Hardware Thread, UPS runtime - what's your set up? in Technical; Hello, We have a few APC UPSs here at the school, powering all servers, all with network shut down etc ...
  1. #1

    Join Date
    Jan 2007
    Location
    The Console
    Posts
    234
    Thank Post
    22
    Thanked 29 Times in 23 Posts
    Rep Power
    21

    Question UPS runtime - what's your set up?

    Hello,

    We have a few APC UPSs here at the school, powering all servers, all with network shut down etc However currently these are set to shut down servers after about 3 minutes on battery due to load vs runtime with a buffer for shut down delays etc.

    We've just allowed remote access to our students meaning they can log in from home....which has led me to think that just because the school has a power cut, those students 10 or 20 miles away won't so it would be nice if they could work uninterrupted. Looking at options, I could get an additional battery for my UPS to increase (for example) full load run time from 8 mins to 40 minutes, getting over the problem of short local power cuts.

    What do you do at your school? Do you just have a standard UPS which shuts stuff done, and tough luck to remote users? Or, do you have a power system which will run for hours?

    Thanks for any replies!

  2. #2


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,537
    Thank Post
    271
    Thanked 752 Times in 590 Posts
    Rep Power
    218
    Does your server room need aircon/forced air to keep within acceptable operating temperatures? That's our limiting factor.

  3. #3
    Duke's Avatar
    Join Date
    May 2009
    Posts
    1,014
    Thank Post
    300
    Thanked 172 Times in 158 Posts
    Rep Power
    57
    If I shut down a few non-essential servers then I can get about 15-20 minutes off the main UPS and roughly the same off the SAN UPS. Nowhere near as long as I'd like if I don't shut some stuff down, and the big aircon isn't UPS'd so it gets hot quick in summer. Very much not ideal, although virtualising will help us hugely in this area (less physical servers, DR/failover site). I'd want at least 10 minutes to get everything shut down so it sounds like you could do with an upgrade (don't forget about things like redundant UPS's and putting dual power supplies on servers onto different UPS's), but my biggest concern would be time for clean server shutdowns and handling short outages with no downtime rather than keeping remote users happy.

    Power outages are an 'oh s**t' situation that shouldn't ever be my department's fault or responsibility, so if there is downtime caused by them I wouldn't expect people to blame me (unless someone had offered me the budget for a huge UPs and generator and I'd turned it down!).

    Chris

  4. #4

    Join Date
    Jan 2007
    Location
    The Console
    Posts
    234
    Thank Post
    22
    Thanked 29 Times in 23 Posts
    Rep Power
    21
    That's a very good point and one that escaped my mind We have air con, but the particular conditioner we have does not automatically come back on after a power cut, so that would be a bit of a problem!

SHARE:
+ Post New Thread

Similar Threads

  1. Italc runtime errors
    By superatticman in forum Network and Classroom Management
    Replies: 0
    Last Post: 18th November 2009, 04:02 PM
  2. Activprimary 3 runtime error 9
    By bladedanny in forum Educational Software
    Replies: 7
    Last Post: 24th September 2009, 10:39 AM
  3. How common is the Silverlight runtime ?
    By autismuk in forum Windows
    Replies: 4
    Last Post: 13th May 2009, 11:01 PM
  4. [For Sale] Promethean 32 set Activote Set (Brand New)
    By lgfl_it_guy in forum Classified Adverts
    Replies: 20
    Last Post: 8th February 2009, 11:41 AM
  5. Updating Java Runtime
    By ITWombat in forum Windows
    Replies: 3
    Last Post: 18th May 2006, 12:44 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •