    UPS Advice

    really need some help with UPS' please

    is there a logic set/rules for number of UPS' per server? ie they have many outputs for power but only one for RS232. my predecessor didnt seem to have much of an idea and nor do i.

    at present i am rearranging the server cab and struggling to find space.

    also do you guys and gal leave much space between servers, UPS'?

    looks like we are going to have to upgrade our air con too lol

    at present in our server cab we have-
    • server 1
    • server 2
    • server 3
    • mis server
    • web server
    • exchange server
    • nas 1
    • nas 2
    • smartcache


    we will have
    • server 4
    • server 5
    • admin server
    • terminal server
    • gateway server


    UPS wise we have
    • APC 750
    • APC 750
    • APC 1000
    • APC 1500
    • APC 3000
    • APC 3000


    Waiting to go in (somewhere!)
    APC 1500
    and another in storage (cant remember what one tho)

  2. #2

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,528
    Thank Post
    513
    Thanked 2,406 Times in 1,862 Posts
    Blog Entries
    24
    Rep Power
    822
    Seems like a lot of individual UPSes? I have a similar number of servers, but with 2 APC 5000's, each with its own 16A power ring. These are networked, and soon (when I get round to it) all the connected servers will get the network shutdown software installed. The switch is also on the UPS (well, on both in fact, dual PSUs).

    Any possibility that you can get rid of that giant stack of UPSes and replace em with a couple of large ones?

    Regarding space - no. Any space has stuff in it. I've got a total of 2U spare in our server cab.

  3. Thanks to localzuk from:

    gibbo_ap (6th April 2010)

  4. #3
    gibbo_ap's Avatar
    Join Date
    Nov 2007
    Location
    Staffs, UK
    Posts
    937
    Thank Post
    233
    Thanked 81 Times in 64 Posts
    Rep Power
    36
    Quote Originally Posted by localzuk View Post
    Seems like a lot of individual UPSes? I have a similar number of servers, but with 2 APC 5000's, each with its own 16A power ring. These are networked, and soon (when I get round to it) all the connected servers will get the network shutdown software installed. The switch is also on the UPS (well, on both in fact, dual PSUs).

    Any possibility that you can get rid of that giant stack of UPSes and replace em with a couple of large ones?

    Regarding space - no. Any space has stuff in it. I've got a total of 2U spare in our server cab.
    cheers would, say, the two APC 3000 plus a APC 1500 be enough? ...... oh i forgot one more thing going in!!! my server console! :P that needs 1U, and i have that allocated for the gateway server aggg. i hate servers lol

  5. #4

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    15,773
    Thank Post
    865
    Thanked 1,663 Times in 1,448 Posts
    Blog Entries
    11
    Rep Power
    442
    We stick an APC 3000 on every server eeekk

    What sort of spec are your servers? How power Hungary are they?

  6. Thanks to FN-GM from:

    gibbo_ap (6th April 2010)

  7. #5

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,528
    Thank Post
    513
    Thanked 2,406 Times in 1,862 Posts
    Blog Entries
    24
    Rep Power
    822
    What's the goal of the UPSes? ie. is the intention to allow servers just to turn off? Or more to allow them to allow to run for a while?

    A 3kW UPS per server is well overkill IMO, unless you have major power issues in your building.

  8. Thanks to localzuk from:

    gibbo_ap (6th April 2010)

  9. #6

    Join Date
    Jan 2009
    Location
    England
    Posts
    1,479
    Thank Post
    297
    Thanked 304 Times in 263 Posts
    Rep Power
    82
    We have two 10kva hardwired UPS for the entire server room. These each feed a PDU in the server racks. All servers/switches connect to both of these PDUs to ensure that all servers are connected to more than one UPS

  10. Thanks to Soulfish from:

    gibbo_ap (6th April 2010)

  11. #7


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,619
    Thank Post
    275
    Thanked 777 Times in 604 Posts
    Rep Power
    223
    You don't want to leave gaps because it allows airflow to slip between servers, rather than going through them. If you need to leave space for whatever reason, use a blanking panel.

    Regarding UPS sizing you basically work it out like:

    What's the maximum draw of $bunch_of_kit?
    If power goes out, how long can we keep kit running without aircon before it overheats?
    Historically, how long are our power outages?
    Historically, what's the "yeah, it'll be off for a while" point?
    Plus room for expansion / fudge factor.

    APC have a sizing tool on their site.

  12. Thanks to pete from:

    gibbo_ap (6th April 2010)

  13. #8
    gibbo_ap's Avatar
    Join Date
    Nov 2007
    Location
    Staffs, UK
    Posts
    937
    Thank Post
    233
    Thanked 81 Times in 64 Posts
    Rep Power
    36
    Quote Originally Posted by localzuk View Post
    What's the goal of the UPSes? ie. is the intention to allow servers just to turn off? Or more to allow them to allow to run for a while?

    A 3kW UPS per server is well overkill IMO, unless you have major power issues in your building.
    more to give them the shutdown in my eyes... the stations are going to be off anyway if there is a power cut, the only thing that it would inturupt would be the cbs

  14. #9

    john's Avatar
    Join Date
    Sep 2005
    Location
    London
    Posts
    10,498
    Thank Post
    1,488
    Thanked 1,049 Times in 918 Posts
    Rep Power
    301
    Make sure you have, if funds allow, 2 UPS's, I am at my wits end with the stupid APC ones we have 2 out of the 3 are now faulty and as a result they randomly turn off, I'm still juggling power leads around to try and get all dual powered kit onto a good one and a bad one / the mains instead to stop us falling over weekly. You want them all network connected and don't forget your switches and router to ensure that they stay in if you have a power failure so it can email you (we will be putting the one good one we have left in the cabinet with that kit in as its elsewhere) and then a large new UPS (or2 smaller ones) in the main Server Room to power all the new kit we have.

    I don't go near APC UPS's now and only use MGE UPS's, they bought APC out but you can buy there own brand still which are good, they are known as MGE Comet and MGE Comet Extreme the UPSs and are still available.

  15. Thanks to john from:

    gibbo_ap (6th April 2010)

  16. #10

    Ric_'s Avatar
    Join Date
    Jun 2005
    Location
    London
    Posts
    7,590
    Thank Post
    109
    Thanked 762 Times in 593 Posts
    Rep Power
    180
    My initial advice is to check out UPS Selector Sizing Applications as that will give you an idea of what to run there.

    In an ideal world, you would stick two chunky UPSs with a NIC and environmental monitoring card into the bottom of each rack. These UPSs would then each power a vertical PDU. Your kit would then be plugged into both UPSs (assuming dual PSUs).

    You would probably want to use different sources for the power too to give you a chance of keeping a power source if one goes west.

    Of course, this is an ideal situation. I have one 7.5kVA UPS powering 2 racks with the second PSUs on the servers directly connected to a 'clean' mains supply.

  17. Thanks to Ric_ from:

    gibbo_ap (6th April 2010)

  18. #11
    gibbo_ap's Avatar
    Join Date
    Nov 2007
    Location
    Staffs, UK
    Posts
    937
    Thank Post
    233
    Thanked 81 Times in 64 Posts
    Rep Power
    36
    Thanks all. I have now wired up all servers to the 3000s I will be taking some off to a 1500 and then deciding what do with the rest. To heavy for eBay lol jk. Need the space and we seem to be ups mad. Lol. Way can I get fill the space..... I actually want to virtualize some. Print server n smart cache for start. No idea where to start n don't want to yet. To much happening as u can c with the 'servers to come list'

  19. #12
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    47
    Quote Originally Posted by Ric_ View Post
    My initial advice is to check out UPS Selector Sizing Applications as that will give you an idea of what to run there.

    In an ideal world, you would stick two chunky UPSs with a NIC and environmental monitoring card into the bottom of each rack. These UPSs would then each power a vertical PDU. Your kit would then be plugged into both UPSs (assuming dual PSUs).

    You would probably want to use different sources for the power too to give you a chance of keeping a power source if one goes west.

    Of course, this is an ideal situation. I have one 7.5kVA UPS powering 2 racks with the second PSUs on the servers directly connected to a 'clean' mains supply.
    how do you ensure a clean supply without a second ups ?

    it's my understanding that you can't get a truly clean supply on the cheap.
    Last edited by torledo; 6th April 2010 at 09:24 PM.

  20. Thanks to torledo from:

    gibbo_ap (7th April 2010)

SHARE:
+ Post New Thread

Similar Threads

  1. UPS - No. per UPS?
    By owen1978 in forum Hardware
    Replies: 29
    Last Post: 15th December 2009, 01:12 PM
  2. UPS.....
    By IanT in forum Hardware
    Replies: 12
    Last Post: 10th September 2009, 08:44 AM
  3. CV advice, and general Job searching advice
    By mossj in forum Educational IT Jobs
    Replies: 14
    Last Post: 14th May 2009, 09:32 PM
  4. New UPS
    By harris-gav in forum Hardware
    Replies: 17
    Last Post: 18th March 2008, 05:49 PM
  5. ups
    By russdev in forum Wireless Networks
    Replies: 14
    Last Post: 20th January 2006, 07:34 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •