    Server room temperature monitoring

    Just had the a\c fail in our server room, I only noticed as one minor switch packed up! Does anyone have a monitor that would email out when it hits a threshold?

  2. #2

    Join Date
    Feb 2008
    Location
    Wiltshire
    Posts
    905
    Thank Post
    287
    Thanked 141 Times in 114 Posts
    Blog Entries
    28
    Rep Power
    42
    We've got a CM-2 from The Climate - it's setup so it sends a SMS text alert (via an e-mail gateway) if certain thresholds are exceeded. Monitors Light, Sound, Humidity and Temperature out of the box but you can add extra sensors and cameras on it.

    Pete

  3. #3
    truebluesteve's Avatar
    Join Date
    Jan 2008
    Posts
    462
    Thank Post
    71
    Thanked 58 Times in 49 Posts
    Rep Power
    27
    Quote Originally Posted by FragglePete View Post
    We've got a CM-2 from The Climate - it's setup so it sends a SMS text alert (via an e-mail gateway) if certain thresholds are exceeded. Monitors Light, Sound, Humidity and Temperature out of the box but you can add extra sensors and cameras on it.

    Pete
    Same here.... Very good piece of kit!

  4. #4

    Join Date
    Oct 2008
    Location
    Lincolnshire
    Posts
    2,348
    Thank Post
    13
    Thanked 241 Times in 229 Posts
    Rep Power
    70
    Have a look at the APC NetBotz kit, its really good and not badly priced either.

  5. #5
    ADMaster's Avatar
    Join Date
    May 2012
    Posts
    356
    Thank Post
    5
    Thanked 39 Times in 34 Posts
    Rep Power
    25
    I have Temperature @lert it is a USB device that will send emails for high and low temps.

    Not to highjack the thread, but what is a good temp for the server room? I have one room that gets into the high 80's low 90's (30 - 35) if I do not keep the door open in the summer.

    Thanks,

  6. #6
    southhamster's Avatar
    Join Date
    Jan 2013
    Location
    South Devon
    Posts
    65
    Thank Post
    48
    Thanked 30 Times in 10 Posts
    Rep Power
    9
    You might be able to configure nagios to do something - maybe using the server motherboard/ambient temp sensor?
    Some switches can also monitor temperature - I don't know if there's some way maybe of using snmp to monitor that, again maybe with nagios or similar.
    Ideal server room temp - I was always told the lower the better although aircon costs can make it very expensive.
    Lateral thinking is, locate the server room on the North side of the building, possibly using louvred but secure vents to the outside with an extract fan on a temp sensor. It always amuses me to see schools who have installed an extract fan in the (completely sealed) server room with no inlet vent. How does that work?
    Which reminds me, it's so annoying to see brand new schools (BSF PFI) with IT Suites on the south side of a building, massive non-opening windows and then aircon installed afterwards to remove the heat. grrrr. Do architects do it on purpose?

    I'd be a bit concerned about temps above 20-25 deg C. 30-35 sounds a bit much!
    I'd also think about humidity - I'd assume that drier is better to avoid oxidising contacts and increase heat dissipation, but low humidity does increase the effect of static electricity.

  7. #7

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,821
    Thank Post
    272
    Thanked 1,140 Times in 1,036 Posts
    Rep Power
    351
    ive used room alert before, nice and robust and customizable

  8. #8

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    13,689
    Thank Post
    756
    Thanked 1,715 Times in 1,526 Posts
    Rep Power
    438
    Quote Originally Posted by dana_lehman View Post
    I have Temperature @lert it is a USB device that will send emails for high and low temps.

    Not to highjack the thread, but what is a good temp for the server room? I have one room that gets into the high 80's low 90's (30 - 35) if I do not keep the door open in the summer.

    Thanks,
    Have a look at what the kit says it's happy with it's really consistency that's the key.

    Ben

  9. #9
    Elison's Avatar
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    259
    Thank Post
    64
    Thanked 21 Times in 20 Posts
    Rep Power
    13
    Quote Originally Posted by FragglePete View Post
    We've got a CM-2 from The Climate - it's setup so it sends a SMS text alert (via an e-mail gateway) if certain thresholds are exceeded. Monitors Light, Sound, Humidity and Temperature out of the box but you can add extra sensors and cameras on it.
    We use it as well.

  10. #10
    old_n07's Avatar
    Join Date
    Jun 2012
    Location
    North Staffordshire
    Posts
    99
    Thank Post
    10
    Thanked 17 Times in 15 Posts
    Rep Power
    8
    We've got a monitor that plugs into our APC UPS and monitors temp via powerchute, it performs shut downs based on a temp threshold set in the software.

    We lost Aircon a few months ago as sites were working on the electric and had the phase off on a Saturday (didn't tell IT) and they forgot to turn it back on again, the first we knew was when the Equalogic SAN's, EMC SAN and blade centres started emailing about temperature. This would have been picked up in the week but at a weekend it was lucky that I checked my email when I saw 130 new emails on my phone.

    This highlighted the fact that we needed propper warnings so the BMS system has now been configured to automatically SMS message the duty caretaker, head of IT and head of estates should anything happen again as this has temp monitors in the server room but nothing had been configured, and the APC module bought for the UPS.

    We were lucky in that we didn't loose anything despite seeing intake temps of 70 degrees reported but it doesn't mean that the serviceable life of components hasn't been reduced and we will get premature failures down the line.

  11. #11
    edie209's Avatar
    Join Date
    Mar 2006
    Location
    Kernow
    Posts
    705
    Thank Post
    42
    Thanked 19 Times in 18 Posts
    Rep Power
    22
    Quote Originally Posted by FragglePete View Post
    We've got a CM-2 from The Climate - it's setup so it sends a SMS text alert (via an e-mail gateway) if certain thresholds are exceeded. Monitors Light, Sound, Humidity and Temperature out of the box but you can add extra sensors and cameras on it.

    Pete
    Same here, although it took a Air Con failure to get it

  12. #12

    Join Date
    Apr 2007
    Location
    Cornwall
    Posts
    347
    Thank Post
    22
    Thanked 96 Times in 67 Posts
    Rep Power
    40
    I like the idea to get a temperature warning system, but looking at the costs, I might just create one out of an arduino/netduino... That should keep the costs down.

    Meldrew

  13. #13

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,850
    Thank Post
    110
    Thanked 598 Times in 514 Posts
    Blog Entries
    1
    Rep Power
    227
    Quote Originally Posted by dana_lehman View Post
    Not to highjack the thread, but what is a good temp for the server room? I have one room that gets into the high 80's low 90's (30 - 35) if I do not keep the door open in the summer.
    A temperature range of 16–24 °C (61–75 °F) and humidity range of 40–55% with a maximum dew point of 15 °C.

  14. #14
    Chris_'s Avatar
    Join Date
    Jul 2010
    Location
    UK
    Posts
    734
    Thank Post
    142
    Thanked 125 Times in 105 Posts
    Rep Power
    47
    I've been looking at the offering from Ubiquiti - mFi. Could get an mPort, and temperature sensor for less than £100. Could then add another two sensors to the mPort to make more use of it such as a PIR/door sensor so we could log when the server room door is opened or movement in there, or a current sensor so we can monitor power usage of the UPS and equipment.

  15. #15

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,772
    Thank Post
    1,308
    Thanked 804 Times in 698 Posts
    Rep Power
    247
    Quote Originally Posted by Geoff View Post
    A temperature range of 16–24 °C (61–75 °F) and humidity range of 40–55% with a maximum dew point of 15 °C.
    A Dell salesperson told me the other day that Dell's new server range is designed to run "at room temperature", which I guess means you can set the thermostat on the airconditioning to 24°C and leave them to it. I don't know how badly temperature affects battery performance on UPSes - our UPS batteries seemed to fail very quickly (about 18 months), and they should last longer than that. Our air conditioning is not up to the job, but we're now moving the whole server cupboard over the summer. We have issues installing a decent airconditioning unit with an external heat exchanger as we're right in a residential area, in a listed building, with neigbour's windows very close (a couple of metres). We might go for a snazzy water-cooled air conditioning unit in our new server cupboard, which transfers the heat to water from the mains - and you can even use that "waste" water and put it into a hot water tank for later.



SHARE:
+ Post New Thread
Page 1 of 2 12 LastLast

Similar Threads

  1. Replies: 8
    Last Post: 14th May 2013, 06:14 PM
  2. Server Room Temperature Sensor?
    By Gongalong in forum Hardware
    Replies: 10
    Last Post: 5th February 2013, 03:48 PM
  3. Server room environment monitoring
    By localzuk in forum Hardware
    Replies: 27
    Last Post: 28th November 2007, 10:35 AM
  4. Server room temperature
    By netadmin in forum General Chat
    Replies: 30
    Last Post: 11th June 2007, 08:35 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •