How do you do....it? Thread, air con problems in Technical; Anyone here experts on Air-Cons? Our unit in the server room has exploded. Well I came in last Tuesday and ...
  1. #1

    tmcd35's Avatar
    Join Date
    Jul 2005
    Location
    Norfolk
    Posts
    5,620
    Thank Post
    845
    Thanked 882 Times in 731 Posts
    Blog Entries
    9
    Rep Power
    326

    air con problems

    Anyone here experts on Air-Cons? Our unit in the server room has exploded. Well I came in last Tuesday and found a very wet box of old toner carts and loads of black stuff under the unit. It refuses point blank to turn on now

    When the air-con was fitted in the last school a guy came out and used some formula based on the PSU's of the servers to work out how much heat they generate and the rating of Air-Con unit needed to dissipate that heat.

    I have a chap coming in tomorrow to look at the broken unit and give us an estimate on temporary repair and/or replacement. But would like to have some figures for him ahead of time as to what we need/want.

    Anyone know how to calculate the correct rating for a new air con?

    Cheers

    Terry.

  2. #2

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224

  3. 4 Thanks to Geoff:

    localzuk (20th April 2009), Sylv3r (20th April 2009), tmcd35 (20th April 2009), UKDarkstar (20th April 2009)

  4. #3

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,631
    Thank Post
    514
    Thanked 2,442 Times in 1,890 Posts
    Blog Entries
    24
    Rep Power
    831
    Interesting formula that! It means that our 3kW air con is precisely 4 times too small for the job it is doing... No wonder it keeps breaking. Always wondered why the installers never asked me about the ratings of the machinery in the actual room when they installed it (I didn't organise it...).

  5. #4

    tmcd35's Avatar
    Join Date
    Jul 2005
    Location
    Norfolk
    Posts
    5,620
    Thank Post
    845
    Thanked 882 Times in 731 Posts
    Blog Entries
    9
    Rep Power
    326
    Thanks Geoff. Just did some sums on a back of a napkin. We need a 10KW unit apparently. No wonder our 5-year old 24/7 6.5KW unit bit the dust!

  6. #5

    Join Date
    Jan 2009
    Location
    England
    Posts
    1,480
    Thank Post
    297
    Thanked 304 Times in 263 Posts
    Rep Power
    82
    Quote Originally Posted by tmcd35 View Post
    Thanks Geoff. Just did some sums on a back of a napkin. We need a 10KW unit apparently. No wonder our 5-year old 24/7 6.5KW unit bit the dust!
    Hmmm I've just done some calculations for our server room and we're going to need around a 12kw unit once our new servers/SAN get switched on.

    Just need to convince SMT that we do need a dedicated server room and that the sick bay is going to get a little warm this summer!

SHARE:
+ Post New Thread

Similar Threads

  1. Air con help
    By Little-Miss in forum How do you do....it?
    Replies: 20
    Last Post: 25th March 2009, 07:54 PM
  2. air con
    By amyr in forum General Chat
    Replies: 19
    Last Post: 28th February 2007, 02:44 PM
  3. Air Con recommendations
    By mark in forum Other Stuff
    Replies: 3
    Last Post: 12th July 2005, 02:23 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •