    APC PDUs question. changing commando sockets to normal plug?

    I Have a question about this APC PDUs. We have just purchased 16amp and 32amp version of these PDUs but the non metered ones. I think they are called Basic PDUs. They have about 20 C13 sockets on them.

    My question is we are in the process of installing cable tray with 16amp and 32amp commando sockets which will then go back to a distribution board wheres feed will be coming from a UPS backed system.

    At the moment though we dont have this and part of power resiliency work is to get rid of all the extensions that are currently in the back of our racks. Install these PDU's and start wiring with these rather using extension sockets.

    Problem is because the ends of these PDUs have 16amp and 32amp commando sockets. I want to temporarily just use these on the mains until the UPS are installed. Which could at least another month or two.

    I can take of the commando sockets as its seems to be modular in design and I can see the normal plug wiring like earth, nuetral and Live.

    Would I be able to do this as long as I don't over provision the sockets.

    I have 2 x 16amp PDU's and 2 X 32 amp PDUs. I noticed that the 32amp version as much more of a thicker cable. I am assuming because it probably has more resistance but I could stick a 13 amp plug on this as well?

    As you can tell from my questions, my knowledge on electrical is non existent so any helpful advice that you can advise would be great.

    Thanks

  2. #2
    Chris_'s Avatar
    Join Date
    Jul 2010
    Location
    UK
    Posts
    691
    Thank Post
    134
    Thanked 115 Times in 98 Posts
    Rep Power
    44
    Yes. You could just wire 13a plugs on the end. You might have a problem getting a 13a plug to fit due to the gauge or wire so it might be easier to get some adapters like a 13a -> 16a and a 13a -> 32a.

  3. Thanks to Chris_ from:

    ranj (8th October 2011)

  4. #3
    ranj's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    730
    Thank Post
    98
    Thanked 42 Times in 32 Posts
    Rep Power
    25
    I dont understand what you mean by the adapter. Do you have a picture??

    Quote Originally Posted by Chris_ View Post
    Yes. You could just wire 13a plugs on the end. You might have a problem getting a 13a plug to fit due to the gauge or wire so it might be easier to get some adapters like a 13a -> 16a and a 13a -> 32a.

  5. #4
    Chris_'s Avatar
    Join Date
    Jul 2010
    Location
    UK
    Posts
    691
    Thank Post
    134
    Thanked 115 Times in 98 Posts
    Rep Power
    44
    13a -> 16a 16A, 240V SOCKET TO 13A PLUG - IS1053 - PRO ELEC
    13a -> 32a http://www.vikinglighting.co.uk/cata...able/13-32.jpg

    Just means that you don't need to re-wire the plugs and try to get the 32a cable into a 13a plug.

  6. #5

    Oaktech's Avatar
    Join Date
    Jul 2011
    Location
    Bournemouth
    Posts
    2,840
    Thank Post
    785
    Thanked 552 Times in 432 Posts
    Rep Power
    261
    how much current are you going to draw in reality?

    work out how much current you are using worst case and then decide whether you can legitimately use an adapter, or if you need to get an electrician to fit some temporary power.

    max rated amps is max rated amps, you can't suck more than that out of the cable,

    16a is about 3800 watts, 32 is about 7600 watts roughly.

SHARE:
+ Post New Thread

Similar Threads

  1. Changing display name to userlogon name
    By Theblacksheep in forum Windows Server 2008
    Replies: 2
    Last Post: 14th September 2010, 05:38 PM
  2. Replies: 4
    Last Post: 22nd July 2010, 12:54 PM
  3. Changing from Sleuth to SIMS for behaviour monitoring
    By IT_Man_Dan in forum MIS Systems
    Replies: 2
    Last Post: 28th March 2010, 06:22 AM
  4. ex-RAID drive return to normal size?
    By contink in forum Hardware
    Replies: 2
    Last Post: 8th June 2009, 06:46 PM
  5. Replies: 1
    Last Post: 15th October 2007, 08:47 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •