    UPS For Server Cupboard

    Hello All,

    I'm currently figuring out what work needs doing to our two server cupboards over the summer. The idea is that we have two cupboards, in separate wings of the school, so if something diasaterous happens to one then the other is left to keep running. This only works up to a point at the moment - the second server cupboard has no cooling and tends to get good and toasty, and the UPS didn't handle testing so well today ("Power's off, is stuff still running?", "No.", "Bother.").

    I have environment monitoring sorted out - simply a PC with a temperature sensor and UPS-monitoring cable plugged in. It's set to turn itself off if running on battery for more than a minute or if the temperature gets too high, then I plan to have another PC monitoring that.

    The UPS currently in use is an APC Smart-UPS 750. Simply switching the power off to it made the two machines attached to it fail, which makes it a bit pointless. Is that failure maybe just due to an aged bettery, or is there possibly a different brand of UPS that people would recommend?

    --
    David Hicks

  2. #2
    ChrisH's Avatar
    Join Date
    Jun 2005
    Location
    East Lancs
    Posts
    4,996
    Thank Post
    120
    Thanked 280 Times in 258 Posts
    Rep Power
    106
    It will likely be the batteries. They look all nice and charged until you actually try to use them and they say not today thank you!

  3. Thanks to ChrisH from:

    dhicks (16th June 2010)

  4. #3

    3s-gtech's Avatar
    Join Date
    Mar 2009
    Location
    Wales
    Posts
    2,697
    Thank Post
    143
    Thanked 542 Times in 486 Posts
    Rep Power
    148
    We have an identical setup which I'm currently working on, responses will be interesting. I'd like a small air-con unit and UPS for the second cupboard, but may be a bit pushed!

  5. #4

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by ChrisH View Post
    It will likely be the batteries. They look all nice and charged until you actually try to use them and they say not today thank you!
    The monitoring software (APC's PowerChute Business Edition, monitoring the UPS via serial as USB failed to work for some reason) says the UPS has 23 minutes runtime left, however actual runtime is 0 (cut the power, everything stops). With the failed USB and dodgy readouts I'm inclined to get a whole new UPS - I don't want to get new batteries to find that the UPS still doesn't work reliably.

    --
    David Hicks

  6. #5

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by 3s-gtech View Post
    We have an identical setup which I'm currently working on, responses will be interesting. I'd like a small air-con unit and UPS for the second cupboard, but may be a bit pushed!
    The cheap-as-possible temperature sensor from eBay is currently reporting a temperature of 31C - I've just borrowed a thermometer from science to double-check that's accurate. I'm guessing it's got a lot hotter in there in the past, though - there's only one server running in there now as the other one packed up, I think from overheating. I was maybe thinking of a floor-standing air conditioner capable of a "ton" of cooling (1200 BTUs, I think) - around 500 from Argos, which seems pretty resonable for an all-in-one, drop-in solution.

    --
    David Hicks

  7. #6


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,618
    Thank Post
    275
    Thanked 777 Times in 604 Posts
    Rep Power
    223
    Quote Originally Posted by dhicks View Post
    With the failed USB and dodgy readouts I'm inclined to get a whole new UPS - I don't want to get new batteries to find that the UPS still doesn't work reliably.
    It'll require some downtime, but does the other UPS use the same batteries? It's a cheap test if it does - swap them for a test and give it a dummy load (stuff without data on) and see how well it fares.

  8. Thanks to pete from:

    dhicks (16th June 2010)

  9. #7

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by pete View Post
    It'll require some downtime, but does the other UPS use the same batteries?
    Good point, thanks. We've got a Smart-UPS 1000 and 1000XL in the other server cupboard, it's worth a check to see if they are battery-compatible.

    --
    David Hicks

  10. #8

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    10,986
    Thank Post
    850
    Thanked 2,652 Times in 2,252 Posts
    Blog Entries
    9
    Rep Power
    764
    A smartUPS 750 is quite small for a two PC load let alone a two server one, it is probably the batteries but it could also very well be pulling too much current for the unit itself to supply when on battery power. I would be looking at a 1500 for a couple of machines just to give it the overhead, this should also give you longer runtimes for the servers in the case of a short powercut or something simmilar.

  11. Thanks to SYNACK from:

    dhicks (16th June 2010)

  12. #9

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by SYNACK View Post
    A smartUPS 750 is quite small for a two PC load let alone a two server one
    Good point - I think we're going to be maybe looking at the 2200. The cupboard will have at least four machines running in it: mirroring VM server, backup file server, video file server and environment monitoring PC, plus a network switch. Power only has to last long enough for the monitoring software to register the fact and gracefully shut everything down, so 5 to 10 minutes should be fine.

    --
    David Hicks

  13. #10
    rsenior's Avatar
    Join Date
    Mar 2009
    Posts
    22
    Thank Post
    0
    Thanked 1 Time in 1 Post
    Rep Power
    0
    Hi Dave ,
    Have look at this link :UPS Selector Sizing Applications

    It will give you a good idea of what to buy load wise . We use r5000va on all of our server cupboards(most have 5 or more server +switches, etc) and they are excellent.Comes with temp. shutdown and web interfaced software. Always worth checking the load rate on the ups ,most of the larger units require a 30amp supply and you should have a clean earth on the cab.

  14. #11

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by rsenior View Post
    Have look at this link
    Thanks, but a bit pricey for us - we might be able to stretch to a Smart-UPS 2200, but anything beyond that would be pushing it a bit.

    --
    David Hicks

  15. #12

    Join Date
    May 2010
    Location
    Lancashire/Yorkshire
    Posts
    43
    Thank Post
    2
    Thanked 10 Times in 8 Posts
    Rep Power
    0
    david

    sory to jump on the thread - but if we can help you out in quoting for the UPS please do let me know.

    kind regards

    zak

  16. #13

    dhicks's Avatar
    Join Date
    Aug 2005
    Location
    Knightsbridge
    Posts
    5,611
    Thank Post
    1,226
    Thanked 772 Times in 670 Posts
    Rep Power
    234
    Quote Originally Posted by VirtueTechnologies View Post
    if we can help you out in quoting for the UPS please do let me know.
    I'm trying to figure out what sort of size of UPS we're likly to be looking at, first. I think our second server cupboard is likly to wind up containing a server running a bunch of virtual machines, a large (12 SATA disks) file server and a smaller (4 SATA disks) file server. It will also contain a PC set up to monitor power and temperature, and there's a 16-port network switch, but those can run off a Back-UPS 350. Some room for future expansion would probably be a good idea. How much power are those three servers, some with lots of disks, likely to draw? Do I allow 1KW each for them, or is that being a bit excessive? What UPSes do you sell - just APC, or can you particularly recommend another brand?

    --
    David Hicks
    Last edited by dhicks; 17th June 2010 at 10:10 AM.

  17. #14

    Join Date
    May 2010
    Location
    Lancashire/Yorkshire
    Posts
    43
    Thank Post
    2
    Thanked 10 Times in 8 Posts
    Rep Power
    0
    Hello David

    i think you approach is right its better to be safe than sorry.

    This UPS should suffice, we always recommend APC for their reliability

    SUA1500RMI2U

    We also recommend a management card to allow graceful shutdown of all servers

    AP9630

    Maybe worth searching the web/APC website to get the specs for the above products.

    regards

    Zak

  18. #15

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    10,986
    Thank Post
    850
    Thanked 2,652 Times in 2,252 Posts
    Blog Entries
    9
    Rep Power
    764
    I'd look at the detailed specs of each of the bits that you are looking at using and seeing how much power it is likely to use Internal Hard Drive | Barracuda XT Desktop Hard Drive | Seagate | Seagate

    I'd then double what you come up with for overhead and future expantion and aim for that. Most hardware will have current draw specs and if not just make an estimate on the generous side for the device. This is easier with some equipment from major manufacturers as there is are lots of load calculators that will help size the ups as have been suggested before.

SHARE:
+ Post New Thread
Page 1 of 3 123 LastLast

Similar Threads

  1. hyper v server 2008 r2 and ups
    By sted in forum Windows Server 2008 R2
    Replies: 16
    Last Post: 28th March 2012, 04:18 PM
  2. UPS Internal Temp or Server ?
    By mattx in forum Hardware
    Replies: 2
    Last Post: 18th November 2009, 02:15 PM
  3. Laptop cupboard
    By L_Smith in forum Hardware
    Replies: 4
    Last Post: 4th September 2009, 02:06 PM
  4. planning to turn my airing cupboard into server room at home
    By itwasntme in forum How do you do....it?
    Replies: 18
    Last Post: 14th August 2009, 04:34 PM
  5. Server and UPS
    By plexer in forum Our Advertisers
    Replies: 3
    Last Post: 9th June 2009, 03:20 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •