General Chat Thread, A challenge in General; 1) S 2) 1360 3) 2.2m x 3.8m 4) No 5) Yes - office and and a store room knocked ...
  1. #16

    Join Date
    Apr 2007
    Location
    Sutton Coldfield
    Posts
    207
    Thank Post
    29
    Thanked 34 Times in 28 Posts
    Rep Power
    20
    1) S
    2) 1360
    3) 2.2m x 3.8m
    4) No
    5) Yes - office and and a store room knocked together
    6) 4 Racks
    7) APC
    8) 3 Racks (Server etc) are 42U - 60cm wide and 1.1m depth, 1 Rack (Comms) is 42U - 80cm wide and 1.1m depth)
    9) Server Rack - 18U Servers, 2U ToR Switches (rest is empty), Storage Rack - 16U SANs, 3U iSCSI Switches (rest is empty), VDI/Backup Rack - 15U Servers, 2U Shelf for Mac Mini/Securus/Time Capsule, 2U Tapeloader, 2U ToR Switches (rest is empty), Comms Rack, 11U Patch Panels, 9U Switches/Routers/Firewalls/Ruckus Controller. (rest is empty)
    10) Server/SAN Racks, about 12 Amps Drawn and Comms Rack about 5amps. 15000KVA UPS is available that services all racks.
    11) Not sure
    12) Servers etc racks about 190-200KG, Comms about 100KG
    13) 10KW plus 7KW

    Thanks,

    Rob
    Last edited by robknowles; 22nd November 2012 at 05:55 PM.

  2. Thanks to robknowles from:

    GrumbleDook (22nd November 2012)

  3. #17

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,497
    Thank Post
    513
    Thanked 2,391 Times in 1,853 Posts
    Blog Entries
    24
    Rep Power
    819
    1. M
    2. 545
    3. 2m x 3m
    4. Yes, toner storage
    5. Yes, used to be a paper store
    6. 1
    7. Prism
    8. 19" x 42U don't know depth - standard depth
    9. 10U UPS, 1U environment monitoring, 1U Wireless controller, 3U fibre patch panels, 4U switch, 2U KVM, 18U servers, 3U cable management
    10. 32A available around 16A drawn.
    11. Don't know
    12. Don't know
    13. Don't know

    With 9 - 18U servers will become 9U servers soon, when 9U are retired, meaning 10 will also drop by about 4.5A.

  4. Thanks to localzuk from:

    GrumbleDook (22nd November 2012)

  5. #18
    aleach2's Avatar
    Join Date
    Apr 2008
    Location
    Bracknell
    Posts
    64
    Thank Post
    9
    Thanked 17 Times in 16 Posts
    Rep Power
    15
    1) S
    2) 1100
    3) 3.7m x 2.7m
    4) Some Minor Storage (Toners & Spare Laptops)
    5) Dedicated Room
    6) 2
    7) Prism
    8) 19" x 47U x 1200mm
    9) Rack 1 = 4U UPS (2x 2 UPS), 4U Hitachi SAN, 9U Servers (4 x 2U + 1 x 1U), 2U NAS, 2U Switches (VMware Backend), 25U Free | Rack 2 = 4U Core Switch, 2U Routher, 1U WiFi Controller, 1U Smoothwall Appliance, 1U Virgin Switch, 1U Fibre Converter, 11U Fibre Cables, 8U Cable Management Arms.
    10) 3 x 16Amp Commando Connectors, not sure how much power is used
    11) Unknown
    12) Heavy!!!!!!
    13) Unknown, we have 1 x moderate size AC
    Last edited by aleach2; 22nd November 2012 at 06:19 PM.

  6. Thanks to aleach2 from:

    GrumbleDook (22nd November 2012)

  7. #19

    Sylv3r's Avatar
    Join Date
    Jul 2005
    Location
    Co. Durham
    Posts
    3,197
    Thank Post
    370
    Thanked 373 Times in 331 Posts
    Rep Power
    147
    1. S
    2. 1,514
    3. 5m x 3m x 2m (length x width x height)
    4. No
    5. It has already been designated as the server room, but only within the last few years does it tick all boxes
    6. 3
    7. Can't remember
    8. 3 x 19" x 42Ux 1200)
    9. Off the top of my head, can't think
    10. Don't know
    11. Don't know
    12. Don't know
    13. Don't know

  8. Thanks to Sylv3r from:

    GrumbleDook (22nd November 2012)

  9. #20


    Join Date
    May 2009
    Posts
    2,866
    Thank Post
    258
    Thanked 766 Times in 581 Posts
    Rep Power
    269
    Cripes.

    1. S
    2. ~2400
    3. We have two server rooms, a primary and a 'backup'. P is ~3m*5m, B is ~3*2.5 (but is a wierd shape).
    4. (presume you mean room). Not really, although some surplus stuff lingers too long until I nag.
    5. School predates technology so they are both conversions.
    6. 4 in primary, 1 in secondary but soon to expand to 2.
    7. No idea.
    8. 4 * 42U 19" 1200 inm primary, 1 24/27U in backup.

    I need to check to answer the rest with any degree of accuracy!

  10. Thanks to pcstru from:

    GrumbleDook (22nd November 2012)

  11. #21

    DaveP's Avatar
    Join Date
    Oct 2006
    Location
    Can't talk now: The mother-ship is calling!
    Posts
    8,698
    Thank Post
    351
    Thanked 1,268 Times in 866 Posts
    Blog Entries
    4
    Rep Power
    1124
    @GrumbleDook: quite a few replies have indicated in reply 12 that the loaded rack is HEAVY [my reply included] and @twin--turbo mentioned a consideration not included in your post: server Room location: Ground floor or first floor?

    Our Server Room is located on the first floor and although our loaded rack is heavy it is not a 'threat' to the floor. This may not be true for all schools?

    [Our Finance Department has a safe that certainly could not be located on our upper floors]

  12. Thanks to DaveP from:

    GrumbleDook (22nd November 2012)

  13. #22

    GrumbleDook's Avatar
    Join Date
    Jul 2005
    Location
    Gosport, Hampshire
    Posts
    9,921
    Thank Post
    1,332
    Thanked 1,773 Times in 1,100 Posts
    Blog Entries
    19
    Rep Power
    593
    Quote Originally Posted by DaveP View Post
    @GrumbleDook: quite a few replies have indicated in reply 12 that the loaded rack is HEAVY [my reply included] and @twin--turbo mentioned a consideration not included in your post: server Room location: Ground floor or first floor?

    Our Server Room is located on the first floor and although our loaded rack is heavy it is not a 'threat' to the floor. This may not be true for all schools?

    [Our Finance Department has a safe that certainly could not be located on our upper floors]
    I'm not so much worried about which floor the server room is in for this survey ... that question was mainly to give examples weights so that the consideration of threat to raised floors ... not that many schools have raised floors in their server rooms.

  14. #23

    glennda's Avatar
    Join Date
    Jun 2009
    Location
    Sussex
    Posts
    7,784
    Thank Post
    272
    Thanked 1,129 Times in 1,025 Posts
    Rep Power
    348
    Quote Originally Posted by glennda View Post
    This is for my previous school

    1. Secondary
    2. 1600
    3. 3 x 4
    4. no
    5. Yes built out of old store room.
    6. 3 (was 4)
    7. HP
    8. 19" 42U 1200
    9. rack 1 4U UPS - Rest Servers 4U San 1U Fiber Switch. Rack 2 - Switching and Patch panels Rack 3. Servers, KVM and routers. 1 x B500 free standing ups
    10. B500 is 3 phase 32 amp, APC SUA10000 - 32amp 3 phase
    11. not a clue
    12. A lot
    13. Don't know but had two large Daikin Air con units for the room kept at 19 degrees.
    Should have also said there was a second "backup room" which consisted of 2 x 42U racks - on with patch and switching in, the second with 8u of servers storing onsite backup (1 x 4U 36bay 32TB backup server 1 x HP DL380, 1 x HP MSA60).

  15. #24

    DaveP's Avatar
    Join Date
    Oct 2006
    Location
    Can't talk now: The mother-ship is calling!
    Posts
    8,698
    Thank Post
    351
    Thanked 1,268 Times in 866 Posts
    Blog Entries
    4
    Rep Power
    1124
    Quote Originally Posted by GrumbleDook View Post
    ... that question was mainly to give examples weights so that the consideration of threat to raised floors ... not that many schools have raised floors in their server rooms.
    For clarity we do not have a raised floor [false floor] in our sever room.

  16. #25

    elsiegee40's Avatar
    Join Date
    Jan 2007
    Location
    Kent
    Posts
    10,629
    Thank Post
    1,771
    Thanked 2,155 Times in 1,594 Posts
    Rep Power
    767
    Going back to the dark ages of mainframes... weight of equipment was rarely a threat to the raised floor. There was too much cable underneath holding it up. We rarely reused cabling as kit changed. It was left in place and new cables laid under the floor where we could find room!

  17. #26

    SYNACK's Avatar
    Join Date
    Oct 2007
    Posts
    10,981
    Thank Post
    850
    Thanked 2,648 Times in 2,250 Posts
    Blog Entries
    9
    Rep Power
    763
    If you want distant schools:
    1 PMJ
    2 500
    3 2M by 5M by 3M high
    4 some computer parts/spares as it is secure
    5 was storage
    6 1 x 42u - full
    7 hp
    8 19" rails, 42u, umm - standard four post
    9 5u UPS, 9U Server, 2U San, 1U Ruckus, 5U phonesystem, 4U switching, rest is patch pannels
    10 16A
    11 don't know
    12 heavy
    13 can't remember

    1 PJ
    2 500
    3 4M by 5M by 2.5M high
    4 some computer parts/spares as it is secure
    5 dedicated
    6 2 x 42u - full
    7 hp
    8 19" rails, 42u, umm - standard four post
    9 11u UPS, 17U Server, 2U San, 5U phonesystem, 7U switching, rest is patch pannels, about 20u free
    10 32A+ 16A
    11 don't know
    12 heavy
    13 can't remember

  18. Thanks to SYNACK from:

    GrumbleDook (23rd November 2012)

  19. #27

    elsiegee40's Avatar
    Join Date
    Jan 2007
    Location
    Kent
    Posts
    10,629
    Thank Post
    1,771
    Thanked 2,155 Times in 1,594 Posts
    Rep Power
    767
    1. NP
    2. 150
    3. 6' x 6' x sloping roof (approx 4' at its lowest to 8')
    4. Photocopier and general storage
    5. No. Servers just put where there was space
    6. Zero. 2 servers, but neither are rack mounts. Switches, etc are in cabinets wall mounted high in rooms around the school.
    7. HP
    8. Roughly 20" x9" footprint each
    9. Don't know
    10. Don't know
    11. Don't know
    12. Don't know
    13. What air con?

  20. Thanks to elsiegee40 from:

    GrumbleDook (23rd November 2012)

  21. #28

    tmcd35's Avatar
    Join Date
    Jul 2005
    Location
    Norfolk
    Posts
    5,568
    Thank Post
    833
    Thanked 872 Times in 725 Posts
    Blog Entries
    9
    Rep Power
    324
    Interesting survey. There seem to be a number of similarities (as well as differences) between schools. For instance, Toner storage. Are we all under the mis-guided believe that the Air Con is somehow beneficial to the powder .

    A couple of other questions do naturally flow from this if we were to compare IT structure between schools.

    > How many use the server room as an office? (I did at my last school for about a year until teachers were booted out the office opposite).
    > How many NM's share an office with other IT staff, or do you have your own? (I've just got my very own office for the first time this year! )
    > How far away from the server room is your office? (Previously I was in the next room, techs still are. I'm now half a corridor away but was nearly moved to the other side of the school)
    > Do you have a secondary/back up server room? (We have a wall mount cabinet with a 2U NAS box in a remote cupboard)

    but the question that made me think of this reply...

    >Whose setup's pre-date them as a NM?

    Mine does. Oh, I've completely change the servers, added storage, virtualisation, etc. But the actual racks, switches, electrics, cabling, room, etc, all pre-date me and might even pre-date my predecessor!

    Just for completeness, my server room is also on the first floor and the cabinets are both free standing (UPS's along make them unmovable), they are not secured to the walls, floor, ceiling in any way as far as I know,

  22. #29

    localzuk's Avatar
    Join Date
    Dec 2006
    Location
    Minehead
    Posts
    17,497
    Thank Post
    513
    Thanked 2,391 Times in 1,853 Posts
    Blog Entries
    24
    Rep Power
    819
    Quote Originally Posted by tmcd35 View Post
    Interesting survey. There seem to be a number of similarities (as well as differences) between schools. For instance, Toner storage. Are we all under the mis-guided believe that the Air Con is somehow beneficial to the powder .
    Lol, no. Its actually pretty detrimental, as when the A/C unit breaks down and leaks all over the boxes it isn't good. Its just a space thing for me.

  23. #30

    twin--turbo's Avatar
    Join Date
    Jun 2012
    Location
    Carlisle
    Posts
    2,334
    Thank Post
    1
    Thanked 381 Times in 340 Posts
    Rep Power
    150
    Quote Originally Posted by tmcd35 View Post
    > How many NM's share an office with other IT staff, or do you have your own? (I've just got my very own office for the first time this year! )
    Would not want my own office. We work as a team, we discuss issues during work flow. Having to go to another office would be detreimental to day to day operation and development.

    Rob

SHARE:
+ Post New Thread
Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Multiple Sclerosis Challenge
    By NBC_Sys_C-ord in forum General Chat
    Replies: 0
    Last Post: 26th June 2007, 02:19 PM
  2. Please Help - What are the challenges and opportunities faci
    By doc69 in forum School ICT Policies
    Replies: 2
    Last Post: 20th May 2007, 07:28 PM
  3. Who wants $50 - web challenge!
    By _Bat_ in forum Web Development
    Replies: 5
    Last Post: 14th March 2007, 01:09 PM
  4. Challenge
    By SteveT in forum General Chat
    Replies: 12
    Last Post: 30th April 2006, 08:27 PM
  5. Replies: 8
    Last Post: 13th February 2006, 03:05 PM

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •