Hardware Thread, New Server Room in Technical; Originally Posted by timzim In terms of H&S I'm not sure anyone called in to fix a leaking boiler would ...
  1. #16

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,986
    Thank Post
    64
    Thanked 379 Times in 289 Posts
    Rep Power
    160
    Quote Originally Posted by timzim View Post
    In terms of H&S I'm not sure anyone called in to fix a leaking boiler would be particularly enthusiastic to know you've got a whole lot of electrical equipment in the room adjacent either
    Oh for pity's sake! Do you not think that a boiler room will have plenty of power in it anyway? How do you think pumps run, or boilers are controlled?

    If SMT won't spring for A/C up front, insist on some decent air handling fans. In the UK it is seldom over 30C outside, so pulling fresh air in will help keep temps under control. These (two for redundancy) would need sensors to detect failure, but that is trivial to achieve.

  2. Thanks to Andrew_C from:

    torledo (29th April 2009)

  3. #17
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by Andrew_C View Post
    Oh for pity's sake! Do you not think that a boiler room will have plenty of power in it anyway? How do you think pumps run, or boilers are controlled?

    If SMT won't spring for A/C up front, insist on some decent air handling fans. In the UK it is seldom over 30C outside, so pulling fresh air in will help keep temps under control. These (two for redundancy) would need sensors to detect failure, but that is trivial to achieve.
    great post. stumbled across an article yesterday about using fresh air ahu's to save a bundle on A/C costs....but presumably the feasability of fresh air cooling would reach a limit depending on size of the room, total btu etc. ? is fresh air cooling a better than nothing approach.

  4. #18
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by sdc View Post
    We have Riello UPS devices (two - one in each server rack). They're excellent - they include digital readouts on the front panels, giving a huge amount of information (more is available via the management software), and for our 17 servers, most of which are pretty powerful, we get two hours' runtime after power failure. I've set them up to power down when only 15 minutes remains in the UPS batteries. Servers with dual power supplies are fed from both UPSes.

    This is the model we've gone for: Dialog Dual

    We purchased from UPS Systems PLC, who were very competitive and most helpful.

    Hope that helps!

    PS - we also have APC SmartUPSes in critical comms cabinets.
    how many battery expansion packs do you have to provide 2 hours of runtime for 17 servers ?

  5. #19

    Join Date
    Jun 2007
    Location
    London
    Posts
    894
    Thank Post
    64
    Thanked 171 Times in 140 Posts
    Rep Power
    55
    Quote Originally Posted by Andrew_C View Post
    Oh for pity's sake! Do you not think that a boiler room will have plenty of power in it anyway? How do you think pumps run, or boilers are controlled?
    Durrr, apart from the boiler's electrics being fairly waterproof (waterproof servers??) a boiler room has to have (by law) an electrical isolator switch. Even if you configured this to also turn off power to the server room there's a whole bunch of UPSs in there keeping the lot live.

  6. #20

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    Quote Originally Posted by timzim View Post
    Durrr, apart from the boiler's electrics being fairly waterproof (waterproof servers??)
    You said earlier 'in the room adjacent'. I'd say a wall was pretty waterproof myself.

    a boiler room has to have (by law) an electrical isolator switch. Even if you configured this to also turn off power to the server room there's a whole bunch of UPSs in there keeping the lot live.
    No, there's a bunch of UPSs keeping the device side of the system live. The boiler room side is dead as the dodo.
    Last edited by powdarrmonkey; 29th April 2009 at 12:29 PM.

  7. #21

    Join Date
    Jun 2007
    Location
    London
    Posts
    894
    Thank Post
    64
    Thanked 171 Times in 140 Posts
    Rep Power
    55
    Quote Originally Posted by powdarrmonkey View Post
    The boiler room side is dead as the dodo.
    Unless there's a foot of water on the floor (i.e the boiler's leaked). That's my point.

  8. #22

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    2,986
    Thank Post
    64
    Thanked 379 Times in 289 Posts
    Rep Power
    160
    Quote Originally Posted by timzim View Post
    Durrr, apart from the boiler's electrics being fairly waterproof
    Have you ever seen a boiler with IP anything rated wiring? I certainly haven't. All a bit academic as the OP says
    The floor is being raised due to a large concrete plinth that is too difficult to remove, so the servers will be at a much higher height than the boiler room so hopefully if the water pipes do burst we'll have some time to respond before the room floods totally!

  9. #23

    Join Date
    Dec 2008
    Posts
    2
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    We fitted our server room out with open racks which be purchased from cablenet. They were a good quality and could supply cable trays and rings as required. They also supplied a rack mounted tft screen with built in 16 port KVM

    We use a largish APC ups which has extra batteries added to give an extended run time with a nework interface and envirmental monitoring. It was oversized when we purchased it but additional servers have been fitted unexpectely this year and any further servers will need to go on a second.

    The server are connected to the UPS through a APC Switched PDU this means we can control the start up sequence as we have a server that appears to be reliant on another being up. It can also be used to perform a hard reset with out a visit to the server room.

    The room has AC which is massivly overrated but it did not add to much to the price to go for the larger one. It is attualy a heat pump so it could be used for heating (not that we want that) because of this there is a subsidy availiable for fitting one.

    We have a Lascar EL-USB-RT this logs temperature and humdidty and sends an email alert out if the room goes out of range and cost about £35.

    Finaly if all else has failed there is a temperature sensor that if the room gets really hot cuts the power. The ups will then start a safe shutdown of the room.

  10. #24
    Butuz's Avatar
    Join Date
    Feb 2007
    Location
    Wales, UK
    Posts
    1,579
    Thank Post
    211
    Thanked 220 Times in 176 Posts
    Rep Power
    63
    Lol they fresh-aired my server room when I originally managed to get it built. It took 5 years to get it built so I didnt kick up a hissy fit over air con. It sook 5 mins to melt the entire world though....

    Biggest make ever. 4 Portable air con units later I am still pushing for reliable, powerful, permanant air con.... *sigh*

    Go for £2k worth of air con now IMHO.

    Butuz

  11. #25
    Marci's Avatar
    Join Date
    Jun 2008
    Location
    Wakefield, West Yorkshire
    Posts
    895
    Thank Post
    84
    Thanked 235 Times in 194 Posts
    Rep Power
    82
    Spring for aircon now rather than later... ambient aircooling is insufficient... fresh air cooling adds further risks over winter, especially if you shut servers down over Christmas hols etc, unless you can completely close the vents to outdoors...

    If SMT are against this, there is plenty of research out there online to back up the need. Find a way to hint to them that they're being blatantly ignorant by skimping on it, without being as blunt as I tend to be when I deal with them

    Enviro monitoring on the cheap: http://www.t-balancer.com/english/bng.htm
    Analog sensors can be positioned to monitor and record to CSV files ambient temps, internal case temps etc etc. Can also be used to trigger 12v devices on / off (eg: additional case fans, or solenoids to additional 240v rack fans) - can report all back to MBM5 or similar free mobo monitoring software, and can be used to trigger shutdowns based on temps of any sensor attached to it that you specify.
    Last edited by Marci; 29th April 2009 at 07:00 PM.

  12. #26
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by Marci View Post
    Spring for aircon now rather than later... ambient aircooling is insufficient... fresh air cooling adds further risks over winter, especially if you shut servers down over Christmas hols etc, unless you can completely close the vents to outdoors...

    If SMT are against this, there is plenty of research out there online to back up the need. Find a way to hint to them that they're being blatantly ignorant by skimping on it, without being as blunt as I tend to be when I deal with them

    Enviro monitoring on the cheap: mCubed Information Technology GmbH
    Analog sensors can be positioned to monitor and record to CSV files ambient temps, internal case temps etc etc. Can also be used to trigger 12v devices on / off (eg: additional case fans, or solenoids to additional 240v rack fans) - can report all back to MBM5 or similar free mobo monitoring software, and can be used to trigger shutdowns based on temps of any sensor attached to it that you specify.
    what do you mean by ambient aircooling ? by that do you mean opening a door or a window ?

    am curious as to the risks of fresh air cooling, how cold does a room get with fresh air vents where it effects the health of machines which are in an off state. the fresh air system we have has pretty basic controls to regulate flow at the supply and return vent ends....presumably you can get systems with more advanced controls ?

  13. #27

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,225
    Thank Post
    874
    Thanked 2,717 Times in 2,302 Posts
    Blog Entries
    11
    Rep Power
    780
    Quote Originally Posted by torledo View Post
    what do you mean by ambient aircooling ? by that do you mean opening a door or a window ?

    am curious as to the risks of fresh air cooling, how cold does a room get with fresh air vents where it effects the health of machines which are in an off state. the fresh air system we have has pretty basic controls to regulate flow at the supply and return vent ends....presumably you can get systems with more advanced controls ?
    Ambient aircooling just means using air of an uncontroled temperature from the surrounding environment so yes an open door or a fan duct system.

    Humidity and contaminants (bugs, dirt, stray bears depending on vent size , etc) are the big concerns, when the gear is left off moisture can easily build up inside the machines which causes huge messes when the power is pushed back through. Experiments have been carried out by the big box manufacturers and MS notibly with MS's server rack in a tent experiment but this puts extra strain on the equipment and is still not recommended practice. Additionally the extra contaminants can increase the rate of oxidisation of the metals inside the server which can lead to other issues.

  14. #28
    Butuz's Avatar
    Join Date
    Feb 2007
    Location
    Wales, UK
    Posts
    1,579
    Thank Post
    211
    Thanked 220 Times in 176 Posts
    Rep Power
    63
    If I turn my air con off the server room goes from 20 to 30 degrees in 20 mins

    Butuz

  15. #29
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    48
    Quote Originally Posted by SYNACK View Post
    Ambient aircooling just means using air of an uncontroled temperature from the surrounding environment so yes an open door or a fan duct system.

    Humidity and contaminants (bugs, dirt, stray bears depending on vent size , etc) are the big concerns, when the gear is left off moisture can easily build up inside the machines which causes huge messes when the power is pushed back through. Experiments have been carried out by the big box manufacturers and MS notibly with MS's server rack in a tent experiment but this puts extra strain on the equipment and is still not recommended practice. Additionally the extra contaminants can increase the rate of oxidisation of the metals inside the server which can lead to other issues.
    with the contamainents issue, would server floor carpets be one of the biggest culprits for machines which are left off ? what's the best way to deal with the dust issue clogging components ?

  16. #30

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,225
    Thank Post
    874
    Thanked 2,717 Times in 2,302 Posts
    Blog Entries
    11
    Rep Power
    780
    Quote Originally Posted by torledo View Post
    with the contamainents issue, would server floor carpets be one of the biggest culprits for machines which are left off ? what's the best way to deal with the dust issue clogging components ?
    Dust is easy, just open it up and hit it with compressed air every so often. Compressed air in a can is the safest as an air compressor will codence a lot of water vapor into the air stream. You need at least one moisture trap in the line to minimize this, check out my blog posting on here for more details.

    Oh and carpets are a bad idea, they host dust moisture and static quite effectivly, linolium is the answer or tile or painted concrete, these are also less or a fire hazard.

    The more pressing concern is the moisture, as the servers and components contain semi enclosed pockets of air that are insulated a bit and so heat and cool at a differing rate condensation can form inside the systems. This in turn can rain down on components along with contaminants and can even form inside hard drives and under cpus. This is made more dangerous if you are in an enviroment which can have sub zero temperatures as when water freezes it expands and if lodged under or in components can do damage.

    Living things also like the slightly warmer indoor environment and so you need to be careful that your equipment does not become an impromptu nest for a wayward colony of insects or worse.
    Last edited by SYNACK; 29th April 2009 at 10:00 PM.

SHARE:
+ Post New Thread
Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Humidity and server room
    By localzuk in forum Hardware
    Replies: 6
    Last Post: 20th April 2009, 01:20 PM
  2. Dream Server Room
    By SYNACK in forum Blue Skies
    Replies: 15
    Last Post: 16th April 2009, 03:47 PM
  3. Server room floor
    By Oops_my_bad in forum Wireless Networks
    Replies: 17
    Last Post: 12th December 2007, 10:09 AM
  4. working in the server room
    By Uraken in forum General Chat
    Replies: 27
    Last Post: 21st November 2007, 09:39 AM
  5. Server room temperature
    By netadmin in forum General Chat
    Replies: 30
    Last Post: 11th June 2007, 07:35 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •