    Choosing a UPS

    I intend to purchase a HP DL380 and a HP DL120. But i have no idea what UPS to go for, it needs to be rack mountable and if the power goes OFF then all the desktops are going down anyway, soi would just it to be able to run on battery long enough for me to shut them down. Any suggestions on how i select something that will suit?

  2. #2

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,060
    Thank Post
    853
    Thanked 2,674 Times in 2,269 Posts
    Blog Entries
    9
    Rep Power
    768
    Have a look at this:
    UPS Selector Sizing Applications

    It depends on how long you need them to run for and how long they take to shutdown. A 1500VA unit would probably cut it but a 2200VA would be better and would provide a little more overhead. The larger ones run much higher wall socket amperages though so you will need to factor in the cost of an electition for a high current feed if going much over 2000VA.

  3. #3
    Frut02's Avatar
    Join Date
    Oct 2011
    Location
    Cambridge
    Posts
    103
    Thank Post
    4
    Thanked 10 Times in 10 Posts
    Rep Power
    7
    This is a good website to evaluate what UPS would be best for you, Just choose the server and it will work out the load that the UPS needs to support

    Exalt

  4. #4

    m25man's Avatar
    Join Date
    Oct 2005
    Location
    Romford, Essex
    Posts
    1,621
    Thank Post
    49
    Thanked 451 Times in 334 Posts
    Rep Power
    137
    The APC Smart Range of Rackmount UPS' forsake battery capacity in place of Inverter assemblies, the end result is that you can end up with a 3000KVA capable Inverter with a runtime of no more than 6 minutes.

    You need:-

    1. An inverter capacity capable of running your desired equipment with ease
    2. Enough runtime to accomplish everything you need to do in a blackout.

    DL380's come with PSU's rated between 400w and 1Kw (the newer models being the lowest) so if both servers ran at 50% of peak you would probably be looking around a 500w working load.
    This would mean an APC 1500 would probably be sufficient, a 2200 better and a 3000 overkill for just 2 servers.

    Any of the above would suffice, but in your case without the expense of extended runtime options just buy the biggest the budget will stretch to.
    Last edited by m25man; 25th May 2012 at 01:05 PM.

SHARE:
+ Post New Thread

Similar Threads

  1. Setting up home wireless network with MAC and PC..?
    By tosca925 in forum General Chat
    Replies: 6
    Last Post: 21st November 2011, 04:39 PM
  2. Meet Up / Conference Latest
    By russdev in forum Other Stuff
    Replies: 51
    Last Post: 27th December 2005, 06:27 PM
  3. Technician - Salary Up to £29,582 - Kingston
    By tosca925 in forum Educational IT Jobs
    Replies: 5
    Last Post: 14th October 2005, 09:52 PM
  4. ICT Support Technician up to 30k (London)
    By tosca925 in forum Educational IT Jobs
    Replies: 0
    Last Post: 24th September 2005, 09:31 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •