General Chat Thread, Whiteboard Calibration in General; Not entirely sure which forum I should really be dumping this topic in... buuuuut HEEEELP! Got a teacher here who ...
  1. #1
    Friez's Avatar
    Join Date
    Dec 2006
    Posts
    839
    Thank Post
    22
    Thanked 22 Times in 21 Posts
    Rep Power
    23

    Whiteboard Calibration

    Not entirely sure which forum I should really be dumping this topic in... buuuuut HEEEELP!

    Got a teacher here who whinges almost every day about his interactive whiteboard (he's officially the schools biggest moaner!) Anyway.... this time he does have something to moan about!

    His interactive whiteboard (SMART) has trouble calibrating. In the mornings he declares that it is knocked well out of line (and sometimes during the course of the day). At first I suspected a student may have been playing a prank on him when he had his back turned, but now I'm not so sure.

    I managed to catch him when his board was knocked out of line and attempted to recalibrate myself.... and I discovered that it actually refused to calibrate properly!

    Check the attached image.

    Those lines were drawn using a straight edge as a guide, notice how they're significantly wobbly on the far left / right side near the bottom.

    Admittedly this is better than it was, the lines were almost an entire square out of line before calibration, but its still not spot on (even after several failed attempts at calibrating).

    This guy is a maths teacher too, so it causes him hell in lessons where precision is required (such as coordinates and the like).

    Anyone had a problem like this before? Anyone figured out how to solve it? Should I be going back to the manufacturer?
    Attached Thumbnails Attached Thumbnails Whiteboard Calibration-boardcalibration.png  

  2. #2

    Domino's Avatar
    Join Date
    Oct 2006
    Location
    Bromley
    Posts
    4,104
    Thank Post
    217
    Thanked 1,308 Times in 805 Posts
    Blog Entries
    4
    Rep Power
    515

    Re: Whiteboard Calibration

    is the projector at a strange angle or straight on?

    Also is the keystoning all set up right?

  3. #3

    elsiegee40's Avatar
    Join Date
    Jan 2007
    Location
    Kent
    Posts
    9,825
    Thank Post
    1,823
    Thanked 2,252 Times in 1,658 Posts
    Rep Power
    805

    Re: Whiteboard Calibration

    We had this problem with one of our boards. It was only a couple of months old, but it turned out it had started to delaminate. For us it was replaced under guarantee...

  4. #4

    Join Date
    Mar 2007
    Location
    Devon
    Posts
    1,042
    Thank Post
    226
    Thanked 63 Times in 56 Posts
    Rep Power
    30

    Re: Whiteboard Calibration

    We are getting a similar problem with one of our smartboards i am going to give it a good test at breaktime see if it's the user or something more important. Will let you know how i get on.

  5. #5
    alexknight's Avatar
    Join Date
    Jul 2005
    Location
    Somerset
    Posts
    205
    Thank Post
    7
    Thanked 1 Time in 1 Post
    Rep Power
    20

    Re: Whiteboard Calibration

    Umm, strange. We have the same problem with one of our newer Smart Boards.

    When it has been calibrated the alignment is not correct. the problem is that when you write on the board the actual writing appears about 2 cm above where you are writing. Never had this problem before and I don't think it would be down to the projector?

    Alex

  6. #6
    Disease's Avatar
    Join Date
    Jan 2006
    Posts
    1,100
    Thank Post
    118
    Thanked 70 Times in 48 Posts
    Rep Power
    56

    Re: Whiteboard Calibration

    What point calibration are you set at? We use 20 point callibration here and never had a problem.

  7. #7

    Join Date
    Mar 2007
    Location
    Central Scotland
    Posts
    829
    Thank Post
    12
    Thanked 8 Times in 8 Posts
    Rep Power
    19

    Re: Whiteboard Calibration

    I use 9 point calibration and never had a problem - never noticed any improvement with the higher level calibration even for handwriting.

    Looking that the OPs picture I'd say it was a faulty smartboard, but you could replace the USB cable to see if that helps - hell you never know!

  8. #8

    Join Date
    Mar 2007
    Location
    Barnsley south yorkshire
    Posts
    157
    Thank Post
    2
    Thanked 12 Times in 5 Posts
    Rep Power
    18

    Re: Whiteboard Calibration

    is it an older 500 series bored (with the black plastic around the edges) or a newer 600 series with the silver edges?

    how long has it been in? did you register the board for the extra 3 years warrenty when you installed the software?

  9. #9
    enjay's Avatar
    Join Date
    Apr 2007
    Location
    Reading, Berkshire, UK
    Posts
    4,488
    Thank Post
    282
    Thanked 196 Times in 167 Posts
    Rep Power
    76

    Re: Whiteboard Calibration

    We had something similar on one of our 580s - got it replaced under warranty for a 680!

  10. #10

    SimpleSi's Avatar
    Join Date
    Jun 2005
    Location
    Lancashire
    Posts
    5,824
    Thank Post
    1,476
    Thanked 593 Times in 445 Posts
    Rep Power
    168

    Re: Whiteboard Calibration

    Make sure you register the board for the guarantee extension.

    Many people have no problems with their boards - that just means they are lucky - I've had 2 reported faulty in last 2 weeks

    You need to go down the route of software/hardware subsitution.

    Swap board with another class - does the fault go with it.

    Try a laptop (pref that has never had Smart software on it before) see what happens.

    Swap cable if possible.

    Check version of driver on a a working machine vs the faulty class.

    Sacrifice small animal.

    Contact your supplier and see if they are interested in helping you find the fault :P

    When all else fails - contact Steljes (the UK importer) but pe prepared for the worst support you've ever ever experiencd

    Good luck

    regards

    Simon

  11. #11
    TechSupp's Avatar
    Join Date
    Mar 2007
    Location
    South Yorkshire
    Posts
    1,916
    Thank Post
    315
    Thanked 122 Times in 103 Posts
    Rep Power
    42

    Re: Whiteboard Calibration

    I had a similar one, caused problems when teacher was trying to demonstrate correct hand writting techniques! Eventually fixed by re-routing the USB cable away from any power sources. If its a new board (silver edge) there is a warning that they are very sensitive to EMF, even to what walls they are fixed to.

  12. #12
    Friez's Avatar
    Join Date
    Dec 2006
    Posts
    839
    Thank Post
    22
    Thanked 22 Times in 21 Posts
    Rep Power
    23

    Re: Whiteboard Calibration

    Sacrifice small animal.
    Will do.

    how long has it been in?
    Only a few months.

    is the projector at a strange angle or straight on?
    It's mounted to the ceiling, not straight on (kids would be bumping their heads otherwise), but it's reasonable. Same height as other rooms, and this issue never used to exist before. It's keystoned rather well, seems pretty well aligned with the board.

    What point calibration are you set at?
    I set it to the finest (20) as part of my usual install routine. I've discovered from experience that 9 or 4 tend to achieve less accurate results, and these guys are zealots for accuracy.

    I'll try as many of the suggestions above that I am able to while the NM is out and report my findings back here! Thanks for the advice!

  13. #13

    Join Date
    Mar 2007
    Location
    Barnsley south yorkshire
    Posts
    157
    Thank Post
    2
    Thanked 12 Times in 5 Posts
    Rep Power
    18

    Re: Whiteboard Calibration

    if it is a new 600 series board try removing the pen tray, (a couple of clips undernearth if you look you will see them) then loosen the 2 screws that hold the board to the wall slightly, if these are 2 tight is will bend the board slightly making the orientation go out.

    you could also try swapping the control box on the back if the problem carrys on, i cant see it being this tbh but it is woth a try its only a couple of screws.

    finaly get your self an A-B usb cable and unplug the existing usb cable from the back of the board and go straight from there to your computer canceling out your break out box.

    if all this fails contact the company that installed it and let them deal with it if it has only been in a few months.

  14. #14

    Join Date
    Nov 2008
    Posts
    5
    Thank Post
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Quote Originally Posted by SimpleSi View Post
    Make sure you register the board for the guarantee extension.

    Many people have no problems with their boards - that just means they are lucky - I've had 2 reported faulty in last 2 weeks

    You need to go down the route of software/hardware subsitution.

    Swap board with another class - does the fault go with it.

    Try a laptop (pref that has never had Smart software on it before) see what happens.

    Swap cable if possible.

    Check version of driver on a a working machine vs the faulty class.

    Sacrifice small animal.

    Contact your supplier and see if they are interested in helping you find the fault :P

    When all else fails - contact Steljes (the UK importer) but pe prepared for the worst support you've ever ever experiencd

    Good luck

    regards

    Simon
    Hi Simon,

    Apologies for the bad experience you have had with steljes. Please email me your concerns at services@steljes.co.uk and I will be more than happy to look into this for you. Please note that this email applies to everyone. Please email us and we will look into resolving the issues you have.

    Regards

    Steve

  15. #15
    DarrenC's Avatar
    Join Date
    Aug 2008
    Location
    Leeds
    Posts
    158
    Thank Post
    2
    Thanked 29 Times in 22 Posts
    Rep Power
    18
    Its nice to hear a distributor offering assistance to schools, however I would suggest that everyone should speak to the company they bought their equipment from first.

    It is most definitely the suppliers job to offer support and assistance where ever possible to their customers. Too many companies now rely on the distributors/manufacturers to offer their customer support for them.

    It sounds like this may end up with replacing the board under warranty, if not it will be an install issue so you should definitely contact your supplier.

SHARE:
+ Post New Thread
Page 1 of 2 12 LastLast

Similar Threads

  1. Webster whiteboard software
    By cookie_monster in forum Educational Software
    Replies: 0
    Last Post: 7th December 2007, 01:55 PM
  2. Laptop/Whiteboard problem
    By witch in forum Hardware
    Replies: 26
    Last Post: 6th December 2007, 10:00 AM
  3. Projecting on Whiteboard Issue !
    By drewinc in forum Hardware
    Replies: 18
    Last Post: 22nd November 2007, 02:06 PM
  4. Whiteboard alignment
    By witch in forum Hardware
    Replies: 18
    Last Post: 17th October 2007, 06:25 PM
  5. Interactive Whiteboard Courses
    By TossPot in forum Courses and Training
    Replies: 8
    Last Post: 28th July 2005, 09:38 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •