    Over the break we had a power cut which in turn left the server room air-con switched off, the first I knew was when I popped in 4 days later to do something and nearly passed out in the 50+ degree heat in the server room.

    I want to create an early warning system but know nothing about electronics ( I am adept at following instructions though)

    Is anyone able to help me out by designing a plan to build from parts a temp sensor with a theshold level with alarm and flashing light that I can get from say maplins?

    I know it's a big ask, but would appreciate any help.

  2. #2

    Join Date
    Nov 2010
    Posts
    471
    Thank Post
    64
    Thanked 72 Times in 59 Posts
    Rep Power
    35
    Starter for 10 - arduino ( / freeduino) plus a DS18B20 one wire calibrated temp sensor, driving a mains relay (via a transistor) which drives a flasher / siren / whatever.

  3. #3
    mdench's Avatar
    Join Date
    Oct 2011
    Location
    Billingshurst
    Posts
    812
    Thank Post
    40
    Thanked 104 Times in 94 Posts
    Rep Power
    39
    Not something to build buy maybe a possible future investment? AVTECH - Room Alert 4ER Monitors Real-Time Temperature, Humidity, Power, Flood, Smoke, Room Entry, Air Flow, Heat Index, Motion, Sound, Light, IP Network Cameras, Panic Buttons & More with Logging, Graphing, Alerting, Signal Lights (optional) & Autom

    can set threshold and warning levels, with a web UI and can set it up to email you when the various limits are reached.

  4. #4

    Domino's Avatar
    Join Date
    Oct 2006
    Location
    Bromley
    Posts
    4,109
    Thank Post
    217
    Thanked 1,343 Times in 821 Posts
    Blog Entries
    4
    Rep Power
    526
    this: Temperature sensor tutorial - Using the TMP36 / LM35 outputs the temp readings to the serial console, but it should be a simple bit of coding to add a trigger for an attached light, etc

    any good?

  5. #5
    Chris_'s Avatar
    Join Date
    Jul 2010
    Location
    UK
    Posts
    715
    Thank Post
    140
    Thanked 122 Times in 102 Posts
    Rep Power
    45
    Or if you want an off the shelf system you could look at things like the APC NetBotz environmental monitoring system.

    NetBotz 200 - Product Information

  6. #6

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    11,268
    Thank Post
    884
    Thanked 2,747 Times in 2,321 Posts
    Blog Entries
    11
    Rep Power
    785
    How good are your servers, depending on their managment ability many can be told to send an email when internal temperature reaches a certain level. Not as accurate as an external thermometer but will still give you some warnings.

  7. #7

    plexer's Avatar
    Join Date
    Dec 2005
    Location
    Norfolk
    Posts
    13,613
    Thank Post
    746
    Thanked 1,706 Times in 1,519 Posts
    Rep Power
    437
    HomeChip

    One of those can be configured to latch it's relay and thus activate a strobe/alarm etc... at a certain temp.

    Ben

  8. #8

    Andrew_C's Avatar
    Join Date
    Sep 2005
    Location
    Winchester
    Posts
    3,087
    Thank Post
    64
    Thanked 404 Times in 307 Posts
    Rep Power
    165
    Much simpler would be a standard room stat, a battery, and a bell/buzzer. All you need to do is check that the stat doesn't have a heater in it (some do). However, the more complex solutions are better in that they could warn you when you were away from the site.

  9. #9
    Disease's Avatar
    Join Date
    Jan 2006
    Posts
    1,108
    Thank Post
    120
    Thanked 70 Times in 48 Posts
    Rep Power
    57
    Thanks all a lot to look at, I was hoping to get some sort of battery powered unit, as when the power is off none of the network monitoring units will work. I want a visual, audible alarm that would indicate to caretakers walking past that there is a problem and to contact IT.

    Thanks for all the suggestions, I did find this as well, IRPS1363 GSM Remote Power Socket - control mains devices by text messages - www.audon.co.uk
    or this http://www.audon.co.uk/home_sms/gd04.html
    Last edited by Disease; 11th June 2012 at 11:55 AM.

  10. #10

    Join Date
    Nov 2010
    Posts
    471
    Thank Post
    64
    Thanked 72 Times in 59 Posts
    Rep Power
    35
    Quote Originally Posted by Andrew_C View Post
    Much simpler would be a standard room stat, a battery, and a bell/buzzer. All you need to do is check that the stat doesn't have a heater in it (some do). However, the more complex solutions are better in that they could warn you when you were away from the site.
    Really simple. Like it. Mains charger (eg motorbike charger) to 12v leisure battery to 12v siren / beacon. 12v stats must be available. No mains isolation issues.

  11. #11

    Join Date
    Feb 2008
    Location
    Wiltshire
    Posts
    898
    Thank Post
    282
    Thanked 141 Times in 114 Posts
    Blog Entries
    28
    Rep Power
    42
    We got one of these;

    CM-2, The Original Climate Monitor*::*Climate Monitors*::*The Climate

    Sends Text messages via a e-mail if a condition is met (so you need to ensure your network/gateway is powered in the event of a power failure) - various bits and bobs can be added to monitor other things link power.

    Pete

  12. #12

    3s-gtech's Avatar
    Join Date
    Mar 2009
    Location
    Wales
    Posts
    2,999
    Thank Post
    156
    Thanked 628 Times in 561 Posts
    Rep Power
    163
    Our server room air-con used to do this - we got the engineers in to change the settings on the unit so it now autostarts. Can you do that for a start?

  13. Thanks to 3s-gtech from:

    Disease (11th June 2012)

  14. #13
    Disease's Avatar
    Join Date
    Jan 2006
    Posts
    1,108
    Thank Post
    120
    Thanked 70 Times in 48 Posts
    Rep Power
    57
    Thanks 3s will ask them.

  15. #14
    BatchFile's Avatar
    Join Date
    Aug 2007
    Location
    Cumbria
    Posts
    958
    Thank Post
    548
    Thanked 128 Times in 106 Posts
    Rep Power
    60
    I've got a UPS on the aircon... but it's just a small domestic unit as the server count isn't huge

    (Rural location => Lumpy electricity)



SHARE:
+ Post New Thread

Similar Threads

  1. Atomic Clock Sync - Anyone know anything about it.
    By Davit2005 in forum Wired Networks
    Replies: 10
    Last Post: 20th October 2011, 11:22 PM
  2. Replies: 13
    Last Post: 15th June 2011, 10:50 PM
  3. Does anyone know anything about Maximizer 10 CRM?
    By riskyburden in forum MIS Systems
    Replies: 1
    Last Post: 12th August 2010, 11:53 PM
  4. Anyone know anything about Microphones?
    By maniac in forum General Chat
    Replies: 2
    Last Post: 13th October 2009, 10:42 AM
  5. Replies: 2
    Last Post: 29th September 2009, 08:33 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •