    Server room aircon - how not to wire it!

    Was showing a contractor where some cabling needed to be finished in our new server room earlier - its got the 'old' and the 22k worth of 'new' servers in there.

    Open the door to be blasted by the heat. Air con has no life, its only 3 months old. Phone up electrician who sorted it out - he comes out - and after much head scratching realised he had cabled it into the emergency stop button in the dt room next door.

    Which the dt teacher does randomly through the day and every night and weekend.

    Great start to the day!

  2. #2

    twin--turbo's Avatar
    Join Date
    Jun 2012
    Location
    Carlisle
    Posts
    2,334
    Thank Post
    1
    Thanked 381 Times in 340 Posts
    Rep Power
    150
    Good effort!

  3. #3
    gibbo_ap's Avatar
    Join Date
    Nov 2007
    Location
    Staffs, UK
    Posts
    937
    Thank Post
    233
    Thanked 81 Times in 64 Posts
    Rep Power
    36
    i actually lol'ed......well almost

  4. #4


    Join Date
    Dec 2005
    Location
    In the server room, with the lead pipe.
    Posts
    4,618
    Thank Post
    275
    Thanked 777 Times in 604 Posts
    Rep Power
    223
    Now place the order for climate monitoring kit that'll notify you.

    And bill the A/C installer for the electrician's work.

  5. #5
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,401
    Thank Post
    648
    Thanked 277 Times in 244 Posts
    Rep Power
    78
    Pah .. you people and your server rooms .. if only I had a server room to complain about instead of a desk in the ICT suit with the servers sat on and the UPS underneath .. lol ..

    I feel your pain though .. not the brightest sparky there .. I mean, where did he think he was wiring it into? Surely to have wired it into something you didn't know shows a lack of competence ..

  6. #6

    X-13's Avatar
    Join Date
    Jan 2011
    Location
    /dev/null
    Posts
    8,854
    Thank Post
    588
    Thanked 1,902 Times in 1,315 Posts
    Blog Entries
    19
    Rep Power
    805
    Quote Originally Posted by soveryapt View Post
    Surely to have wired it into something you didn't know shows a lack of competence ..
    Murphy's law.

  7. #7
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,401
    Thank Post
    648
    Thanked 277 Times in 244 Posts
    Rep Power
    78
    Quote Originally Posted by X-13 View Post
    lol

    (and lol again to meet the minimum 6 characters .. teehee)

  8. #8

    twin--turbo's Avatar
    Join Date
    Jun 2012
    Location
    Carlisle
    Posts
    2,334
    Thank Post
    1
    Thanked 381 Times in 340 Posts
    Rep Power
    150
    We had our self installed split system replaced with a York system in our old building, the reasonning was two fold.

    1) the old self install system was just not up to the task of cooling the server room.
    2) the pipework for the self fit units had 7M max length and we could only get teh condenser unit as far as a disuesd store room. Said store room was cool most of the year, but in summer he heat would build up. The room was directly below the Heads office, he said his floor was red hot and the room unberable .... So we got the PRO's in.


    The york system ocaisonal went off of it's own accord, after 3 different A/C specialists checked it over the last one did some research and found that the unit as being disrupted by the Wi-Fi aparently. Eventualy that got replaced as it was a hazzard to the health of the equipment.

    Rob

  9. #9

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,786
    Thank Post
    272
    Thanked 1,129 Times in 1,025 Posts
    Rep Power
    348
    Get yourself one of these bad boys - top job and really good/easy to setup!.

    AVTECH - TemPageR 3ER Monitors Real-Time Temperature with Logging, Graphing, Alerting & Automatic Corrective Action!

  10. #10

    Join Date
    Apr 2012
    Posts
    413
    Thank Post
    39
    Thanked 35 Times in 28 Posts
    Rep Power
    15
    Quote Originally Posted by soveryapt View Post
    Pah .. you people and your server rooms .. if only I had a server room to complain about instead of a desk in the ICT suit with the servers sat on and the UPS underneath .. lol ..

    I feel your pain though .. not the brightest sparky there .. I mean, where did he think he was wiring it into? Surely to have wired it into something you didn't know shows a lack of competence ..
    Oh I had that before I started, a cupboard with some benching with servers on and a chair. I have got them to build me new office, repair area and a server room. Only been here 3 months.

  11. #11
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,401
    Thank Post
    648
    Thanked 277 Times in 244 Posts
    Rep Power
    78
    Quote Originally Posted by mattianuk View Post
    Oh I had that before I started, a cupboard with some benching with servers on and a chair. I have got them to build me new office, repair area and a server room. Only been here 3 months.
    First question: What drug did you use to persuade them to do all that?
    Second question: Where do I get hold of it or do you have any spare?



    I was once given a small (and I mean small) office for repairs and stuff, only to have it taken off me later with the promise that the store cupboard was going to have air con put in so it could house the servers too, only to have that then changed last minute as they decided it was too expensive .. but they then redeveloped the "office" I did have and gave it to a new deputy head .. FUN! :/
    Last edited by soveryapt; 19th July 2012 at 02:46 PM.

  12. #12

    Join Date
    Apr 2012
    Posts
    413
    Thank Post
    39
    Thanked 35 Times in 28 Posts
    Rep Power
    15
    Quote Originally Posted by soveryapt View Post
    First question: What drug did you use to persuade them to do all that?
    Second question: Where do I get hold of it or do you have any spare?



    I was once given a small (and I mean small) office for repairs and stuff, only to have it taken off me later with the promise that the store cupboard was going to have air con put in so it could house the servers too, only to have that then changed last minute as they decided it was too expensive .. but they then redeveloped the "office" I did have and gave it to a new deputy head .. FUN! :/
    I have been very lucky, even got to keep the old cupboard as secure storage.

    But then I have been given 150k to spend this year, and we are 600 pupil school with 300 machines - so LOTS of new toys

  13. #13
    soveryapt's Avatar
    Join Date
    Jan 2009
    Location
    Lancashire
    Posts
    2,401
    Thank Post
    648
    Thanked 277 Times in 244 Posts
    Rep Power
    78
    Quote Originally Posted by mattianuk View Post
    I have been very lucky, even got to keep the old cupboard as secure storage.

    But then I have been given 150k to spend this year, and we are 600 pupil school with 300 machines - so LOTS of new toys
    Blimey .. you have been lucky .. mind you, I can't complain, in my first few years here I was able to resuite the entire school with decent machines and I've been able to get 2 new servers and a Mac Mini Server as well so, I can't complain too much! lol ..

  14. #14

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,786
    Thank Post
    272
    Thanked 1,129 Times in 1,025 Posts
    Rep Power
    348
    Quote Originally Posted by mattianuk View Post
    But then I have been given 150k to spend this year, and we are 600 pupil school with 300 machines - so LOTS of new toys
    That isn't bad - i had that normally for a school 3 times the size (1600 kids - 200 staff - 950 machines). But last financial year we had an extra 100k from a building project and 40k at the end of the yearfrom *oh S*T we need to spend this money* budget.

    All in all i had lots of new kit!

SHARE:
+ Post New Thread

Similar Threads

  1. [Website] How NOT to design a website...
    By Gatt in forum Jokes/Interweb Things
    Replies: 67
    Last Post: 26th April 2012, 10:03 AM
  2. [Video] How not to pull a car out of the snow.
    By mattx in forum Jokes/Interweb Things
    Replies: 6
    Last Post: 10th February 2009, 06:59 PM
  3. big sing how not to do a world record attempt.
    By russdev in forum General Chat
    Replies: 0
    Last Post: 27th November 2008, 10:30 AM
  4. [Video] How not to take a tree down
    By phreak in forum Jokes/Interweb Things
    Replies: 7
    Last Post: 17th March 2008, 11:59 AM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •