    Question Patch Panel Room * Advice*

    At work we have a room with a Comms cab half full with switches. Also in the room we have a UPS to power a whole office block.

    My concern is that during summer and warmer days the room does seem to get extremely hot! so hot you cannot be stood in it with a tie on !


    The room was also used for storage, i have emptied the room so all that stands inside now is the equipment (To reduce Temp), were looking at upgrading our Norstar phone system to VOIP too, This will be located in the same room. Main concern is the temperature of the room, what would be the possible options of keeping it at a cool temperature and is there any chance of the equipment getting damaged from heat ?

    Our Server room is located in a different room, this has a air con fitted running 24/7 and stays really cool.
    Also is there any preventative maintanance i should carry out on comms cabs ? UPS ?


    Many thanks

  2. #2

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224
    It depends what temperature it is. Anything over 30C is problematic and anything over 40C is dangerous. If the room is getting in this temperature range ('borrow' the thermal sensor kit science departments always have, or a simple greenhouse thermometer with min/max on it) then you will need to fit air con or reduce the amount of equipment you have in that room.

  3. #3
    chazzy2501's Avatar
    Join Date
    Jan 2008
    Location
    South West
    Posts
    1,781
    Thank Post
    213
    Thanked 263 Times in 213 Posts
    Rep Power
    67
    I have a few tight storage areas, fitting simple vents in the room (into another room in one case) brought the temperature down to acceptable levels. But yes as @Geoff says get a high low temperature monitor.

  4. #4

    Join Date
    Jan 2013
    Location
    Derbyshire
    Posts
    4
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Brilliant stuff, the room did have a thermometer fitted showing -15oC Haha, ive replaced this and going to leave it over night, ill post back soon with my results

  5. #5

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224
    Quote Originally Posted by chazzy2501 View Post
    I have a few tight storage areas, fitting simple vents in the room (into another room in one case) brought the temperature down to acceptable levels.
    Just be aware ventilation on it's own may not enough. Ventilation will do very little for you if the outside ambient temperature is high enough (granted we've not had a hot summer for a while now). More of a concern for me is that you don't have any control over the humidity (venting directly to the outside might make the humidity higher in some cases too). Condensation tends to love to collect on all those metal surfaces that make up your racks and equipment casings. So my advice if you can then do go for full climate control air conditioning.

  6. #6

    Join Date
    Jan 2013
    Location
    Derbyshire
    Posts
    4
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Yes, i carnt agree more, personally this room is the heart of the network, it already has vents to outside but like you say, i am also concerned to with condensation,
    in the next couple of months the room will be hosting a VoIP telephone system for approximately 170 users. ill see what temps come back as and see if i can get air con fitted.

  7. #7


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,630
    Thank Post
    275
    Thanked 777 Times in 604 Posts
    Rep Power
    223
    We found intumescent* door grills (one high in the door, one near the bottom) shaved 5-10 degrees (depends on time of year) off a cupboard that was getting a bit warm.


    *if there's a fire they're self-sealing.

  8. #8
    AJWhite1970's Avatar
    Join Date
    Sep 2012
    Location
    Wiltshire
    Posts
    326
    Thank Post
    83
    Thanked 75 Times in 57 Posts
    Rep Power
    16
    Another vote for two door grills bringing down the temp in small cupboards holding switches. Also the addition of a small simple desktop fan running in the cupboard keeps the air circulating and stops the formation of stale air pockets round the back of the cabinets which also helps with reducing temperature.

    Nothing beats proper air con though if it's mission critical.

  9. #9

    Geoff's Avatar
    Join Date
    Jun 2005
    Location
    Fylde, Lancs, UK.
    Posts
    11,803
    Thank Post
    110
    Thanked 583 Times in 504 Posts
    Blog Entries
    1
    Rep Power
    224
    Do you get any noise complaints from using that setup anywhere (library, offices, etc?)

  10. #10

    Join Date
    Jan 2013
    Location
    Derbyshire
    Posts
    4
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    actually its next to one of our directors offices,when in his office there is a humming noise form the UPS Under load etc. You can also here the UPS Fans as you walk past aswell. Noise is ok at the moment.

SHARE:
+ Post New Thread

Similar Threads

  1. Fibre Patch Panel Visio Stencil
    By TriggerHappyUK in forum Wireless Networks
    Replies: 11
    Last Post: 4th July 2013, 06:59 PM
  2. [For Sale] Free Belkin Cat 5e Patch Panels
    By gshaw in forum Classified Adverts
    Replies: 3
    Last Post: 1st March 2009, 07:44 PM
  3. Network patch panels
    By KWestos in forum Wireless Networks
    Replies: 5
    Last Post: 27th November 2008, 02:26 PM
  4. Patch Panel Sockets
    By rhyds in forum Wireless Networks
    Replies: 8
    Last Post: 22nd January 2008, 04:32 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •