    UPS sizing calculators APC vs HP

    Having been sizing up Power requirements for some new HP servers I found that there is quite a large variance between APC and HP's utilites:

    For a HP DL380 G7 - with 2 x Xeon 5620, 72Gb RAM, 2 x 146Gb 15k SAS, 1 x NC550SFP 10Gbe NIC, 2 x SC08e 6GB SAS card, 2 x 460W PSUs

    HP (itemising all options - server@100 % utilisation)) = 310VA 299Watt
    APC (simple generic HP options for DL380 G7) = 625VA 438Watt


    Quite a large difference!


    You could have a play with your configs and see what results you get:

    HP Power Advisor 3 Download:

    HP Power Advisor

    APC Product selector:

    UPS Selector Sizing Applications

  2. #2

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    18,343
    Thank Post
    525
    Thanked 2,597 Times in 2,015 Posts
    Blog Entries
    24
    Rep Power
    888
    The HP one is likely closer to reality - I've found that the APC calculator is somewhat over-eager with its recommendations. However, I always 'over spec' UPSs anyway, so it has always worked well for me.

  3. Thanks to localzuk from:

    MrWu (8th July 2012)

  4. #3

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,821
    Thank Post
    272
    Thanked 1,140 Times in 1,036 Posts
    Rep Power
    351
    don't buy HP ups's they are awful imho and half of them are apc rebadged. Borri's ups' are good and they will come to site and spec something up to suit you needs and go through all the power requirements.

  5. Thanks to glennda from:

    MrWu (8th July 2012)

  6. #4

    Join Date
    Dec 2011
    Posts
    408
    Thank Post
    372
    Thanked 45 Times in 33 Posts
    Rep Power
    13
    Yep, did have Borri pop over and did a survey.

    Have quoted for a B500 10kva on line, wired straight to the distribution board, maintenance bypass switch and scope to buy another B500 in parallel for redundancy.

    Long story but school has issues setting up an account with Borri in time for install :-(. So using a APC SURT8000XLI might be Plan B, with existing SMT3000RMI2Us acting as the redundant backup UPS for servers with 2xPSUs

  7. #5

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,821
    Thank Post
    272
    Thanked 1,140 Times in 1,036 Posts
    Rep Power
    351
    How quickly do you need install? I had them drop mine in a week and a half. If you need a Sparky that has wired one before I can give you the name of the fella I used.

  8. Thanks to glennda from:

    MrWu (8th July 2012)

  9. #6

    Join Date
    Dec 2011
    Posts
    408
    Thank Post
    372
    Thanked 45 Times in 33 Posts
    Rep Power
    13
    Hi glenda, ideally over summer.

    We have our own sparky(However I think Borri will include tapping into our distribution board so all our existing pdus and sockets work) its more the school going through T&Cs for all new suppliers and some they are rejecting to trade with...and theres a backlog of them. They know it's urgent however..so I'm hopeful...

    I remember you had Borri as well, I like the idea of Borri feeding th distribution board, and I think by adding another Borri in parallel would provide redundancy(although not as good as having dual seperate circults I suppose...but it will be the same if I went for say redundant conventional APCs UPSs)

    What is the shutdown software like for Borri vs APC network shutdown? Usual agent installs on servers? Does it cope with Hyper-V VMs?

    Ta

  10. #7

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,821
    Thank Post
    272
    Thanked 1,140 Times in 1,036 Posts
    Rep Power
    351
    You don't have to get borri to do the connections to dist boards - I didn't and saved quite a bit just had them come in to commision (setup the batteries etc). The agent is ok and works well although can't say i have used it with Hyper-V. But you can execute a batch file which can be used to shutdown the vm's (something like shutdown -f -s -t 01 -m \\machinename).

  11. Thanks to glennda from:

    MrWu (8th July 2012)

  12. #8

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,268
    Thank Post
    884
    Thanked 2,747 Times in 2,321 Posts
    Blog Entries
    11
    Rep Power
    785
    I'd also overspec with the APC figures, also just backing up the stay clear of HP UPSs advice, horrible and not APC rebrands. I have actually had really god service from APC gear. Never tried Bori as its not available here. APC 'now' has good free network shutdown software too.

  13. Thanks to SYNACK from:

    MrWu (8th July 2012)



SHARE:
+ Post New Thread

Similar Threads

  1. New UPS - APC vs Delta
    By Irazmus in forum Hardware
    Replies: 6
    Last Post: 21st September 2011, 10:02 PM
  2. Setting up mapping and Lun on HP MSA SAN
    By ranj in forum Hardware
    Replies: 2
    Last Post: 31st August 2010, 07:40 PM
  3. Dell Vostro 3500 vs Hp Compaq 610
    By LukeC in forum General Chat
    Replies: 4
    Last Post: 6th May 2010, 04:00 PM
  4. Extreme vs HP Procurve
    By tjb in forum Wireless Networks
    Replies: 7
    Last Post: 21st August 2009, 01:12 AM
  5. Up to £400 cashback on HP printers
    By Norphy in forum Hardware
    Replies: 8
    Last Post: 12th May 2006, 08:03 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •