    UPS - No. per UPS?

    I got a SmartUPS 1000

    Which is powering 3 servers and a monitor.
    Is that too much for it to handle?

    The local council Brum, say that each curriculum and admin server
    should have their own UPS?

    Thanks

  2. #2


    Join Date
    Jul 2007
    Location
    Rural heck
    Posts
    2,662
    Thank Post
    120
    Thanked 434 Times in 353 Posts
    Rep Power
    126
    If it's a CRT, do not pass go, do not collect 200, disconnect it now.

    If it's a TFT, it's still well underspecced. I'd have either a 1000 for each server, or maybe a 1500 for two. Although it depends how big the servers are.

    Have you actualy tested to see how much run time you get when you pull the plug.

  3. #3
    Jamman960's Avatar
    Join Date
    Sep 2007
    Location
    London/Kent
    Posts
    988
    Thank Post
    186
    Thanked 194 Times in 156 Posts
    Rep Power
    46
    I'd imagne with that load you'll get very little run time, probably not enough to shut down the servers.

    Have a look at the load LED's on the front, I'd imagine most if not all will be lit.

    SmartUPS 1000:
    Typical Backup Time at Half Load 20.6 minutes (335 Watts)
    Typical Backup Time at Full Load 6.1 minutes (670 Watts)

  4. #4

    Edu-IT's Avatar
    Join Date
    Nov 2007
    Posts
    7,139
    Thank Post
    403
    Thanked 622 Times in 568 Posts
    Rep Power
    181
    Quote Originally Posted by Jamman960 View Post
    I'd imagne with that load you'll get very little run time, probably not enough to shut down the servers.

    Have a look at the load LED's on the front, I'd imagine most if not all will be lit.

    SmartUPS 1000:
    Typical Backup Time at Half Load 20.6 minutes (335 Watts)
    Typical Backup Time at Full Load 6.1 minutes (670 Watts)
    Should these lights be lit all the time?

  5. #5

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,680
    Thank Post
    516
    Thanked 2,451 Times in 1,897 Posts
    Blog Entries
    24
    Rep Power
    832
    Quote Originally Posted by Edu-IT View Post
    Should these lights be lit all the time?
    They indicate load, so if you want a long run time on battery, then you want as few as possible lit.

  6. #6

    Michael's Avatar
    Join Date
    Dec 2005
    Location
    Birmingham
    Posts
    9,262
    Thank Post
    242
    Thanked 1,568 Times in 1,250 Posts
    Rep Power
    340
    You can quite comfortably run two servers off a UPS, but as others have stated, this'll typically reduce your backup power in the event of a power cut.

    If you install the APC software this will give you fairly accurate readings how high the power consumption is. Alternatively there will be two readings on the front. One for the battery (which should be full 5 out of 5) and the second for how much the servers are using. Realistically this shouldn't be anymore than 3/4 out of 5.

  7. #7

    Join Date
    Nov 2009
    Posts
    114
    Thank Post
    0
    Thanked 9 Times in 9 Posts
    Rep Power
    11
    On the front;

    Battery 5 out 5
    Load (or No. Devices connected, its got a picture of a computer?) 3/5

    Just checked the APC Powerchute console - no big errors apart from the battery age
    Last edited by owen1978; 14th December 2009 at 03:09 PM.

  8. #8
    Number6's Avatar
    Join Date
    Feb 2009
    Location
    Worcester, UK
    Posts
    457
    Thank Post
    2
    Thanked 9 Times in 8 Posts
    Rep Power
    13
    We use a 1500 UPS for each server and a further one that powers the server room switches, 2 x CDPs, a KVM, ADSL modem and a pull-out rack keyboard & monitor thingy.

  9. #9

    Join Date
    Nov 2009
    Posts
    114
    Thank Post
    0
    Thanked 9 Times in 9 Posts
    Rep Power
    11
    Also just checked the UPS Load in the console its at 50%

  10. #10
    Jamman960's Avatar
    Join Date
    Sep 2007
    Location
    London/Kent
    Posts
    988
    Thank Post
    186
    Thanked 194 Times in 156 Posts
    Rep Power
    46
    PowerChute should also give you an estimated runtime, if the time given is enough to shutdown the servers(probably 15mins+) I'd say your ok with the UPS you have.

  11. #11

    teejay's Avatar
    Join Date
    Apr 2008
    Posts
    3,176
    Thank Post
    284
    Thanked 773 Times in 583 Posts
    Rep Power
    335
    Also, if you are running redundant psu's in your servers then ideally they should be plugged into seperate UPS's. You can do this by sharing 2 UPS's between 2 servers.

  12. #12

    Edu-IT's Avatar
    Join Date
    Nov 2007
    Posts
    7,139
    Thank Post
    403
    Thanked 622 Times in 568 Posts
    Rep Power
    181
    Ours is showing no load on the front so I'm not convinced it's working?

  13. #13
    Jamman960's Avatar
    Join Date
    Sep 2007
    Location
    London/Kent
    Posts
    988
    Thank Post
    186
    Thanked 194 Times in 156 Posts
    Rep Power
    46
    Quote Originally Posted by Edu-IT View Post
    Ours is showing no load on the front so I'm not convinced it's working?
    What UPS is it and how many servers are hanging off it?

    Also what does powerchute say regarding load etc?

    James

  14. #14
    GorgeousGeorge's Avatar
    Join Date
    Dec 2009
    Location
    New York, New York
    Posts
    2
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Quote Originally Posted by owen1978 View Post
    I got a SmartUPS 1000

    Which is powering 3 servers and a monitor.
    Is that too much for it to handle?

    The local council Brum, say that each curriculum and admin server
    should have their own UPS?

    Thanks

    If the unit doesn't have over 80% load on it and you're satisfied with the run time, you'd be good to go. If you're unhappy with the runtime, feel it's too short or don't have enough time to safely shut down, you need to get a different UPS.

    Sizing UPSs is tricky, you want enough but not too much, if you have too much it costs longer in the long run as maintenance is more expensive.

    How often do you have power outages?

  15. #15

    Join Date
    Nov 2009
    Posts
    114
    Thank Post
    0
    Thanked 9 Times in 9 Posts
    Rep Power
    11
    Quote Originally Posted by GorgeousGeorge View Post
    If the unit doesn't have over 80% load on it and you're satisfied with the run time, you'd be good to go. If you're unhappy with the runtime, feel it's too short or don't have enough time to safely shut down, you need to get a different UPS.

    Sizing UPSs is tricky, you want enough but not too much, if you have too much it costs longer in the long run as maintenance is more expensive.

    How often do you have power outages?
    I've got it to initiate a shutdown sequence as soon as its been on battery for a minute, the curric
    server then runs the default.cmd script which then sends a shutdown command to the admin server.

    Once a year probably, rather be safe than sorry!

SHARE:
+ Post New Thread
Page 1 of 2 12 LastLast

Similar Threads

  1. UPS.....
    By IanT in forum Hardware
    Replies: 12
    Last Post: 10th September 2009, 08:44 AM
  2. What UPS?
    By CHR1S in forum Hardware
    Replies: 6
    Last Post: 1st May 2009, 07:21 AM
  3. New UPS
    By harris-gav in forum Hardware
    Replies: 17
    Last Post: 18th March 2008, 05:49 PM
  4. Which UPS?
    By Ste_Harve in forum Hardware
    Replies: 7
    Last Post: 9th November 2007, 09:41 AM
  5. ups
    By russdev in forum Wireless Networks
    Replies: 14
    Last Post: 20th January 2006, 07:34 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •