Hardware Thread, Server CPU Temp at 87c! in Technical; It wont run for that Xeon chip...
  1. #16

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    It wont run for that Xeon chip

  2. #17

    Join Date
    Aug 2005
    Location
    London
    Posts
    3,157
    Thank Post
    116
    Thanked 529 Times in 452 Posts
    Blog Entries
    2
    Rep Power
    124
    Does sound a bit high :-)

    We have a threshold temp of 35C; above that alarms go off and people fix things ASAP (I know that there was a problem last night, for example)

    You need to get some of this: TROX | Data Centres

    The liquid CO2 cooling basically puts an extra "door" behind your server racks. This contains the liquid CO2 coolant and so air drawn through it is cooled. It's much more efficient than blowing air randomly into a server room and hoping some of it gets to the servers!

  3. #18

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,193
    Thank Post
    875
    Thanked 2,720 Times in 2,303 Posts
    Blog Entries
    11
    Rep Power
    781
    Assuming the sensors are correct this is probably the break down of the thermal compound between the CPU and its heatsink. Over time and with moisture or contaminants this compound does break down and no longer conducts heat properly to the heatsink.

    First remove the old compound (Arctic Silver do a great cleaning product ArctiClean by Arctic Silver) and then apply some new high performance thermal compound to the CPU. This should better thermally link the CPU and heatsink allowing the fans and cold air to cool it properly.

  4. Thanks to SYNACK from:

    CHR1S (25th May 2010)

  5. #19

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    Quote Originally Posted by srochford View Post
    Does sound a bit high :-)

    We have a threshold temp of 35C; above that alarms go off and people fix things ASAP (I know that there was a problem last night, for example)

    You need to get some of this: TROX | Data Centres

    The liquid CO2 cooling basically puts an extra "door" behind your server racks. This contains the liquid CO2 coolant and so air drawn through it is cooled. It's much more efficient than blowing air randomly into a server room and hoping some of it gets to the servers!
    Server Racks? The servers sit in a store room, no aircon .....


    Quote Originally Posted by SYNACK View Post
    Assuming the sensors are correct this is probably the break down of the thermal compound between the CPU and its heatsink. Over time and with moisture or contaminants this compound does break down and no longer conducts heat properly to the heatsink.

    First remove the old compound (Arctic Silver do a great cleaning product ArctiClean by Arctic Silver) and then apply some new high performance thermal compound to the CPU. This should better thermally link the CPU and heatsink allowing the fans and cold air to cool it properly.
    The heatsink is red hot to the touch, I just think the ambient temperature for the room is just too much for the type of server, with it being a rackmount (minus the rack and proper cooling)

  6. #20
    Butuz's Avatar
    Join Date
    Feb 2007
    Location
    Wales, UK
    Posts
    1,579
    Thank Post
    211
    Thanked 220 Times in 176 Posts
    Rep Power
    63
    What is the ambient temperatuture in your room? If its 30 or more then yes you just need to get air con!!

    If ambient is low (under 25) it could indicate a problem with the cpu fan / heatsink itself.

    Butuz

  7. Thanks to Butuz from:

    CHR1S (25th May 2010)

  8. #21

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    Ambient temperature is 20c, server temps are as follows -

    1 IO Board 34 C
    2 CPU 63 C
    4 Power Supply 25
    5 System 24 C

  9. #22
    Mako's Avatar
    Join Date
    Apr 2009
    Location
    North Yorkshire
    Posts
    441
    Thank Post
    51
    Thanked 108 Times in 82 Posts
    Rep Power
    71
    Echoing SYNACK's suggestion here. Try applying some new thermal paste. You need to remove possible problems before isolating the fault. You'd be suprised at the heat build up caused by crumbly old thermal solution, especially the stock stuff. Clean it off and throw some Arctic Silver on it, or equivalent, and see if it makes a difference. Your other temperatures seem to be within reasonable operating ranges, so I would look at the heatsink/cpu contact first. If there's more than one server in that room, and no others are throwing up overheating errors, then it points to the individual machine's cooling efficiency. Ambient temperature is fine.

  10. Thanks to Mako from:

    CHR1S (25th May 2010)

  11. #23

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    Ok, will give the thermal compound a go and report back.

    Thanks

  12. #24

    tmcd35's Avatar
    Join Date
    Jul 2005
    Location
    Norfolk
    Posts
    5,727
    Thank Post
    859
    Thanked 905 Times in 750 Posts
    Blog Entries
    9
    Rep Power
    330
    Quote Originally Posted by Hightower View Post
    Please ensure you take photo's of your injuries. I doubt they'll help much in your legal case, but if you post them up here we'll be sure to get a laugh out of them =P
    Oh, I dunno - I'm sure pictures of the 'Intel Inside' tongue tatoo will make for some pretty compelling evidence

  13. #25

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    Well, I stripped and cleaned the CPU and HS then applied the Arctic Silver 5 and set it all back up again. It seems to idle at 65c and with less than 1 minute of prime95 it went mental hit 87c and was still climbing and shut down

    Going to let it settle over night then check the compound tomorrow and re-apply etc. as required.

  14. #26
    danrhodes's Avatar
    Join Date
    Sep 2008
    Location
    Wath Upon Dearne
    Posts
    1,513
    Thank Post
    157
    Thanked 181 Times in 150 Posts
    Rep Power
    68
    Is the heat sink sitting flush up to the top of the chip, remove it and you will be able to tell due to the marks the thermal paste has left behind.

    If not it may be a new chip as this one sounds as though its screwed, either that or theres a voltage problem and the mobo is supplying too much juice, have you checked your voltages in BIOS?

    D

  15. #27

    CHR1S's Avatar
    Join Date
    Feb 2006
    Location
    Birmingham
    Posts
    4,505
    Thank Post
    1,585
    Thanked 486 Times in 304 Posts
    Rep Power
    217
    I had a brain wave last night, when I was redoing the paste I noticed that with it being single CPU that the second socket was free and we all know stuff likes to take the path of least resistance decided to block off the CPU socket.

    Now with the air being forced through the heatsink instead of the free socket its an amazing 15c cooler!!

    Piece of cardboard 1 - HP Server 0

  16. #28
    danrhodes's Avatar
    Join Date
    Sep 2008
    Location
    Wath Upon Dearne
    Posts
    1,513
    Thank Post
    157
    Thanked 181 Times in 150 Posts
    Rep Power
    68
    Good idea, but has it really solved your issues, are there other underlying problems that could escalate if left untouched, if so you may have a dead server on your hands one day if your guna call it fixed by using a bit of cardboard!?

  17. #29

    Michael's Avatar
    Join Date
    Dec 2005
    Location
    Birmingham
    Posts
    9,262
    Thank Post
    242
    Thanked 1,572 Times in 1,252 Posts
    Rep Power
    340
    Correct me if I am wrong, but the 3.4Ghz Irwindale is the same generation/slight revision of the Pentium 4 Prescott branded a Xeon. These always ran incredibly hot and are comparably poor compared to newer Xeon's or Core 2 Duo/Quad.

    As already suggested re-applying thermal paste may improve the temperature, but you may also want to consider a larger heatsink + fan. The heatsink can make a huge difference.

  18. #30
    danrhodes's Avatar
    Join Date
    Sep 2008
    Location
    Wath Upon Dearne
    Posts
    1,513
    Thank Post
    157
    Thanked 181 Times in 150 Posts
    Rep Power
    68
    Yep your correct they are the offspring of the Prescott Core.

    A slightly updated core called "Irwindale" was released in early 2005, with 2 MB L2 cache and the ability to have its clock speed reduced during low processor demand. Both of these Prescott-derived Xeons have the product code 80546

SHARE:
+ Post New Thread
Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. UPS Internal Temp or Server ?
    By mattx in forum Hardware
    Replies: 2
    Last Post: 18th November 2009, 02:15 PM
  2. Citrix Presentation Server with 100% CPU Usage
    By jack0w in forum Windows Server 2000/2003
    Replies: 0
    Last Post: 9th October 2009, 12:15 PM
  3. Server CPU Usage at 100%
    By DSapseid in forum Windows
    Replies: 14
    Last Post: 5th December 2008, 10:07 PM
  4. temp or temp to perm sharepoint install engineer £neg
    By SpecialAgent in forum Educational IT Jobs
    Replies: 1
    Last Post: 20th March 2008, 10:15 AM
  5. CPU on server at 100%
    By kennysarmy in forum Windows
    Replies: 5
    Last Post: 16th March 2008, 10:55 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •