmount rack for a tower server?
    By pete in forum Hardware
    Replies: 9
    Last Post: 6th March 2009, 07:44 AM
  2. MS Terminal Server Bandwidth Requirements (WAN)
    By RobFuller in forum Thin Client and Virtual Machines
    Replies: 6
    Last Post: 5th August 2008, 02:18 PM
  3. Mobile server rack?
    By Abaddon in forum Hardware
    Replies: 2
    Last Post: 4th July 2008, 05:38 PM
  4. [Wanted] Server rack/cabinet
    By IA76 in forum Classified Adverts
    Replies: 0
    Last Post: 14th April 2008, 11:23 AM
  5. Microsoft Communicator 2007 Server requirements & RM?
    By Nexus-6 in forum Wireless Networks
    Replies: 0
    Last Post: 8th February 2008, 09:39 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •