    Change UPS Battery

    Hi

    We have an APC 3000 UPS. The battery is dead. I am just about the change it but do i need to unplug the UPS from the mains or can i keep everything running while i change it?

    Thanks

  2. #2
    sdc
    sdc is offline
    sdc's Avatar
    Join Date
    Apr 2008
    Location
    Dorset, UK
    Posts
    312
    Thank Post
    53
    Thanked 42 Times in 37 Posts
    Rep Power
    42
    I'm fairly sure you can leave the supply and the load connected whilst changing the battery - they're hot-swap. We have done a number of APC devices this way without any issue. Just hope you don't get a power cut in the middle of the proces....!!

  3. #3
    BatchFile's Avatar
    Join Date
    Aug 2007
    Location
    Cumbria
    Posts
    948
    Thank Post
    544
    Thanked 128 Times in 106 Posts
    Rep Power
    60
    ...and put on your wellies and rubber gloves just to be on the safe side

    I did one a couple of years ago - I THINK it hot swapped ok

  4. #4
    Butuz's Avatar
    Join Date
    Feb 2007
    Location
    Wales, UK
    Posts
    1,579
    Thank Post
    211
    Thanked 220 Times in 176 Posts
    Rep Power
    63
    I shut mine down during swap coz I'm a scaredy cat

    Butuz

  5. #5

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    16,028
    Thank Post
    887
    Thanked 1,723 Times in 1,488 Posts
    Blog Entries
    12
    Rep Power
    453
    just done it on a live cab. All went fine, a little tricker than expected becuase the batteries swelled.

  6. #6

    Little-Miss's Avatar
    Join Date
    Oct 2007
    Location
    London
    Posts
    5,559
    Thank Post
    2,377
    Thanked 753 Times in 461 Posts
    Blog Entries
    2
    Rep Power
    544
    Me a scaredy cat too. Uplugged mine, but im lucky enough to have one running next to it that could take an extra server without being overloaded.

    Remember i asked about swapping them and someone mentioned they swell? They werent joking!! Had to get a MAN to do it in the end!!! Pah!!!

  7. #7
    sdc
    sdc is offline
    sdc's Avatar
    Join Date
    Apr 2008
    Location
    Dorset, UK
    Posts
    312
    Thank Post
    53
    Thanked 42 Times in 37 Posts
    Rep Power
    42
    Nice... glad it worked OK for you though. What do you do with your dead batteries?

  8. #8

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    16,028
    Thank Post
    887
    Thanked 1,723 Times in 1,488 Posts
    Blog Entries
    12
    Rep Power
    453
    Quote Originally Posted by sdc View Post
    Nice... glad it worked OK for you though. What do you do with your dead batteries?
    erm they are in a store cupboard we are leaving it for BSF to deal with

  9. #9

    powdarrmonkey's Avatar
    Join Date
    Feb 2008
    Location
    Alcester, Warwickshire
    Posts
    4,859
    Thank Post
    412
    Thanked 777 Times in 650 Posts
    Rep Power
    182
    Quote Originally Posted by FN-GM View Post
    erm they are in a store cupboard we are leaving it for BSF to deal with
    ha, awesome idea!

  10. #10
    DMcCoy's Avatar
    Join Date
    Oct 2005
    Location
    Isle of Wight
    Posts
    3,461
    Thank Post
    10
    Thanked 496 Times in 436 Posts
    Rep Power
    113
    Quote Originally Posted by FN-GM View Post
    just done it on a live cab. All went fine, a little tricker than expected becuase the batteries swelled.
    How hot are they getting? I've never seen this happen over many years with ups batteries, even in quite warm rooms.

  11. #11


    Join Date
    Sep 2007
    Location
    UK
    Posts
    5,449
    Thank Post
    1,447
    Thanked 889 Times in 570 Posts
    Rep Power
    647
    Quote Originally Posted by FN-GM View Post
    erm they are in a store cupboard we are leaving it for BSF to deal with
    Would you like some projector bulbs to keep them company?

  12. #12

    Domino's Avatar
    Join Date
    Oct 2006
    Location
    Bromley
    Posts
    4,159
    Thank Post
    215
    Thanked 1,261 Times in 792 Posts
    Blog Entries
    4
    Rep Power
    507
    Quote Originally Posted by DMcCoy View Post
    How hot are they getting? I've never seen this happen over many years with ups batteries, even in quite warm rooms.
    Just has ours replaced in our incredibly meaty ups after a aircon failure caused them to swell.

    Mind you, it was blummin hot...

  13. #13

    Little-Miss's Avatar
    Join Date
    Oct 2007
    Location
    London
    Posts
    5,559
    Thank Post
    2,377
    Thanked 753 Times in 461 Posts
    Blog Entries
    2
    Rep Power
    544
    I think heat was to blame for our batteries swelling. Before i arrived at the school the servers etc were moved into a cupboard with poor ventilation and cooling. So i wouldnt be suprised if that was the reason!

  14. #14

    Join Date
    May 2006
    Location
    West Bromwich
    Posts
    2,191
    Thank Post
    299
    Thanked 215 Times in 185 Posts
    Rep Power
    56
    Quote Originally Posted by laserblazer View Post
    Would you like some projector bulbs to keep them company?
    If you have an issue with trying to get rid of used projector lamps can i suggest Simply Lamps?

    Even if you don't purchase from them they will collect your used bulbs free of charge. I haven't used them yet but plan on doing so very soon. I called and sorted out what i need to do but not got round to it yet

  15. #15

    FN-GM's Avatar
    Join Date
    Jun 2007
    Location
    UK
    Posts
    16,028
    Thank Post
    887
    Thanked 1,723 Times in 1,488 Posts
    Blog Entries
    12
    Rep Power
    453
    Hi,

    I changed the battery at the time of the first post. This morning the UPS is showing a red light still. How do i get rid of it please?

    thanks

    EDIT: fixed it just held in the test button
    Last edited by FN-GM; 28th April 2009 at 08:23 AM.

SHARE:
+ Post New Thread
Page 1 of 2 12 LastLast

Similar Threads

  1. UPS Battery ....
    By Little-Miss in forum Learning Network Manager
    Replies: 21
    Last Post: 5th November 2009, 10:57 AM
  2. How long does your battery last?
    By eean in forum General Chat
    Replies: 2
    Last Post: 24th March 2009, 09:09 AM
  3. UPS Battery pack: Homebrew replacement?
    By rhyds in forum Hardware
    Replies: 11
    Last Post: 27th August 2008, 11:59 PM
  4. How long should a battery last?
    By button_ripple in forum Hardware
    Replies: 4
    Last Post: 20th April 2008, 11:21 AM
  5. Battery Life
    By Mano in forum Hardware
    Replies: 3
    Last Post: 18th November 2005, 09:06 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •