    New Server Room

    Hi Everyone,

    Since I started here a couple of months ago I've been looking to move the server rack into a dedicated server room (out of the first aid room/disabled lift room!). After talking to my line manager and the caretaker we finally think we have a workable solution (partitioning part of the boiler room to give us a dedicated server room!), and now we're talking to SMT to get approval to go ahead.

    As part of this move we're looking to also sort out our currently very poor UPS setup and put in some new racks. I was wondering what rack manufacturers people recommend? Which ones do you find easy to work with and give you all the nice cable routing features you want

    Also what UPS setups do people have. We'd be starting from scratch, and it looks like there won't be enough cash to put in a single (well 2 to give redundancy ) UPS for the room so I'm looking at what other schools are currently doing.

    I'm also looking for suggestions on environmental monitoring. We're not putting in A/C to begin with since the boiler room is around 15C all year round, but I was told if temperature/humidity is a problem then we'll get it installed. So a decent system to monitor this and other things like water/smoke detection would be great

    Finally anyone got any suggestions or hints/tips for putting in a new server room? We're currently hoping to get the room ready by the summer to allow us to move everything over once the school breaks up, and at the same time allow us to lay new fibre to all the comms cabinets. If anyone has any suggestions for companies that do cable installs in the south east (sussex) then that would also be greatly appreciated

    John

  2. #2

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,684
    Thank Post
    516
    Thanked 2,453 Times in 1,899 Posts
    Blog Entries
    24
    Rep Power
    833
    Our UPS solution isn't ideal either, so I can't really advise on that. What I will say is that you should put A/C in from the outset. It may be 15 degrees now, but when you stick some servers in there, it'll soon heat up. Especially if it is a closed room. We have a dozen machines in our room, and without A/C it'd be hitting 40 degrees in there.

  3. #3

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    15,952
    Thank Post
    886
    Thanked 1,700 Times in 1,477 Posts
    Blog Entries
    12
    Rep Power
    448
    Will a holier room next door not be hot for servers

  4. #4

    Join Date
    Mar 2007
    Location
    Heywood, Lancs
    Posts
    211
    Thank Post
    7
    Thanked 50 Times in 45 Posts
    Rep Power
    28
    Would agree totally about the air-con.
    You will need it as soon as the servers are up and running, and it will be easier to fit it during other building work than retro-fitting it later.

    As for UPS, redundancy is the key. Better to have several smaller capacity than one to service the whole lot, expecially if you have redundant power supplies in the servers.

  5. #5

    Join Date
    Oct 2007
    Posts
    131
    Thank Post
    16
    Thanked 14 Times in 14 Posts
    Rep Power
    16
    The Aircon failed in our server room this summer with only 5 servers 5 switches and 2 ups running in there and as server rooms go its quite large. We came back in on monday (it had failed over weekend) and you could have cooked an egg on the plaster board wall, the other tech opened the door and burn his hand on the door handle and thats not next to a boiler room, other consideration is when boiler starts leaking and your server room is under water will the insurance pay out not the ideal place to have it.

  6. #6
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by Linfit View Post
    As for UPS, redundancy is the key. Better to have several smaller capacity than one to service the whole lot, expecially if you have redundant power supplies in the servers.
    can you explain why ? what do you know about the redundancy of units sufficiently sized and designed to provide backup power and power filtering for all servers ?

    have you not heard of a 2N configuration ?

    For the OP, the big four server vendors all make good equipment racks. My preference would be hp or ibm.

    apc also do a good range, but most rack vendors have a number of cable management options so nothing stands out in that regard. some racks are wider to accomodate cable routing channels, but i don't think those are necessary in most cases.

    i would say split rear doors are a nice feature, and a size below 42u and above 24u is a good size for getting under doors, getting to top equipment in the rack and having enough room to accomodate a small server estate. hp's 36u racks are possibly the most convenient height.

  7. #7
    wesleyw's Avatar
    Join Date
    Dec 2005
    Location
    Kingswinford
    Posts
    2,207
    Thank Post
    225
    Thanked 50 Times in 44 Posts
    Blog Entries
    1
    Rep Power
    30
    2N configuration?

    Wes

  8. #8
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by wesleyw View Post
    2N configuration?

    Wes
    sorry, i meant N+1 when using a single ups.

    2N is the configuration for having dual ups. It's not the case that you need dual UPS for a redundant configuration with servers that have dual power supplies. you could have dual power strips but they can both go into a suitably sized ups. infact many larger orgs use a single big ups with an automatic transfer switch upstream connected to mains power and generator for power source redundancy.

    there may be a cost implication for going with a larger single ups vs two or more smaller ups but there's enough redundancy.

  9. Thanks to torledo from:

    wesleyw (28th April 2009)

  10. #9

    Join Date
    Jan 2009
    Location
    England
    Posts
    1,524
    Thank Post
    300
    Thanked 304 Times in 263 Posts
    Rep Power
    83
    While I'd love to stick A/C in now it's something SMT want to hold off on until we know more about the temps in the room with the servers in there. The current location doesn't have A/C either and is currently sitting at around 30C (without any of the new servers being switched on!), which is one of the major considerations in moving the servers.

    Having never been near our boiler when it's on I've been assured that the room stays cold throughout winter and summer, and I've also been assured that the water pipes are on the opposite side of the (very) large boiler room. The floor is being raised due to a large concrete plinth that is too difficult to remove, so the servers will be at a much higher height than the boiler room so hopefully if the water pipes do burst we'll have some time to respond before the room floods totally!

    Which UPS manufacturers (other than APC) are people using? Or is it just worth sticking to the APC range of UPS equipment?

  11. #10
    somabc's Avatar
    Join Date
    Oct 2007
    Location
    London
    Posts
    2,337
    Thank Post
    83
    Thanked 388 Times in 258 Posts
    Rep Power
    111
    What is a 2N configuration?

    For non redundant UPS systems, a 2N configuration can be used to achieve high levels of availability. In a 2N configuration, the load is connected to two UPSs via an Automatic Transfer Switch (ATS). Each UPS is connected to two separate AC lines (each UPS receives power from a separate power source) and the ATS monitors the power quality from both the primary and redundant UPS and automatically switches the load to the redundant UPS when it detects a potential disruption to the load, such as a UPS failure or replacement.

  12. Thanks to somabc from:

    wesleyw (28th April 2009)

  13. #11

    Join Date
    Jun 2007
    Location
    London
    Posts
    894
    Thank Post
    64
    Thanked 171 Times in 140 Posts
    Rep Power
    55
    I've got to agree with Alex - why would you want to site your servers next to your boiler room? I presume the boiler room is on the ground floor so what is the drainage like around the room?

    In terms of H&S I'm not sure anyone called in to fix a leaking boiler would be particularly enthusiastic to know you've got a whole lot of electrical equipment in the room adjacent either

    Sounds like someone needs to do a risk assessment...

  14. #12

    Join Date
    Aug 2005
    Location
    London
    Posts
    3,156
    Thank Post
    116
    Thanked 529 Times in 452 Posts
    Blog Entries
    2
    Rep Power
    124
    With or without aircon, you need some kind of environmental monitor so that if the room gets too hot then systems get shut down cleanly. You can also get the electricians to install the aircon supply in such a way that if it fails, the power for the servers gets cut off. UPS will then take over but they will then shut down the servers before everything melts.

    There's a whole raft of monitoring stuff which you can get that just rack mounts and gives SNMP info but I found this at Dartmount college which gives a rather simple DIY system. the web site refers to US suppliers but I think homechip sell all the bits you need

  15. #13

    john's Avatar
    Join Date
    Sep 2005
    Location
    London
    Posts
    10,611
    Thank Post
    1,496
    Thanked 1,051 Times in 920 Posts
    Rep Power
    303
    I would look at the APC stuff (well the MGE stuff seen as MGE own APC) I'm still partial to the MGE onces which look very impressive.

  16. #14
    Batman's Avatar
    Join Date
    Mar 2009
    Location
    Northampton
    Posts
    940
    Thank Post
    115
    Thanked 118 Times in 74 Posts
    Rep Power
    40
    Quote Originally Posted by alextreadwell View Post
    The Aircon failed in our server room this summer with only 5 servers 5 switches and 2 ups running in there and as server rooms go its quite large. We came back in on monday (it had failed over weekend) and you could have cooked an egg on the plaster board wall, the other tech opened the door and burn his hand on the door handle and thats not next to a boiler room, other consideration is when boiler starts leaking and your server room is under water will the insurance pay out not the ideal place to have it.
    We have a lot more stuff than that... 20 servers, a big stack of switches... two ups units. Our air con got switched off. The lino on the floor melted, the feet of the racks are now sunk about a centimetre into the floor! We were extremely lucky, the metal covers came off the sprinklers so had the heat risen a few more degrees it could have been very messy.

    All the servers except one powered themselves off when they got too hot, and all except one came back on with no problems... yup... it had to be the SIMS server that went down. You can guarantee if something's gonna break it's gonna be SIMS!

  17. #15
    sdc
    sdc is offline
    sdc's Avatar
    Join Date
    Apr 2008
    Location
    Dorset, UK
    Posts
    312
    Thank Post
    53
    Thanked 42 Times in 37 Posts
    Rep Power
    41
    We have Riello UPS devices (two - one in each server rack). They're excellent - they include digital readouts on the front panels, giving a huge amount of information (more is available via the management software), and for our 17 servers, most of which are pretty powerful, we get two hours' runtime after power failure. I've set them up to power down when only 15 minutes remains in the UPS batteries. Servers with dual power supplies are fed from both UPSes.

    This is the model we've gone for: Dialog Dual

    We purchased from UPS Systems PLC, who were very competitive and most helpful.

    Hope that helps!

    PS - we also have APC SmartUPSes in critical comms cabinets.

SHARE:
+ Post New Thread
Page 1 of 3 123 LastLast

Similar Threads

  1. Humidity and server room
    By localzuk in forum Hardware
    Replies: 6
    Last Post: 20th April 2009, 01:20 PM
  2. Dream Server Room
    By SYNACK in forum Blue Skies
    Replies: 15
    Last Post: 16th April 2009, 03:47 PM
  3. Server room floor
    By Oops_my_bad in forum Wireless Networks
    Replies: 17
    Last Post: 12th December 2007, 10:09 AM
  4. working in the server room
    By Uraken in forum General Chat
    Replies: 27
    Last Post: 21st November 2007, 09:39 AM
  5. Server room temperature
    By netadmin in forum General Chat
    Replies: 30
    Last Post: 11th June 2007, 07:35 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •