Hardware Thread, Laptop Trolley through UPS - prevent circuit tripping? in Technical; We have a couple of 16x laptop trolleys in the school. However, staff are not very good at following instructions, ...
  1. #1
    docboggle's Avatar
    Join Date
    Jan 2008
    Location
    Northants
    Posts
    95
    Thank Post
    50
    Thanked 13 Times in 7 Posts
    Rep Power
    19

    Laptop Trolley through UPS - prevent circuit tripping?

    We have a couple of 16x laptop trolleys in the school. However, staff are not very good at following instructions, and forget to turn off the switches inside, and subsequently trip the circuit breaker. To make things worse, it is the same circuit as our servers.

    I was wondering if connecting the laptops up to a UPS to charge would prevent this sudden surge of 16 power packs from tripping the fuse breaker, with the UPS dealing with the surge? Was looking at something like Extra Value 500VA UPS - GREAT PRICE | Ebuyer.com

    Would this work? Has anyone faced something similar and found a solution?

  2. #2
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,435
    Thank Post
    672
    Thanked 279 Times in 246 Posts
    Rep Power
    78
    Could you not fit something like PRO ELEC|RCD2-UK|RCD ADAPTOR REWIREABLE | CPC to the trollies that would help? Or get a sparky to fit a surge protected plug socket where they get stored?

  3. #3
    docboggle's Avatar
    Join Date
    Jan 2008
    Location
    Northants
    Posts
    95
    Thank Post
    50
    Thanked 13 Times in 7 Posts
    Rep Power
    19
    Have tried RCDs and both the RCD and main circuit breaker go, so no good

  4. #4
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,435
    Thank Post
    672
    Thanked 279 Times in 246 Posts
    Rep Power
    78
    Quote Originally Posted by docboggle View Post
    Have tried RCDs and both the RCD and main circuit breaker go, so no good
    Wowsers .. have you had the trollies or circuit you're plugging into tested as that sounds a bit extreme to be doing all of that ..

    I guess a UPS would soak up some of the surge, but it's how you would go about making sure the staff plug into that if they can't follow your other instructions too.

  5. #5

    Join Date
    Feb 2007
    Location
    East Sussex
    Posts
    476
    Thank Post
    16
    Thanked 90 Times in 82 Posts
    Rep Power
    31
    What model laptop trolley's do you have? I know the ones we buy offer a 'soft start' (or some similar name) charging option to prevent this happening.

    Steve

  6. #6

    bossman's Avatar
    Join Date
    Nov 2005
    Location
    England
    Posts
    4,017
    Thank Post
    1,253
    Thanked 1,099 Times in 781 Posts
    Rep Power
    337
    @docboggle:

    I would be suggesting another circuit for the 2 laptop trolley's to plug into probably a 16 amp breaker. As with all our ICT suites it is a recommendation that between 6 - 8 computers per trip on each circuit. What you have in effect is 2 x 16 = 32 on one circuit which carries your servers also, no wonder your laptop trolley's are tripping everything.

    That would be my advice from a health and safety point of view.

  7. #7

    Join Date
    Mar 2010
    Posts
    3
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Quote Originally Posted by docboggle View Post
    We have a couple of 16x laptop trolleys in the school. However, staff are not very good at following instructions, and forget to turn off the switches inside, and subsequently trip the circuit breaker. To make things worse, it is the same circuit as our servers.
    That circuit breaker is not reporting staff mistakes. The circuit that is ghastly overloaded.

    You are suppose to know how much power is connected to that circuit. Every appliance has a label (where the power cord connects) that says how much power (watts or amps) that appliance consumes. You are expected to add those numbers.

    Circuit breakers are only emergency safety backups to report when a human has made an addition error. For example, a 20 amp circuit breaker will conduct an overload - 25 amps - for up to two hours before the breaker trips. Your laptops could be drawing more than 30 amps when combined with the power consumptions of the server. That is an overloaded circuit - a human safety threat.

    Also scary is recommeneding a surge protector plug to cure an overload.

    Circuit breaker is repeatedly reporting an overloaded circuit. A 16 amp breaker will easily provide 32 amps for 12 or 25 seconds without tripping. The circuit can be overloaded for that long because breakers are only emgerency backup protection. Stop trying to cure symptoms. You need another circuit. The existing circuit is very much overloaded. That simple. That existing overloaded circuit was obviously a potential fire.

    A mistake started by not summing power numbers from each appliance label. Circuit breaker is reporting a human created failure. Switching off laptops to reduce the still existing overload is another bad solution.
    Last edited by westom; 19th October 2011 at 04:39 PM.

  8. #8
    docboggle's Avatar
    Join Date
    Jan 2008
    Location
    Northants
    Posts
    95
    Thank Post
    50
    Thanked 13 Times in 7 Posts
    Rep Power
    19
    Quote Originally Posted by soveryapt View Post
    but it's how you would go about making sure the staff plug into that if they can't follow your other instructions too.
    Signs, posters and lessons. Short of using them as the circuit breaker, I'm not sure what to do!

    Quote Originally Posted by steveg View Post
    What model laptop trolley's do you have? I know the ones we buy offer a 'soft start' (or some similar name) charging option to prevent this happening.
    We have Bretford trolleys through RM. One of them is quite old now, but even the newer one we had in August doesn't have this facility.
    The 'soft start' seems to be a Loxit product, with the Bretford equivalent being 'EPM'. These upgrades look to be in the region of £200 each and are design to fit inside the trolley.
    This is the type of system that I am after, but would be happy with something that is just attached to the wall where the trolleys are charged (they are never plugged in anywhere else). Is there such a product?

  9. #9

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    13,631
    Thank Post
    747
    Thanked 1,707 Times in 1,520 Posts
    Rep Power
    437
    Having a new circuit with commodo plugs but that would probablu be more than £200

    Ben

  10. #10

    Join Date
    Sep 2008
    Location
    England
    Posts
    276
    Thank Post
    6
    Thanked 70 Times in 62 Posts
    Rep Power
    53
    If the rcds are tripping (rather than circuit breakers), then it isn't just current, it will be the number of devices as well.

    RCDs detect an imbalance between the current flowing in the live and neutral wires. Each device will have a small earth leakage, which isn't a problem on its own, but if you add 32+ computers/laptops/servers onto one rcd, the cumulative imbalance will trip the breaker.

    The advice above about adding up the current is correct. If you are in any doubt, get someone qualified in to check it over. Messing up mains electrics could cause a fire which would be much more expensive getting an electrician in.

    You need to get a properly qualified electrician in to look at this circuit.

    Adding a ups will make things worse at this stage, as it will increase the electrical load and earth leakage, although your servers probably should be on one anyway. You should probably get your servers on their own dedicated circuit that isn't used for anything else, not hoovers, not laptop trolleys, not anything.



SHARE:
+ Post New Thread

Similar Threads

  1. Laptop Trolley
    By kingswood in forum Recommended Suppliers
    Replies: 8
    Last Post: 8th March 2007, 07:42 PM
  2. Setting up a Laptop Trolley
    By thom in forum Hardware
    Replies: 20
    Last Post: 8th August 2006, 05:50 PM
  3. New Equipment - Laptop Trolleys
    By BooBoo in forum Recommended Suppliers
    Replies: 25
    Last Post: 22nd July 2006, 06:10 PM
  4. Laptop Trolley
    By adamyoung in forum How do you do....it?
    Replies: 5
    Last Post: 20th July 2006, 12:16 PM
  5. Laptop Trolley and a server?
    By CM786 in forum Hardware
    Replies: 11
    Last Post: 3rd April 2006, 11:25 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •