    Humidity and server room

    I have just had a look at our air conditioning and the environment monitoring in our server room and I have noticed a few things.

    Firstly is that the humidity of the room has dropped by 15% from 40% to 25% relative humidity within about 2 weeks. This seems to be since I have turned on one more server. Or is it due to the room having been completely closed for most of that time (ie. people usually go through the room to get to a store room during term times).

    The other thing is that using the formula that was posted on the site earlier today, it appears that my servers can produce roughly 40,000 BTU of heat, in a room which is 2.5m x 1.5m in size. The aircon unit is a 3kW wall mounted unit, and has broken down multiple times. So, that formula indicates it is way under spec.

    Comments, suggestions?

  2. #2
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    47
    quick back of the envelope stuff indicates that your 3kw ac unit is seriously underpowered for 40k btu.

    1 ton of cooling capacity [which i think roughly translates to the capacity of your wall mounted unit] will handle 12k BTU.

    The thing to remember is that your equipment isn't drawing the maximum watts during normal operation.
    But, even with equipment drawing a proportion of the rated power that would still leave your AC unit underpowered for the area it needs to cool. It could well be that adding that extra server was the straw.

    How many servers are we talking about here ? Have you virtualised down as low as you can go, and do you have scope to procure a larger AC unit. Or is it just a case of needing to justify a bigger room and improved ventilation.

  3. #3

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,631
    Thank Post
    514
    Thanked 2,442 Times in 1,890 Posts
    Blog Entries
    24
    Rep Power
    831
    We have 9 servers with 700W power supplies, a core switch with a 1200W power supply, and a few other bits and pieces which come to about 2kW total draw. So a total draw is just under 10kW.

    Virtualisation... I have made a start, but it is limited in that my request for a) additional hard drives or b) a SAN for the images to go onto were denied.

    I'm really just looking for comments, so I can go to my manager and say 'the unit supplied via our LEA is not fit for purpose, so it needs either upgrading, or our usage of servers re-looking at and reducing via a virtualisation project, as mentioned by me earlier in the year'.

    I may be able to get rid of around 1400W of power usage in there, but it'll be difficult.
    Last edited by localzuk; 20th April 2009 at 12:24 PM.

  4. #4
    torledo's Avatar
    Join Date
    Oct 2007
    Posts
    2,928
    Thank Post
    168
    Thanked 155 Times in 126 Posts
    Rep Power
    47
    Quote Originally Posted by localzuk View Post
    We have 9 servers with 700W power supplies, a core switch with a 1200W power supply, and a few other bits and pieces which come to about 2kW total draw. So a total draw is just under 10kW.

    Virtualisation... I have made a start, but it is limited in that my request for a) additional hard drives or b) a SAN for the images to go onto were denied.

    I'm really just looking for comments, so I can go to my manager and say 'the unit supplied via our LEA is not fit for purpose, so it needs either upgrading, or our usage of servers re-looking at and reducing via a virtualisation project, as mentioned by me earlier in the year'.

    I may be able to get rid of around 1400W of power usage in there, but it'll be difficult.
    well, the unit supplied doesn't appear to be fit for purpose based on current server count...and more importantly future expansion.

    ofcourse now is a good time to talk to management about new servers to replace old. Because it's not efficient to have 9 700w power supplies when a single multicore server could consolidate that right down. the new ibm x3850 m2 for instance, up to 8-cores, up to 8 sff disks, and one or two 835w power supplies. A couple of those could possibly replace your entire server estate.

    you've also got to factor in the heat generated by your ups if you haven't already done so. could be another factor in looking at server usage.

  5. #5

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,631
    Thank Post
    514
    Thanked 2,442 Times in 1,890 Posts
    Blog Entries
    24
    Rep Power
    831
    Ah, 3 of the servers are terminal servers. (dual quad core xeons with 16GB of ram each, for future expansion to 64bit).

    1 of the servers is a iSCSI san box. 1 of the servers is our backup server (ie 2TB storage).

    The rest are pretty much virtualisable. I'm looking at virtualising our main AD server at some point this term - which will mean 1 less server. But it comes down to a complete lack of budget as the main problem here.

  6. #6

    GrumbleDook's Avatar
    Join Date
    Jul 2005
    Location
    Gosport, Hampshire
    Posts
    9,930
    Thank Post
    1,337
    Thanked 1,781 Times in 1,105 Posts
    Blog Entries
    19
    Rep Power
    594
    It's not just your UPS you have to remember about, but also your switches and lighting too.

  7. #7

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,631
    Thank Post
    514
    Thanked 2,442 Times in 1,890 Posts
    Blog Entries
    24
    Rep Power
    831
    Quote Originally Posted by GrumbleDook View Post
    It's not just your UPS you have to remember about, but also your switches and lighting too.
    That's included in the 'other power usage' block i gave earlier.

SHARE:
+ Post New Thread

Similar Threads

  1. Dream Server Room
    By SYNACK in forum Blue Skies
    Replies: 15
    Last Post: 16th April 2009, 03:47 PM
  2. [Video] Pimp your server room
    By Oops_my_bad in forum Jokes/Interweb Things
    Replies: 2
    Last Post: 20th January 2009, 10:23 PM
  3. Server room outlook
    By KWestos in forum General Chat
    Replies: 43
    Last Post: 22nd May 2008, 08:09 PM
  4. Server room floor
    By Oops_my_bad in forum Wireless Networks
    Replies: 17
    Last Post: 12th December 2007, 10:09 AM
  5. Server room temperature
    By netadmin in forum General Chat
    Replies: 30
    Last Post: 11th June 2007, 07:35 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •